Just one SMX1500RM2UNC isn't recording ambient into data log; universal IO sees sensor just fine?
Hi everyone,
Just one SMX1500RM2UNC isn't recording ambient into data log; universal IO sees sensor just fine? I have many other units, identical model and AP firmware and they record it just fine. This one - the column is blank? All run the latest firmware 6.5.0 and have identical AP9631
Any ideas? Rebooted the AP many times in a hope to kick start it - no go, still T1ambC is blank?
JbwJUlzQm9zpPjGs1jmgug%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:20 AM . Last Modified: 2024-03-11 04:09 AM
Mike Thanks Mike, I did absolutely nothing and when I checked just now it has started working. Wierd...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:20 AM . Last Modified: 2024-03-11 04:09 AM
Hi Boyan,
Is this the temp probe that came with the NMC?
Could you also verify the UPS fw version. You can find this under About > UPS.
A few steps that you can try:
1. Try to move the temp probe to a diff IO port then reboot the NMC after moving.
2. Format the card to factory setting but leave the IP. This can be found under Control > Network > Reset/Reboot > Reset All (put a check on Exclude TCP/IP)
3. Try a different temp probe.
4. Try to move the NMC to a different UPS and see if issue follows.
5. Try to move the temp probe to a diff UPS and see if the issue follows.
If everything else fails, you may want to call tech support for further diagnosis and potential replacements if under warranty.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:20 AM . Last Modified: 2024-03-11 04:09 AM
Mike Thanks Mike, I did absolutely nothing and when I checked just now it has started working. Wierd...