LX 16000 Battery System Status shows 2 new batteries "Vacant"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • LX 16000 Battery System Status shows 2 new batteries "Vacant"
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-12 07:47 AM

0 Likes
6
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-12 07:47 AM

LX 16000 Battery System Status shows 2 new batteries "Vacant"

Added two additional (total of 4) new APC batteries last fall to increase run time but they show as vacant.  Any help would be appreciated.

 -

 
Battery System Status
 
Battery Capacity: 100.0 %
Runtime Remaining: 15min
Nominal Battery Voltage: 120.0 VDC
Actual Battery Bus Voltage: 137.3 VDC
Battery Frame Status
Frame Status Bad Good Total Vacant
Main  OK 0 2 2 2
Total   0 2 2 2

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

Thanks again Richard. So, I did some additional testing and it seems that even if I take a known good battery with the DC switch enabled and move it to a "vacant" battery slot it does not show up. 

I went ahead and ordered new management modules.  They will be here next week and I will have them installed.  I will report back when they are installed.

Thanks.

John

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

Hi John,

 

I would refer to forum

http://forums.apc.com/spaces/8/data-center-facility-3-phase-ups/forums/general/7699/apc-ups-symmetra...

 

Kindest Regards,

Rich…

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

Thanks for the response Richard but I had seen that thread and the only suggested solution I see in there is resetting the MIM, although this didn't full resolve the users problem.

Am I missing something?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

Hi John,

 

Referring to out FAQ FA158934 What is the expected life of my APC UPS battery?

Storage: Do not store APC batteries for extended periods of time. New batteries/units should be stored for no more than 6 months from date of purchase, as they ship from the factory at approximately 80% charge. After this period, the battery should be used or it will lose a great deal of its charge . It is not advisable to store batteries that have already been in use. Extended storage without periodic charging can result in shortened life expectancy and erratic battery performance.

Temperature also plays a large part in battery degradation during storage:

  • If the ambient temperature during storage is - 15°C to + 30°C (+ 5°F to + 86°F), perform a full recharge cycle at least every six months.
  • In environments where the ambient temperature is + 30°C to + 45°C (+ 86°F to + 113°F), perform a full recharge cycle at least every three months.

 

If you are seeing vacant. The UPS is not detecting the battery module. If it’s been this was since last year, I would question the quality of the battery.

Is there a possibility the batteries could have been without charge for long periods of time before they were installed in the UPS?

When you originally purchased the batteries and installed them, did you see the increase of batteries in the UPS battery status page?

Is the DC switch on the front of the new battery closed?

Have they ever been seen to be working correctly?

 

Kindest Regards,

Rich…

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

Thanks again Richard.  We ordered brand new batteries to replace the existing batteries in the chassis.  The original chassis had 3 batteries, we purchased 4 brand new batteries and installed them as part of a preventive maintenance program.  The batteries were purchased brand new from CDW and were delivered in late November 2017 and installed the first week of December 2017.  I do not think that they sat very long.

Upon initial installation of the batteries only two of the four showed up.  The other two show as vacant and have never been working correctly.

We only have two power modules, they are installed in bays 3 & 5. 

The two batteries that are functioning are in bays 1 & 3.

All self tests are successful.

I will pull the vacant batteries today and see if the DC switch is closed.  I am not sure what that is but I will take a look and report back.

Is there a non disruptive procedure for resetting the MIM?

John

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

Hi John,

 

The DC switch can be found on the front of the battery. It is a black plastic button that allows the DC to be connected / disconnected. It is advised to disconnect the DC to the battery before its insertion and removal, then connect the DC when the battery is installed and ready to go.

 

Kind Regards,

Rich…

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:42 AM

Thanks again Richard. So, I did some additional testing and it seems that even if I take a known good battery with the DC switch enabled and move it to a "vacant" battery slot it does not show up. 

I went ahead and ordered new management modules.  They will be here next week and I will have them installed.  I will report back when they are installed.

Thanks.

John

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of