No LEDs are burning on the SURTD3000XLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • No LEDs are burning on the SURTD3000XLI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:44 AM

0 Likes
6
1771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:44 AM

No LEDs are burning on the SURTD3000XLI

Dear,
I recently received an SURTD3000XLI. This UPS was not used for around 8 months. During that time it was not connected to the main power supply. The problem I am facing with is that the UPS doesn't work. If I connect the UPS to the main power supply I can hear the fan and serveral relays but the power outlet is not active. Also the LEDs on the front are not burning. My first thought was that the batteries where dead but I am not sure about that.
I connected the UPS to Hyper Terminal and I get the following response:
-------------------------------------------------------------------------------
American Power Conversion               (c) Copyright 2006 All Rights Reserved
Firmware Revision: 5.1
-------------------------------------------------------------------------------
Model   : Smart-UPS RT 3000 XL
Manufacture Date  : 6/4/2015    Serial Number           : REMOVED
                                Battery Replacement Date: 6/4/2015
Battery Run Time  : 18:12 (h:m) # Internal Battery Packs: 1
Remaining Capacity: 100.0%      # External Battery Packs: 0
Battery Voltage   : 218.4 V     Output Voltage          : 0.00 VAC
Battery Temperature: 21.50 C    Output Frequency        : 0.00 Hz
                                Output Current          : 0.00 Amps
Input Voltage     : 235.1 VAC   Load in Watts           : 0.00%, 0.00 Watts
Input Frequency   : 50.00 Hz    Load in VA              : 0.00%, 0.00 VA
-------- Control And Configuration Console ------------------------------------
        1- UPS Settings
        2- Start/Stop Run Time Calibration
        3- Firmware Upgrade
        4- Factory Data
        - Logout, - Refresh
>
As far as I can see there is nothing wrong with the battery.
If I press 4 (Factory Data) I get the following:
-------------------------------------------------------------------------------
        Factory Data
-------------------------------------------------------------------------------
Faults: 0001 0001 0001 0000
Status: 0010 0010 0010 0010 0030 0010 0010 0010
Cause:  0000 0000 0000 0011 0010 0000 0000 0000
BSE: 0000 PSE: 0000 GE: 0000 LCEC: 0000 MEC: DD60
VINV: 1.82 DCPV: 394.9 DCNV: 394.8
PVINP: 325.1 PVINN: -325.9 PVREFP: 323.7 PVREFN: 322.2
CHGV: 218.2 CSP: 218.3 SCTRL: 0000 BHLTH: 0106
RBTS: 0000 RTCC: 0001 IS: 0001 BIS: 0001
PCBSN: REMOVED
TOT: 1E1A TBYT: 0000 TBAT: 0000085F NOBAT: 001B
Does somebody know if this shows the problem?
I also used PowerChute to get a status from the UPS (See attachment). There I can see that the UPS status is:off but I can't see any reasons why and I don't know how to turn it on.
I hope somebody can tell me what is going on here. Thanks in advance.
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

0 Likes
0
1771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

Before you invest in the $$ for batts.  Try these two things.

(maybe one tray is bad)  Pull the brown battery disconnects out and usse a multimeter and measure each of the two trays.  Both should be above 90vDC. 

(maybe controller ribbon damaged)  See if you can get a network management card.  You can control the unit through that.  If not, check the fragile ribbon and the display connections.  Finally try the rubber button.   If any of these things was loose or damaged, you would get nothing as well.  

And as a final thought.  APC Troubleshooting manual says to try to cold start the unit.

1) Turn off and unplug the Smart-UPS from wall. Remove any attached load.
2) Press and hold the power button (labeled ""I/TEST"" on legacy non-LCD screen units) on the front of the UPS until you hear a LONG beep.
3) Let go DURING the long beep. If you let go after the beep ends you will need to try again.
4) UPS should go through its' normal self test and end up on battery with 4 beeps every 30 seconds. This shows that the UPS is functioning correctly and can both pass a self test and function on battery.
5) You can now plug your UPS back into the wall. If the input power is acceptable the UPS will transfer back online.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:43 AM

0 Likes
0
1771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:43 AM

Hi Rick,

Just to make sure, after plugging the UPS to the wall outlet, did you press the "Test/I" button? This is also the "ON" button of the UPS to turn it on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:43 AM

0 Likes
0
1771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:43 AM

Hi Mike,

Thanks for your response.

Yes I did but nothing happens. If I press the "Off" button I hear a beep but nothing happens. I forgot the attachment in my previous post so I added it to this one.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

0 Likes
0
1770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

Hi Rick,

Basing on the info, this UPS was manufactured in 2015. If the batteries were never replaced, it is possible that it is not supplying the proper juice to the UPS' dc bus because of its age. Typically, APC batteries have a 3-5 yr life span. SURT models, require good working batteries for them to even turn on. If you want to further troubleshoot this UPS, you may want to get new batteries (Part Number APCRBC140). 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

0 Likes
0
1773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

Hi Mike,
Ok, then I will buy a new battery. I've have got this advice now multiple times. Thanks for helping.

Reply

Link copied. Please paste this link to share this article on your social media post.

chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

0 Likes
0
1772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

Before you invest in the $$ for batts.  Try these two things.

(maybe one tray is bad)  Pull the brown battery disconnects out and usse a multimeter and measure each of the two trays.  Both should be above 90vDC. 

(maybe controller ribbon damaged)  See if you can get a network management card.  You can control the unit through that.  If not, check the fragile ribbon and the display connections.  Finally try the rubber button.   If any of these things was loose or damaged, you would get nothing as well.  

And as a final thought.  APC Troubleshooting manual says to try to cold start the unit.

1) Turn off and unplug the Smart-UPS from wall. Remove any attached load.
2) Press and hold the power button (labeled ""I/TEST"" on legacy non-LCD screen units) on the front of the UPS until you hear a LONG beep.
3) Let go DURING the long beep. If you let go after the beep ends you will need to try again.
4) UPS should go through its' normal self test and end up on battery with 4 beeps every 30 seconds. This shows that the UPS is functioning correctly and can both pass a self test and function on battery.
5) You can now plug your UPS back into the wall. If the input power is acceptable the UPS will transfer back online.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

0 Likes
0
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:57 PM . Last Modified: ‎2024-03-07 01:43 AM

Hi Bob,

I ordered a network card. Now I was simply be able to turn on the UPS!

Many thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore