Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
I have the Smart-UPS RT 8000 XL.
Your status is Last Baterry Transfer: Detection of low utility voltage, What does that mean?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
This means your input voltage to the UPS was below the acceptable value. For instance, if your input voltage is 230 volts nominally (that means normally/expected), then if you're input was 190V, you may see this message after the UPS transfers to battery power so it can output 230 volts to your equipment to prevent damage.
If you want to provide your event.txt and data.txt, and config.ini from your network management card, I can elaborate more. Instructions on obtaining these log files are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
This means your input voltage to the UPS was below the acceptable value. For instance, if your input voltage is 230 volts nominally (that means normally/expected), then if you're input was 190V, you may see this message after the UPS transfers to battery power so it can output 230 volts to your equipment to prevent damage.
If you want to provide your event.txt and data.txt, and config.ini from your network management card, I can elaborate more. Instructions on obtaining these log files are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
Network Management Card AOS v6.0.6
Smart-UPS & Matrix-UPS APP v6.0.6
Data Hora Usuário Evento Código
18.11.2013 16:27:13 Sistema Email: Não foi possível enviar email para 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:27:03 Dispositivo No-break:Passou em um autoteste. 0x0105
18.11.2013 16:27:00 Sistema Email: Não foi possível enviar email para 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:26:47 Dispositivo No-break:Não há mais uma condição de bateria descarregada. 0x0108
18.11.2013 16:17:39 Dispositivo No-break:Passou em um autoteste. 0x0105
18.11.2013 16:17:30 Sistema Email: Não foi possível enviar email para 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:17:29 Dispositivo No-break:A energia da bateria está muito baixa para suportar a carga. Se a alimentação falhar, o no-break será desligado imediatamente. 0x0107
18.11.2013 16:17:21 Dispositivo No-break:Não há mais uma falha do inversor. 0x0166
18.11.2013 16:17:16 Dispositivo No-break:Não mais em bypass. 0x011E
18.11.2013 16:15:18 Dispositivo No-break:Recusou um autoteste. O no-break está sobrecarregado. 0x0106
18.11.2013 16:15:18 Dispositivo No-break:Falha do inversor. 0x0165
18.11.2013 16:15:13 Dispositivo No-break:Em bypass devido a uma falha de hardware interna. 0x011B
18.11.2013 12:52:18 Dispositivo No-break:Não há mais uma condição de bateria descarregada. 0x0108
18.11.2013 12:50:33 Dispositivo No-break:Passou em um autoteste. 0x0105
18.11.2013 12:50:20 Dispositivo No-break:A energia da bateria está muito baixa para suportar a carga. Se a alimentação falhar, o no-break será desligado imediatamente. 0x0107
16.11.2013 21:43:16 Dispositivo No-break:Não mais operando por bateria. 0x010A
16.11.2013 21:42:58 Dispositivo No-break:Operando por bateria devido a um problema de alimentação de entrada. 0x0109
07.11.2013 23:16:15 Dispositivo No-break:Passou em um autoteste. 0x0105
07.11.2013 23:16:08 Dispositivo No-break:Autoteste iniciado. 0x0137
07.11.2013 09:47:18 Dispositivo No-break:Não mais operando por bateria. 0x010A
07.11.2013 09:43:08 Dispositivo No-break:Operando por bateria devido a um problema de alimentação de entrada. 0x0109
07.11.2013 09:13:19 Dispositivo No-break:Não mais operando por bateria. 0x010A
07.11.2013 09:13:12 Dispositivo No-break:Operando por bateria devido a um problema de alimentação de entrada. 0x0109
07.11.2013 09:12:40 Dispositivo No-break:Não mais operando por bateria. 0x010A
07.11.2013 09:10:04 Dispositivo No-break:Operando por bateria devido a um problema de alimentação de entrada. 0x0109
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
Can you translate this to english in your interface
and re-download the file and attach it to your post (using the advanced editor option) as a text file? If not, I will have to spend some time translating it and I just don't want to miss anything.
I also need the data.txt...
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
EVENT
zNetwork Management Card AOS v6.0.6
Smart-UPS & Matrix-UPS APP v6.0.6
Date Time User Event Code
18.11.2013 16:27:13 System Email: Could not mail 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:27:03 Device UPS: Passed a self-test. 0x0105
18.11.2013 16:27:00 System Email: Could not mail 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:26:47 Device UPS: A discharged battery condition no longer exists. 0x0108
18.11.2013 16:18:22 System Email: Could not mail 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:18:09 System Email: Could not mail 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:17:56 System Email: Could not mail 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:17:43 System Email: Could not mail 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:17:39 Device UPS: Passed a self-test. 0x0105
18.11.2013 16:17:30 System Email: Could not mail 'mail.casaaffonso.com.br'. 0x001A
18.11.2013 16:17:29 Device UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107
18.11.2013 16:17:21 Device UPS: An inverter fault no longer exists. 0x0166
18.11.2013 16:17:16 Device UPS: No longer in bypass. 0x011E
18.11.2013 16:15:18 Device UPS: Refused a self-test; UPS is overloaded. 0x0106
18.11.2013 16:15:18 Device UPS: An inverter fault exists. 0x0165
18.11.2013 16:15:13 Device UPS: In bypass in response to an internal hardware fault. 0x011B
18.11.2013 12:52:18 Device UPS: A discharged battery condition no longer exists. 0x0108
18.11.2013 12:50:33 Device UPS: Passed a self-test. 0x0105
18.11.2013 12:50:20 Device UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107
16.11.2013 21:43:16 Device UPS: No longer on battery power. 0x010A
16.11.2013 21:42:58 Device UPS: On battery power in response to an input power problem. 0x0109
07.11.2013 23:16:15 Device UPS: Passed a self-test. 0x0105
07.11.2013 23:16:08 Device UPS: Started a self-test. 0x0137
07.11.2013 09:47:18 Device UPS: No longer on battery power. 0x010A
07.11.2013 09:43:08 Device UPS: On battery power in response to an input power problem. 0x0109
07.11.2013 09:13:19 Device UPS: No longer on battery power. 0x010A
07.11.2013 09:13:12 Device UPS: On battery power in response to an input power problem. 0x0109
07.11.2013 09:12:40 Device UPS: No longer on battery power. 0x010A
07.11.2013 09:10:04 Device UPS: On battery power in response to an input power problem. 0x0109
DATA
Network Management Card AOS v6.0.6
Smart-UPS & Matrix-UPS APP v6.0.6
Smart-UPS RT 8000 XL
Date Time Vmin Vmax Vout Iout %Wout Freq %Cap Vbat TupsC %VAout
19.11.2013 15:19:29 216.0 221.7 230.4 3.71 7.0 59.99 100.0 217.0 27.4 10.0
19.11.2013 15:09:29 218.8 224.6 231.6 3.71 7.0 60.02 100.0 217.0 27.4 10.0
19.11.2013 14:59:29 218.8 224.6 231.6 3.71 7.0 60.05 100.0 217.0 27.4 10.0
19.11.2013 14:49:29 220.3 223.2 231.6 3.71 7.0 59.98 100.0 217.0 27.4 10.0
19.11.2013 14:39:29 220.3 223.2 231.6 3.71 7.0 60.00 100.0 217.0 27.4 10.0
19.11.2013 14:29:29 220.3 224.6 231.6 3.71 7.0 60.00 100.0 217.0 27.4 10.0
19.11.2013 14:19:29 221.7 224.6 231.6 3.71 7.0 60.01 100.0 217.0 27.4 10.0
19.11.2013 14:09:29 218.8 223.2 231.6 3.71 7.0 59.98 100.0 217.0 27.4 10.0
19.11.2013 13:59:29 220.3 223.2 231.6 3.71 7.0 59.99 100.0 217.0 27.4 10.0
19.11.2013 13:49:29 220.3 223.2 231.6 3.71 7.0 60.03 100.0 217.0 27.4 10.0
19.11.2013 13:39:29 221.7 223.2 231.6 3.71 7.0 60.00 100.0 217.0 27.4 10.0
19.11.2013 13:29:29 220.3 224.6 231.6 3.71 7.0 60.00 100.0 217.0 27.4 10.0
19.11.2013 13:19:29 216.0 226.0 231.6 3.71 7.0 59.97 100.0 218.1 26.8 10.0
19.11.2013 13:09:29 216.0 220.3 229.3 3.71 7.0 59.98 100.0 217.0 27.4 10.0
19.11.2013 12:59:29 218.8 220.3 229.3 3.71 7.0 60.02 100.0 218.1 26.8 10.0
19.11.2013 12:49:29 218.8 220.3 230.4 3.71 7.0 60.00 100.0 217.0 26.8 10.0
19.11.2013 12:39:29 218.8 221.7 230.4 3.71 7.0 60.03 100.0 218.1 26.8 10.0
19.11.2013 12:29:29 218.8 220.3 230.4 3.71 7.0 60.01 100.0 218.1 26.8 10.0
19.11.2013 12:19:29 218.8 220.3 230.4 3.71 7.0 60.01 100.0 218.1 26.8 10.0
19.11.2013 12:09:29 218.8 221.7 231.6 3.71 7.0 59.97 100.0 218.1 26.8 10.0
19.11.2013 11:59:29 218.8 221.7 230.4 3.71 7.0 60.02 100.0 218.1 26.8 10.0
19.11.2013 11:49:29 218.8 220.3 231.6 3.71 7.0 60.00 100.0 218.1 26.8 10.0
19.11.2013 11:39:28 217.4 220.3 230.4 3.71 7.0 59.98 100.0 218.1 27.4 10.0
19.11.2013 11:29:28 217.4 220.3 232.8 3.71 7.0 60.00 100.0 218.1 27.4 11.0
19.11.2013 11:19:28 217.4 220.3 230.4 3.71 7.0 60.00 100.0 217.0 26.8 10.0
19.11.2013 11:09:28 217.4 218.8 231.6 3.71 7.0 60.03 100.0 217.0 26.8 10.0
19.11.2013 10:59:28 216.0 220.3 231.6 3.71 7.0 60.01 100.0 218.1 26.8 10.0
19.11.2013 10:49:28 217.4 218.8 231.6 3.71 7.0 60.06 100.0 217.0 27.4 10.0
19.11.2013 10:39:28 216.0 218.8 230.4 3.71 7.0 60.01 100.0 217.0 27.4 10.0
19.11.2013 10:29:28 216.0 218.8 231.6 3.71 7.0 60.03 100.0 217.0 27.4 10.0
19.11.2013 10:19:28 216.0 217.4 231.6 3.71 7.0 60.00 100.0 217.0 27.4 10.0
19.11.2013 10:09:28 216.0 218.8 231.6 3.71 7.0 59.96 100.0 217.0 28.0 10.0
19.11.2013 09:59:28 216.0 218.8 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 09:49:28 214.5 218.8 231.6 3.71 7.0 59.97 100.0 217.0 28.0 10.0
19.11.2013 09:39:28 216.0 218.8 231.6 3.71 7.0 59.92 100.0 217.0 27.4 10.0
19.11.2013 09:29:28 217.4 218.8 231.6 3.71 7.0 59.98 100.0 217.0 27.4 10.0
19.11.2013 09:19:28 216.0 218.8 229.3 3.71 7.0 59.98 100.0 217.0 27.4 10.0
19.11.2013 09:09:28 218.8 220.3 231.6 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 08:59:28 218.8 220.3 230.4 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 08:49:28 220.3 221.7 230.4 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 08:39:28 220.3 223.2 230.4 3.71 7.0 60.05 100.0 217.0 28.0 10.0
19.11.2013 08:29:28 220.3 223.2 229.3 3.71 7.0 60.01 100.0 217.0 28.0 10.0
19.11.2013 08:19:28 218.8 223.2 231.6 3.71 7.0 59.97 100.0 217.0 28.0 10.0
19.11.2013 08:09:28 220.3 221.7 230.4 3.71 7.0 60.07 100.0 217.0 28.0 10.0
19.11.2013 07:59:28 220.3 223.2 231.6 3.71 7.0 59.99 100.0 217.0 28.0 10.0
19.11.2013 07:49:28 218.8 223.2 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 07:39:27 220.3 223.2 230.4 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 07:29:27 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 28.0 10.0
19.11.2013 07:19:27 218.8 224.6 231.6 3.71 7.0 60.03 100.0 217.0 28.0 10.0
19.11.2013 07:09:27 220.3 221.7 231.6 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 06:59:27 221.7 223.2 230.4 3.71 7.0 60.03 100.0 217.0 28.0 10.0
19.11.2013 06:49:27 221.7 223.2 231.6 3.71 7.0 59.96 100.0 217.0 28.0 10.0
19.11.2013 06:39:27 221.7 223.2 231.6 3.71 7.0 59.98 100.0 217.0 28.0 10.0
19.11.2013 06:29:27 221.7 223.2 230.4 3.71 7.0 60.05 100.0 217.0 28.0 10.0
19.11.2013 06:19:27 221.7 223.2 230.4 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 06:09:27 221.7 223.2 231.6 3.71 7.0 59.99 100.0 217.0 28.0 10.0
19.11.2013 05:59:27 220.3 221.7 230.4 3.71 7.0 60.01 100.0 217.0 28.0 10.0
19.11.2013 05:49:27 221.7 221.7 230.4 3.71 7.0 59.98 100.0 217.0 28.0 10.0
19.11.2013 05:39:27 220.3 221.7 229.3 3.71 7.0 60.04 100.0 217.0 28.0 10.0
19.11.2013 05:29:27 221.7 223.2 230.4 3.71 7.0 60.03 100.0 217.0 28.0 10.0
19.11.2013 05:19:27 221.7 223.2 229.3 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 05:09:27 221.7 223.2 230.4 3.71 7.0 60.04 100.0 217.0 28.0 10.0
19.11.2013 04:59:27 221.7 223.2 231.6 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 04:49:27 221.7 223.2 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 04:39:26 221.7 223.2 231.6 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 04:29:26 221.7 223.2 230.4 3.71 7.0 59.97 100.0 217.0 28.0 10.0
19.11.2013 04:19:26 221.7 223.2 230.4 3.71 7.0 59.96 100.0 217.0 28.0 10.0
19.11.2013 04:09:26 221.7 223.2 231.6 3.71 7.0 59.99 100.0 217.0 28.0 10.0
19.11.2013 03:59:26 221.7 223.2 231.6 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 03:49:26 221.7 223.2 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 03:39:26 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 28.0 10.0
19.11.2013 03:29:26 221.7 223.2 231.6 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 03:19:26 221.7 223.2 229.3 3.71 7.0 60.01 100.0 217.0 28.0 10.0
19.11.2013 03:09:26 221.7 223.2 229.3 3.71 7.0 59.99 100.0 217.0 28.0 10.0
19.11.2013 02:59:26 221.7 223.2 229.3 3.71 7.0 60.01 100.0 217.0 28.0 10.0
19.11.2013 02:49:26 221.7 223.2 229.3 3.71 7.0 60.01 100.0 217.0 28.0 10.0
19.11.2013 02:39:26 221.7 223.2 230.4 3.71 7.0 60.01 100.0 217.0 28.0 10.0
19.11.2013 02:29:26 221.7 223.2 231.6 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 02:19:26 221.7 223.2 230.4 3.71 7.0 60.02 100.0 217.0 28.0 11.0
19.11.2013 02:09:26 221.7 223.2 230.4 3.71 7.0 59.98 100.0 217.0 28.0 10.0
19.11.2013 01:59:26 221.7 223.2 230.4 3.71 7.0 59.98 100.0 217.0 28.0 10.0
19.11.2013 01:49:26 221.7 223.2 230.4 3.71 7.0 60.04 100.0 217.0 28.0 10.0
19.11.2013 01:39:26 221.7 223.2 230.4 3.71 7.0 60.02 100.0 217.0 28.0 10.0
19.11.2013 01:29:26 221.7 223.2 230.4 3.71 7.0 59.99 100.0 217.0 28.0 10.0
19.11.2013 01:19:26 220.3 224.6 229.3 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 01:09:26 223.2 224.6 231.6 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 00:59:26 223.2 224.6 229.3 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 00:49:26 223.2 224.6 229.3 3.71 7.0 59.99 100.0 217.0 28.0 10.0
19.11.2013 00:39:25 223.2 224.6 229.3 3.71 7.0 60.00 100.0 217.0 28.0 10.0
19.11.2013 00:29:25 224.6 224.6 229.3 3.71 7.0 59.99 100.0 217.0 28.0 10.0
19.11.2013 00:19:25 223.2 224.6 230.4 3.71 7.0 59.97 100.0 217.0 28.0 10.0
19.11.2013 00:09:25 223.2 227.5 231.6 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 23:59:25 224.6 226.0 230.4 3.71 7.0 59.98 100.0 217.0 28.0 10.0
18.11.2013 23:49:25 226.0 227.5 230.4 3.71 7.0 59.97 100.0 217.0 27.4 10.0
18.11.2013 23:39:25 226.0 227.5 231.6 3.71 7.0 60.02 100.0 217.0 28.0 10.0
18.11.2013 23:29:25 224.6 226.0 231.6 3.71 7.0 60.05 100.0 217.0 28.0 10.0
18.11.2013 23:19:25 224.6 227.5 230.4 3.71 7.0 59.96 100.0 217.0 28.0 10.0
18.11.2013 23:09:25 224.6 226.0 230.4 3.71 7.0 60.04 100.0 217.0 28.0 10.0
18.11.2013 22:59:25 223.2 226.0 230.4 3.71 7.0 60.05 100.0 217.0 28.0 10.0
18.11.2013 22:49:25 223.2 227.5 231.6 3.71 7.0 59.90 100.0 217.0 27.4 10.0
18.11.2013 22:39:25 226.0 227.5 229.3 3.71 7.0 59.98 100.0 217.0 28.0 10.0
18.11.2013 22:29:25 224.6 226.0 230.4 3.71 7.0 60.02 100.0 217.0 28.0 10.0
18.11.2013 22:19:25 224.6 226.0 230.4 3.71 7.0 59.96 100.0 217.0 28.0 10.0
18.11.2013 22:09:25 224.6 226.0 228.1 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 21:59:25 224.6 227.5 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
18.11.2013 21:49:25 224.6 226.0 231.6 3.71 7.0 60.00 100.0 217.0 28.0 10.0
18.11.2013 21:39:25 223.2 224.6 231.6 3.71 7.0 60.06 100.0 217.0 28.0 10.0
18.11.2013 21:29:25 223.2 226.0 231.6 3.71 7.0 60.05 100.0 217.0 28.0 10.0
18.11.2013 21:19:25 224.6 226.0 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
18.11.2013 21:09:25 223.2 224.6 231.6 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 20:59:25 223.2 224.6 230.4 3.71 7.0 60.01 100.0 217.0 28.0 10.0
18.11.2013 20:49:25 223.2 224.6 231.6 3.71 7.0 60.03 100.0 217.0 28.0 10.0
18.11.2013 20:39:25 223.2 224.6 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
18.11.2013 20:29:25 223.2 224.6 230.4 3.71 7.0 59.98 100.0 217.0 28.0 10.0
18.11.2013 20:19:24 223.2 223.2 231.6 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 20:09:24 221.7 223.2 231.6 3.71 7.0 59.96 100.0 217.0 28.0 10.0
18.11.2013 19:59:24 220.3 223.2 230.4 3.71 7.0 60.02 100.0 217.0 27.4 10.0
18.11.2013 19:49:24 220.3 223.2 231.6 3.71 7.0 60.03 100.0 217.0 27.4 10.0
18.11.2013 19:39:24 221.7 223.2 230.4 3.71 7.0 60.00 100.0 217.0 27.4 10.0
18.11.2013 19:29:24 223.2 224.6 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
18.11.2013 19:19:24 223.2 224.6 230.4 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 19:09:24 224.6 226.0 231.6 3.71 7.0 60.00 100.0 217.0 28.0 10.0
18.11.2013 18:59:24 224.6 227.5 231.6 3.71 7.0 60.03 100.0 217.0 28.0 10.0
18.11.2013 18:49:24 224.6 226.0 230.4 3.71 7.0 60.01 100.0 217.0 28.0 10.0
18.11.2013 18:39:24 224.6 226.0 230.4 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 18:29:24 223.2 224.6 231.6 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 18:19:24 223.2 224.6 230.4 3.71 7.0 60.01 96.0 217.0 28.0 10.0
18.11.2013 18:09:24 221.7 224.6 231.6 3.71 7.0 59.99 89.0 217.0 28.0 10.0
18.11.2013 17:59:24 220.3 223.2 230.4 3.71 7.0 60.03 82.0 217.0 28.0 10.0
18.11.2013 17:49:24 218.8 221.7 230.4 3.71 7.0 60.02 75.0 217.0 27.4 10.0
18.11.2013 17:39:24 218.8 220.3 230.4 3.71 7.0 60.00 68.0 217.0 28.0 10.0
18.11.2013 17:29:24 217.4 220.3 230.4 3.71 7.0 60.03 61.0 217.0 28.0 10.0
18.11.2013 17:19:24 218.8 220.3 230.4 3.71 7.0 60.02 54.0 217.0 28.0 10.0
18.11.2013 17:09:24 216.0 223.2 231.6 3.71 7.0 60.02 47.0 217.0 28.0 10.0
18.11.2013 16:59:24 221.7 226.0 230.4 3.71 7.0 60.05 40.0 217.0 28.0 10.0
18.11.2013 16:49:24 221.7 224.6 230.4 3.71 7.0 60.04 33.0 217.0 28.0 10.0
18.11.2013 16:39:23 218.8 224.6 231.6 3.71 7.0 60.06 26.0 217.0 28.0 10.0
18.11.2013 16:29:23 220.3 223.2 230.4 3.71 7.0 59.97 19.0 217.0 27.4 10.0
18.11.2013 16:19:23 220.3 223.2 230.4 3.71 7.0 60.00 1.0 217.0 28.0 10.0
18.11.2013 16:09:23 220.3 223.2 230.4 3.71 7.0 60.03 100.0 217.0 28.0 10.0
18.11.2013 15:59:23 220.3 223.2 231.6 3.71 7.0 60.01 100.0 217.0 28.0 10.0
18.11.2013 15:49:23 218.8 221.7 231.6 3.71 7.0 60.03 100.0 217.0 27.4 10.0
18.11.2013 15:39:23 218.8 221.7 231.6 3.71 7.0 59.96 100.0 217.0 27.4 10.0
18.11.2013 15:29:23 216.0 220.3 231.6 3.71 7.0 59.95 100.0 217.0 27.4 10.0
18.11.2013 15:19:23 218.8 220.3 231.6 3.71 7.0 59.99 100.0 217.0 27.4 10.0
18.11.2013 15:09:23 218.8 221.7 231.6 3.71 7.0 59.97 100.0 217.0 27.4 10.0
18.11.2013 14:59:23 217.4 220.3 230.4 3.71 7.0 60.01 99.0 217.0 27.4 10.0
18.11.2013 14:49:23 218.8 220.3 230.4 3.71 7.0 60.02 92.0 217.0 27.4 10.0
18.11.2013 14:39:23 217.4 221.7 230.4 3.71 7.0 60.04 85.0 217.0 28.0 10.0
18.11.2013 14:29:23 218.8 221.7 231.6 3.71 7.0 59.98 77.0 217.0 27.4 10.0
18.11.2013 14:19:23 218.8 220.3 230.4 3.71 7.0 60.00 71.0 217.0 27.4 10.0
18.11.2013 14:09:23 218.8 221.7 230.4 3.71 7.0 59.99 64.0 217.0 28.0 10.0
18.11.2013 13:59:23 218.8 221.7 230.4 3.71 7.0 59.99 56.0 217.0 28.0 10.0
18.11.2013 13:49:23 218.8 221.7 230.4 3.71 7.0 60.00 50.0 217.0 28.0 10.0
18.11.2013 13:39:23 218.8 220.3 230.4 3.71 7.0 60.00 43.0 217.0 28.0 10.0
18.11.2013 13:29:23 216.0 220.3 230.4 3.71 7.0 60.00 35.0 217.0 28.0 10.0
18.11.2013 13:19:23 216.0 218.8 230.4 3.71 7.0 59.98 29.0 217.0 28.0 10.0
18.11.2013 13:09:22 218.8 221.7 231.6 3.71 7.0 59.99 21.0 217.0 28.0 10.0
18.11.2013 12:59:22 218.8 221.7 231.6 3.71 7.0 60.02 14.0 217.0 28.0 10.0
18.11.2013 12:49:22 220.3 223.2 231.6 3.92 7.0 60.02 100.0 217.0 28.0 10.0
18.11.2013 12:39:22 220.3 223.2 230.4 3.71 7.0 60.03 100.0 217.0 28.0 10.0
18.11.2013 12:29:22 220.3 223.2 231.6 3.71 7.0 60.01 100.0 217.0 28.0 10.0
18.11.2013 12:19:22 220.3 223.2 230.4 3.71 7.0 60.01 100.0 217.0 28.0 10.0
18.11.2013 12:09:22 220.3 223.2 230.4 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 11:59:22 220.3 223.2 231.6 3.71 7.0 60.02 100.0 217.0 28.0 10.0
18.11.2013 11:49:22 218.8 221.7 231.6 3.71 7.0 59.94 100.0 217.0 28.0 10.0
18.11.2013 11:39:22 218.8 221.7 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
18.11.2013 11:29:22 218.8 221.7 231.6 3.71 7.0 60.04 100.0 217.0 28.0 10.0
18.11.2013 11:19:22 218.8 221.7 230.4 3.71 7.0 60.02 100.0 217.0 28.0 10.0
18.11.2013 11:09:22 218.8 221.7 230.4 3.71 7.0 60.03 100.0 217.0 28.0 10.0
18.11.2013 10:59:22 218.8 220.3 230.4 3.71 7.0 60.03 100.0 217.0 28.0 10.0
18.11.2013 10:49:22 217.4 220.3 230.4 3.71 7.0 60.00 100.0 217.0 28.0 10.0
18.11.2013 10:39:22 217.4 220.3 229.3 3.71 7.0 59.99 100.0 217.0 28.0 10.0
18.11.2013 10:29:22 217.4 220.3 231.6 3.71 7.0 60.01 100.0 217.0 28.5 10.0
18.11.2013 10:19:22 216.0 218.8 230.4 3.71 7.0 59.97 100.0 217.0 28.5 10.0
18.11.2013 10:09:22 217.4 218.8 230.4 3.71 7.0 59.99 100.0 217.0 29.1 10.0
18.11.2013 09:59:22 217.4 220.3 229.3 3.71 7.0 60.03 100.0 217.0 29.1 10.0
18.11.2013 09:49:22 218.8 220.3 230.4 3.71 7.0 60.00 100.0 217.0 29.1 10.0
18.11.2013 09:39:22 218.8 220.3 229.3 3.71 7.0 60.01 100.0 217.0 29.1 10.0
18.11.2013 09:29:22 218.8 221.7 230.4 3.71 7.0 59.98 100.0 217.0 29.6 10.0
18.11.2013 09:19:22 220.3 221.7 230.4 3.71 7.0 60.00 100.0 217.0 29.1 10.0
18.11.2013 09:09:22 220.3 221.7 229.3 3.71 7.0 60.03 100.0 217.0 29.6 10.0
18.11.2013 08:59:22 221.7 223.2 229.3 3.71 7.0 60.00 100.0 217.0 29.6 10.0
18.11.2013 08:49:21 220.3 223.2 230.4 3.71 7.0 60.00 100.0 217.0 29.6 10.0
18.11.2013 08:39:21 220.3 223.2 230.4 3.71 7.0 60.04 100.0 217.0 29.1 10.0
18.11.2013 08:29:21 220.3 223.2 230.4 3.71 7.0 60.01 100.0 217.0 29.1 10.0
18.11.2013 08:19:21 221.7 223.2 231.6 3.71 7.0 59.98 100.0 217.0 29.6 10.0
18.11.2013 08:09:21 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.6 10.0
18.11.2013 07:59:21 223.2 224.6 231.6 3.71 7.0 60.00 100.0 217.0 29.6 10.0
18.11.2013 07:49:21 224.6 226.0 229.3 3.71 7.0 59.93 100.0 217.0 29.6 10.0
18.11.2013 07:39:21 224.6 226.0 230.4 3.71 7.0 60.02 100.0 217.0 29.6 10.0
18.11.2013 07:29:21 224.6 226.0 229.3 3.71 7.0 59.98 100.0 217.0 29.6 10.0
18.11.2013 07:19:21 220.3 226.0 230.4 3.71 7.0 60.02 100.0 217.0 29.1 10.0
18.11.2013 07:09:21 220.3 223.2 230.4 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 06:59:21 223.2 224.6 230.4 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 06:49:21 223.2 224.6 230.4 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 06:39:21 224.6 226.0 230.4 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 06:29:21 224.6 226.0 231.6 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 06:19:21 224.6 224.6 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 06:09:21 224.6 224.6 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 05:59:21 223.2 224.6 230.4 3.71 7.0 60.05 100.0 217.0 29.6 10.0
18.11.2013 05:49:21 223.2 224.6 231.6 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 05:39:21 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.6 10.0
18.11.2013 05:29:21 223.2 224.6 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 05:19:21 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.6 10.0
18.11.2013 05:09:21 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.6 10.0
18.11.2013 04:59:21 224.6 224.6 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 04:49:21 224.6 224.6 231.6 3.71 7.0 60.00 100.0 217.0 29.6 10.0
18.11.2013 04:39:21 224.6 226.0 231.6 3.71 7.0 60.03 100.0 217.0 29.6 10.0
18.11.2013 04:29:20 224.6 226.0 231.6 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 04:19:20 224.6 226.0 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 04:09:20 224.6 226.0 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 03:59:20 224.6 226.0 231.6 3.71 7.0 60.00 100.0 217.0 29.6 10.0
18.11.2013 03:49:20 224.6 226.0 231.6 3.71 7.0 60.04 100.0 217.0 29.6 10.0
18.11.2013 03:39:20 224.6 226.0 229.3 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 03:29:20 224.6 226.0 229.3 3.71 7.0 60.03 100.0 217.0 29.6 10.0
18.11.2013 03:19:20 224.6 226.0 229.3 3.71 7.0 59.99 100.0 217.0 29.1 10.0
18.11.2013 03:09:20 224.6 226.0 229.3 3.71 7.0 60.00 100.0 217.0 29.6 10.0
18.11.2013 02:59:20 224.6 226.0 229.3 3.71 7.0 60.02 100.0 217.0 29.6 10.0
18.11.2013 02:49:20 224.6 226.0 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
18.11.2013 02:39:20 224.6 226.0 229.3 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 02:29:20 224.6 226.0 229.3 3.71 7.0 60.04 100.0 217.0 29.6 10.0
18.11.2013 02:19:20 223.2 224.6 231.6 3.71 7.0 59.96 100.0 217.0 29.6 10.0
18.11.2013 02:09:20 224.6 224.6 229.3 3.71 7.0 60.02 100.0 217.0 29.6 10.0
18.11.2013 01:59:20 223.2 224.6 230.4 3.71 7.0 60.02 100.0 217.0 29.6 10.0
18.11.2013 01:49:20 223.2 224.6 230.4 3.71 7.0 60.00 100.0 217.0 29.6 10.0
18.11.2013 01:39:20 223.2 224.6 230.4 3.71 7.0 60.02 100.0 217.0 29.6 10.0
18.11.2013 01:29:20 224.6 224.6 230.4 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 01:19:20 224.6 226.0 230.4 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 01:09:20 224.6 226.0 230.4 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 00:59:20 224.6 226.0 231.6 3.71 7.0 60.01 100.0 217.0 29.6 10.0
18.11.2013 00:49:20 224.6 226.0 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
18.11.2013 00:39:20 224.6 226.0 230.4 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 00:29:20 224.6 224.6 229.3 3.71 7.0 59.99 100.0 217.0 29.6 10.0
18.11.2013 00:19:20 224.6 226.0 229.3 3.71 7.0 60.00 100.0 217.0 29.6 10.0
18.11.2013 00:09:19 224.6 226.0 230.4 3.71 7.0 59.98 100.0 217.0 29.6 10.0
17.11.2013 23:59:19 224.6 226.0 229.3 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 23:49:19 224.6 224.6 229.3 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 23:39:19 223.2 224.6 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 23:29:19 223.2 224.6 231.6 3.71 7.0 60.01 100.0 217.0 29.6 9.0
17.11.2013 23:19:19 223.2 224.6 230.4 3.71 7.0 59.95 100.0 217.0 29.1 10.0
17.11.2013 23:09:19 223.2 224.6 230.4 3.71 7.0 60.01 100.0 217.0 29.6 10.0
17.11.2013 22:59:19 223.2 224.6 231.6 3.71 7.0 59.95 100.0 217.0 29.1 10.0
17.11.2013 22:49:19 223.2 224.6 230.4 3.71 7.0 60.03 100.0 217.0 29.6 10.0
17.11.2013 22:39:19 221.7 223.2 230.4 3.71 7.0 60.03 100.0 217.0 29.6 10.0
17.11.2013 22:29:19 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.6 10.0
17.11.2013 22:19:19 221.7 223.2 230.4 3.71 7.0 60.05 100.0 217.0 29.6 10.0
17.11.2013 22:09:19 221.7 223.2 231.6 3.71 7.0 60.02 100.0 217.0 29.6 10.0
17.11.2013 21:59:19 221.7 223.2 230.4 3.71 7.0 60.04 100.0 217.0 29.6 10.0
17.11.2013 21:49:19 221.7 223.2 230.4 3.71 7.0 60.04 100.0 217.0 29.6 10.0
17.11.2013 21:39:19 221.7 223.2 231.6 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 21:29:19 221.7 223.2 230.4 3.71 7.0 60.02 100.0 217.0 29.6 10.0
17.11.2013 21:19:19 223.2 223.2 229.3 3.71 7.0 60.04 100.0 217.0 29.6 10.0
17.11.2013 21:09:19 221.7 223.2 230.4 3.71 7.0 60.02 100.0 217.0 29.6 10.0
17.11.2013 20:59:19 221.7 223.2 231.6 3.71 7.0 60.06 100.0 217.0 29.6 10.0
17.11.2013 20:49:19 221.7 223.2 230.4 3.71 7.0 60.05 100.0 217.0 29.6 10.0
17.11.2013 20:39:19 221.7 223.2 230.4 3.71 7.0 59.99 100.0 217.0 29.6 10.0
17.11.2013 20:29:19 221.7 223.2 230.4 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 20:19:19 220.3 221.7 229.3 3.71 7.0 59.95 100.0 217.0 29.6 10.0
17.11.2013 20:09:19 220.3 221.7 229.3 3.71 7.0 59.97 100.0 217.0 29.6 10.0
17.11.2013 19:59:19 220.3 221.7 229.3 3.71 7.0 59.99 100.0 217.0 29.6 10.0
17.11.2013 19:49:18 218.8 220.3 229.3 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 19:39:18 220.3 221.7 230.4 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 19:29:18 218.8 221.7 230.4 3.71 7.0 59.97 100.0 217.0 29.6 10.0
17.11.2013 19:19:18 220.3 221.7 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 19:09:18 220.3 221.7 231.6 3.71 7.0 59.98 100.0 217.0 29.6 10.0
17.11.2013 18:59:18 220.3 221.7 231.6 3.71 7.0 59.98 100.0 217.0 29.6 10.0
17.11.2013 18:49:18 220.3 221.7 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 18:39:18 220.3 221.7 231.6 3.39 7.0 59.98 100.0 217.0 29.6 11.0
17.11.2013 18:29:18 220.3 221.7 231.6 3.71 7.0 59.98 100.0 217.0 29.6 10.0
17.11.2013 18:19:18 220.3 221.7 230.4 3.71 7.0 60.04 100.0 217.0 29.1 10.0
17.11.2013 18:09:18 220.3 221.7 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 17:59:18 220.3 223.2 231.6 3.71 7.0 59.97 100.0 217.0 29.1 10.0
17.11.2013 17:49:18 221.7 221.7 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 17:39:18 220.3 221.7 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
17.11.2013 17:29:18 220.3 221.7 231.6 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 17:19:18 220.3 221.7 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 17:09:18 220.3 221.7 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 16:59:18 220.3 221.7 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 16:49:18 220.3 221.7 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 16:39:18 220.3 221.7 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 16:29:18 220.3 221.7 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 16:19:18 221.7 221.7 231.6 3.71 7.0 60.00 100.0 217.0 29.6 10.0
17.11.2013 16:09:18 221.7 223.2 231.6 3.71 7.0 60.02 100.0 217.0 29.6 10.0
17.11.2013 15:59:18 220.3 223.2 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 15:49:18 221.7 223.2 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 15:39:18 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 15:29:17 220.3 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.6 10.0
17.11.2013 15:19:17 220.3 221.7 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
17.11.2013 15:09:17 220.3 223.2 231.6 3.71 7.0 59.97 100.0 217.0 29.1 10.0
17.11.2013 14:59:17 221.7 223.2 231.6 3.71 7.0 60.04 100.0 217.0 29.6 10.0
17.11.2013 14:49:17 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 14:39:17 221.7 223.2 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 14:29:17 221.7 223.2 231.6 3.71 7.0 60.04 100.0 217.0 29.1 10.0
17.11.2013 14:19:17 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 14:09:17 220.3 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 13:59:17 220.3 223.2 231.6 3.71 7.0 60.05 100.0 217.0 29.1 10.0
17.11.2013 13:49:17 220.3 223.2 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 13:39:17 220.3 223.2 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 13:29:17 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 13:19:17 221.7 223.2 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 13:09:17 221.7 223.2 231.6 3.71 7.0 59.97 100.0 217.0 29.1 10.0
17.11.2013 12:59:17 221.7 223.2 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 12:49:17 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 12:39:17 221.7 223.2 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 12:29:17 221.7 223.2 231.6 3.71 7.0 60.04 100.0 217.0 29.1 10.0
17.11.2013 12:19:17 221.7 223.2 231.6 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 12:09:17 221.7 223.2 231.6 3.71 7.0 60.05 100.0 217.0 29.1 10.0
17.11.2013 11:59:17 221.7 223.2 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 11:49:17 220.3 223.2 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 11:39:16 221.7 223.2 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 11:29:16 221.7 223.2 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 11:19:16 221.7 223.2 231.6 3.71 7.0 60.05 100.0 217.0 29.1 10.0
17.11.2013 11:09:16 221.7 223.2 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 10:59:16 223.2 223.2 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 10:49:16 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 10:39:16 223.2 224.6 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 10:29:16 223.2 224.6 231.6 3.71 7.0 60.04 100.0 217.0 29.1 10.0
17.11.2013 10:19:16 223.2 224.6 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 10:09:16 223.2 224.6 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 09:59:16 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 09:49:16 224.6 224.6 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 09:39:16 224.6 224.6 231.6 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 09:29:16 223.2 224.6 231.6 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 09:19:16 224.6 224.6 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 09:09:16 224.6 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 08:59:16 223.2 224.6 231.6 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 08:49:16 224.6 226.0 231.6 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 08:39:16 224.6 226.0 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 08:29:16 224.6 226.0 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 08:19:16 224.6 226.0 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 08:09:16 224.6 226.0 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 07:59:16 226.0 226.0 231.6 3.71 7.0 60.03 100.0 217.0 29.1 10.0
17.11.2013 07:49:16 226.0 226.0 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 07:39:16 226.0 227.5 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 07:29:16 226.0 227.5 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 07:19:15 226.0 226.0 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 07:09:15 226.0 227.5 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 06:59:15 226.0 227.5 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 06:49:15 226.0 227.5 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 06:39:15 226.0 226.0 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 06:29:15 224.6 226.0 231.6 3.71 7.0 60.04 100.0 217.0 29.1 10.0
17.11.2013 06:19:15 224.6 226.0 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 06:09:15 223.2 224.6 231.6 3.71 7.0 59.97 100.0 217.0 29.1 10.0
17.11.2013 05:59:15 224.6 226.0 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 05:49:15 224.6 224.6 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 05:39:15 224.6 224.6 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 05:29:15 224.6 226.0 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 05:19:15 224.6 226.0 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 05:09:15 224.6 226.0 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 04:59:15 223.2 224.6 230.4 3.71 7.0 60.04 100.0 217.0 29.1 10.0
17.11.2013 04:49:15 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 04:39:15 223.2 224.6 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 04:29:15 223.2 224.6 230.4 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 04:19:15 223.2 224.6 231.6 3.71 7.0 59.97 100.0 217.0 29.1 11.0
17.11.2013 04:09:15 223.2 224.6 230.4 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 03:59:15 223.2 224.6 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 03:49:15 223.2 224.6 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 03:39:14 223.2 224.6 230.4 3.71 7.0 59.96 100.0 217.0 29.1 10.0
17.11.2013 03:29:14 223.2 224.6 231.6 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 03:19:14 223.2 224.6 230.4 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 03:09:14 223.2 224.6 230.4 3.71 7.0 60.04 100.0 217.0 29.1 10.0
17.11.2013 02:59:14 223.2 224.6 230.4 3.71 7.0 59.97 100.0 217.0 29.1 10.0
17.11.2013 02:49:14 223.2 224.6 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 02:39:14 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 02:29:14 223.2 224.6 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 02:19:14 223.2 224.6 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 02:09:14 223.2 224.6 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
17.11.2013 01:59:14 223.2 226.0 231.6 3.71 7.0 60.02 100.0 217.0 29.1 10.0
17.11.2013 01:49:14 224.6 226.0 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 01:39:14 224.6 226.0 230.4 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 01:29:14 224.6 224.6 231.6 3.71 7.0 60.01 100.0 217.0 29.1 10.0
17.11.2013 01:19:14 224.6 224.6 230.4 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 01:09:14 224.6 224.6 230.4 3.71 7.0 59.97 100.0 217.0 29.1 10.0
17.11.2013 00:59:14 224.6 224.6 230.4 3.71 7.0 59.99 100.0 217.0 29.1 10.0
17.11.2013 00:49:14 223.2 224.6 230.4 3.71 7.0 59.97 100.0 217.0 29.1 10.0
17.11.2013 00:39:14 223.2 224.6 230.4 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 00:29:14 223.2 224.6 230.4 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 00:19:14 224.6 226.0 230.4 3.71 7.0 59.98 100.0 217.0 29.1 10.0
17.11.2013 00:09:14 224.6 224.6 230.4 3.71 7.0 59.96 100.0 217.0 29.1 10.0
16.11.2013 23:59:14 224.6 226.0 230.4 3.71 7.0 59.97 100.0 217.0 29.1 10.0
16.11.2013 23:49:13 224.6 226.0 230.4 3.71 7.0 60.02 100.0 217.0 29.1 10.0
16.11.2013 23:39:13 224.6 226.0 230.4 3.71 7.0 60.01 100.0 217.0 29.1 10.0
16.11.2013 23:29:13 224.6 224.6 230.4 3.71 7.0 59.97 100.0 217.0 29.1 10.0
16.11.2013 23:19:13 224.6 226.0 230.4 3.71 7.0 60.02 100.0 217.0 29.1 10.0
16.11.2013 23:09:13 223.2 224.6 231.6 3.71 7.0 60.04 100.0 217.0 29.1 10.0
16.11.2013 22:59:13 223.2 224.6 231.6 3.71 7.0 60.00 100.0 217.0 29.1 10.0
16.11.2013 22:49:13 223.2 224.6 231.6 3.71 7.0 59.97 100.0 217.0 29.1 10.0
16.11.2013 22:39:13 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 29.1 10.0
16.11.2013 22:29:13 223.2 224.6 231.6 3.71 7.0 59.99 100.0 217.0 29.6 10.0
16.11.2013 22:19:13 223.2 224.6 231.6 3.71 7.0 59.94 100.0 217.0 29.6 10.0
16.11.2013 22:09:13 223.2 224.6 231.6 3.71 7.0 59.98 100.0 217.0 30.2 10.0
16.11.2013 21:59:13 223.2 224.6 231.6 3.71 7.0 60.01 100.0 217.0 29.6 10.0
16.11.2013 21:49:13 0.0 226.0 230.4 3.71 7.0 60.03 96.0 217.0 28.5 10.0
16.11.2013 21:39:13 223.2 224.6 230.4 3.71 7.0 60.06 100.0 217.0 28.0 10.0
16.11.2013 21:29:13 224.6 227.5 230.4 3.71 7.0 60.03 100.0 217.0 28.0 10.0
16.11.2013 21:19:13 224.6 226.0 231.6 3.71 7.0 60.03 100.0 217.0 28.0 10.0
16.11.2013 21:09:13 224.6 226.0 231.6 3.71 7.0 59.99 100.0 217.0 28.0 10.0
16.11.2013 20:59:13 224.6 226.0 230.4 3.71 7.0 60.02 100.0 217.0 28.0 10.0
16.11.2013 20:49:13 224.6 226.0 230.4 3.71 7.0 60.03 100.0 217.0 28.0 10.0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-12 04:40 AM
So on 16.11.2013 21:49:13 you had a loss of input voltage according to the data log. That is the last time the UPS transferred for a power event and why it said for the last transfer reason (to battery) of Detection of low utility voltage. This is just informational incase you wanted to know.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document