network access not working even though I can ping

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • network access not working even though I can ping
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
16
40325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

network access not working even though I can ping

I'm working with a an AP9618 card which was just installed in a 2200 XL UPS.

I can get in through the console and I configured the IP address. Now I can ping to the device and I can ping from it.

However, I can't access it via telnet, ssh, http, https. This is all within the same telnet so there's no firewall between me and the card. From my workstation, I can access other AP96xx cards on the network, no problem.

If I scan the device with nmap, it reports that all TCP ports are filtered. A UDP scan with nmap shows ports 161 and 33281 in an indeterminate state ("open|filtered").

Any ideas how I can get this thing functioning?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

Have you triple checked your subnet mask and default gateway settings between the computer you're at and the AP9618? I see this as a common problem when you can ping but not access. I also am thinking to verify the IP address is correct or that there is no IP conflict anywhere. If you pull the network cable, does the ping stop?

Another thing I thought of was if you had a proxy set up on your system somewhere that was forgetton.

Are the other cards on the same VLAN, LAN, etc as this AP9618?

If you're really sure you've ruled that out, you can also verify these services are actually enabled on the card or if they have been disabled or modified. To check web for example, log in via local console and go to Network-> Web/SSL/TLS and verify what is there to make sure someone didn't change it. You could paste it too here as well.

Another option is just to reset the card to defaults and try one more time. This option is under System->Tools I think and you could reset the card to defaults then make sure to press Esc until you get back to the main menu and press log out or else it won't work until your session times out if you don't actually "log out."

Hope that helps get you started!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

If FTP doesn't work, your last resort is to send the files Xmodem slow boat way from your hyperterminal connection into the card's console. ...it will take about 12 to 15 minutes per download even at the highest speed option (38,400). Good luck!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Yeah, I was thinking of trying a direct ethernet connection, so this morning I connected the card and a laptop to a microswitch. Seemed to work fine.

Then I connected both of them to the same network switch, and it stopped working again. I even tried mirroring the port on which the card is connected so I could monitor it with Wireshark. I can see the traffic being sent to the card, but the card doesn't respond to anything except ping.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Many years later, this thread is still helpful! I was having the exact same issue, where i could ping the UPS but no other services would work. Turns out someone forgot to put in the Default Gateway in the IP configuration. Once that was in, everything worked again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 16
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

I'm working with a an AP9618 card which was just installed in a 2200 XL UPS.

I can get in through the console and I configured the IP address. Now I can ping to the device and I can ping from it.

However, I can't access it via telnet, ssh, http, https. This is all within the same telnet so there's no firewall between me and the card. From my workstation, I can access other AP96xx cards on the network, no problem.

If I scan the device with nmap, it reports that all TCP ports are filtered. A UDP scan with nmap shows ports 161 and 33281 in an indeterminate state ("open|filtered").

Any ideas how I can get this thing functioning?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

Have you triple checked your subnet mask and default gateway settings between the computer you're at and the AP9618? I see this as a common problem when you can ping but not access. I also am thinking to verify the IP address is correct or that there is no IP conflict anywhere. If you pull the network cable, does the ping stop?

Another thing I thought of was if you had a proxy set up on your system somewhere that was forgetton.

Are the other cards on the same VLAN, LAN, etc as this AP9618?

If you're really sure you've ruled that out, you can also verify these services are actually enabled on the card or if they have been disabled or modified. To check web for example, log in via local console and go to Network-> Web/SSL/TLS and verify what is there to make sure someone didn't change it. You could paste it too here as well.

Another option is just to reset the card to defaults and try one more time. This option is under System->Tools I think and you could reset the card to defaults then make sure to press Esc until you get back to the main menu and press log out or else it won't work until your session times out if you don't actually "log out."

Hope that helps get you started!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

In addition to Angela N's most excellent recommendations/advice, you should/could also check to make sure your card's firmware is at the latest revision, which is AOS 3.7.3 / SUMX 3.7.2 given that this is for a Smart-UPS. If its really old / outdated that could cause issues! ...Good luck!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:12 AM . Last Modified: ‎2024-03-12 04:39 AM

Thanks for responding. Yes, I checked all that. I can observe ping traffic using Wireshark, and then the other (failing) traffic, and verify that the MAC address matches that of the device. The other cards are on the same VLAN.

Just tried a reset to defaults, didn't help.

I just had a chat with a support person who told me that I should remove the card and do something called a "Brain Dead Test", then reinsert the card. This will entail shutting down the UPS so it's going to have to wait until scheduled downtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Thanks, Battman. I just stepped away from where I was doing the serial console connection, but the Quality & Assurance slip taped to the outside of the anti-static bag in which the card was packed does say that the FW revision is AOS 3.7.3 / SUMX 3.7.2.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Not sure I've ever heard that brain-deading a UPS made any difference to the network card, but worth a try. Another thing you can do is re-flash the card, as I've seen corruption rear its ugly head once in awhile. You can get the .exe file for the aos/sumx combo from APC and either ftp the files in one at a time, (starting with the AOS) or use the upgrade wizard.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Ah, that sounds promising. Is that what I need: "Network Management Card v3.7.2 Firmware for Smart-UPS with AP9617/8/9"? (Even though it only says 3.7.2 and doesn't mention 3.7.3?)

I tried downloading the utility and running it. But it looks like it only works over IP! When I ran it, it said

Checking network connection ... OK

Testing login ... Login failed

And the result.txt file has:

Using AOS file    : AOS = apc_hw02_aos_373.bin

Using Application file: APP = apc_hw02_sumx_372.bin

Checking network connection ...  ERROR!!! Login unsuccessful.

Not all Network Management Cards were upgraded successfully:

    10.0.4.69: Could not log into the Management Card's FTP server.

Encountered 1 failures during upgrade.


I guess I can go back to the serial connection and see if I can try to enable the FTP server.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Well, FTP server was already enabled. While connected to the serial connection, I did verify the firmware numbers and they are the latest.

I tried turning on https and ssh, instead of http and telnet, but I still can't access the card over the network.

It was interesting, when I turned on https, I got a couple screens to accept, ending with "Type yes to accept or enter to cancel." I hit enter by mistake, but the next screen still showed Accepted.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

If FTP doesn't work, your last resort is to send the files Xmodem slow boat way from your hyperterminal connection into the card's console. ...it will take about 12 to 15 minutes per download even at the highest speed option (38,400). Good luck!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Ah, the two .bin files?

I might try  that. First I'll have to get my hands on HyperTerminal or something else that supports Xmodem for Win7 (doesn't seem to be available in PuTTy).

How do I send both files? I played with the Xmodem option in the card and it looked like it only takes a single download then reboots.

There's another card on my desk, a 9630, which was believed to be defective prior to when I came on board. I wonder if it had the same symptoms; that might point to the UPS after all, and maybe a "brain dead test" will be the answer.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

A braindead only resets the UPS communications and I also agree with Battman that this is a useless step in troubleshooting network connectivity with the Network Management Card. I would skip that and lets move on.

Can you try a direct connection from a computer to this card via a crossover cable?

I don't think firmware is the issue if you're able to log in via serial.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Yeah, I was thinking of trying a direct ethernet connection, so this morning I connected the card and a laptop to a microswitch. Seemed to work fine.

Then I connected both of them to the same network switch, and it stopped working again. I even tried mirroring the port on which the card is connected so I could monitor it with Wireshark. I can see the traffic being sent to the card, but the card doesn't respond to anything except ping.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

I thought maybe it was an issue with the connection to the network switch (maybe the automatic port config or something) so I tried branching off the network switch to the microswitch and then connected the card from there. Didn't work.

So I connected the laptop to the microswitch to at least see if things would keep working within the microswitch. Didn't work.

So then I broke the connection between the microswitch and the network switch. I.e., restoring the test configuration from my previous post. And it still didn't work.

So now I think I may have just gotten lucky that time.

Since you all think that a braindead won't help, any idea what I need to do to reach a tech who will help me without requiring me to jump through pointless hoops?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Hi Elliot,

If you have some time today, I can work with you..I am on eastern time.

I'll send you an email.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Hey, thanks to Angela N. for finding some time to go over this with me on the phone.

It turns out that it was a network config issue after all! I'd set the card to use netmask 255.255.255.252 when it should have been 255.255.252.0.

The inconsistent results in later tests were undoubtedly because I wasn't always using the same IP address on the laptop that I was using to test--sometimes it was in the same /30 subnet as the card, sometimes it wasn't.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

0 Likes
0
40301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 AM . Last Modified: ‎2024-03-12 04:39 AM

Many years later, this thread is still helpful! I was having the exact same issue, where i could ping the UPS but no other services would work. Turns out someone forgot to put in the Default Gateway in the IP configuration. Once that was in, everything worked again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore