Disabling charge circuit

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Disabling charge circuit
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
10
4177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-12 04:40 AM

Disabling charge circuit

I Am using a 5000 unit as an inverter in my pv array system. I use a outback 80 as the battery charge controller for my battery banks. I would like to disable the charging circuit in the ups. Can anyone assist?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
4170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

You are still going to require standby battery charger, otherwise, how do you maintain proper float voltage of the 48 v battery string when there is no solar input (night time, cloudy days for long periods) ?  Disabling the charging circuits in a smart-ups requires schematic ( proprietary ) and extensive understanding of UPS design ....you are likely better off just buying a standalone inverter ?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

Based on  my understanding of the internals of APC smart-ups, what you are asking is impossible. The inverter/charging circuits are tightly integrated under the control of not only one very complex ASIC (application specific integrated circuit) called the "Bridge Charger" ( This ASIC controls pretty much everything that goes on in that functional block of the UPS...controlling the inverter, regulating the charging hi/lo, etc), but furthermore the Bridge Charger is in turn controlled by the main UPS microprocessor with associated DSP circuitry. You cannot simply separate out the charging function as one unit and defeat it. You are more likely to blow the ups up (and possibly yourself with it) if you try to mess with these circuits/architecture.

Save your pennies for a real inverter they can be had for around $500 or less based on ebay listings I just read.

10000w Peak 5000 Watts Pure Sine Wave Power Inverter DC 24V AC 220V 60Hz | eBay

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

I have to agree with Battman. On a line interactive SmartUPS, the inverter is the charger. You might be able to find logic signals that control charging behavior, but maybe not. Other people on this board have managed to change the float voltage.

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

It sounds like you want to use the UPS as a transfer switch (but NOT as a UPS) when you choose to use utility power, or as an inverter when you choose to use your solar array. Could this be accomplished by putting the UPS into bypass? I know bypass mode passes utility power directly to the UPS output and disconnects the inverter output, but does it also disable the charger circuit? Of course, if there was a failure of utility power, any connected load would loose power in this configuration, and I defer to others what you would need to do to execute a "cold start" to bring the inverter online when you disable utility power to use your "off-grid" source, or after being left in bypass when utility power went out. And I know the larger UPSs also have 2 methods for bypass, a manual (I believe "maintenance" or "static") bypass, and a UPS (software) controlled bypass. Someone correct me if I'm wrong, please! I don't know if your UPS has the manual bypass.

The other option would be an external (commercial) transfer switch which would permit you to select either raw utility power or the output of the UPS as a source for your load. In that configuration you would simply leave the utility input to the UPS disconnected and cold start the unit when desired.

Either way, your goal of having it timer controlled is a completely different can of worms!

As others have said, you've got an expensive unit (well ok, free to you!) and you only want to use about half it's functionality...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

I Am using a 5000 unit as an inverter in my pv array system. I use a outback 80 as the battery charge controller for my battery banks. I would like to disable the charging circuit in the ups. Can anyone assist?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

Can you clarify the exact model of the UPS? I believe the answer will be no but I'll have to verify depending on the model.

This is usually found on a white sticker on the back or bottom of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

It sounds like this user is referring to a Matrix 5000 ?  Perhaps he is connecting the solar panels up to the 48 volt Anderson battery connector at the rear and using the ups as an inverter by starting it up offline...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

Smart-UPS XL 5000 RM 7U 208V In 208/120V Out

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

SSolar panels connect to the outback charge controller. Charge controller connected to 48 v battery bank. Ups connected to Abattery bank through nderson connector.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

0 Likes
0
4169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:40 AM

USing ups as inverter continuos duty. When I activate220 v to ups it draws 400watt to charge battery. Charge battery not required from ups.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
4171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

You are still going to require standby battery charger, otherwise, how do you maintain proper float voltage of the 48 v battery string when there is no solar input (night time, cloudy days for long periods) ?  Disabling the charging circuits in a smart-ups requires schematic ( proprietary ) and extensive understanding of UPS design ....you are likely better off just buying a standalone inverter ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore