APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Here is my configuration:
1 x Smart-UPS + NMC
2 x VMware ESX servers with PCNSs
1 x Win2k3 with VMware Virtual Center and PCNS installed
2 x NetApp filers with storage enclosures
ESX servers depends on NetApp storage. NetApp supports UPSs in the way when it sees that x minutes remaining on battery life it initiates shutdown.
I need to shut down all this hardware (and UPS too) immediately after "on battery" event to prevent overheating due to air-conditioners shut off. Here is how I see it:
1. Initiate ESX servers shutdown immediately after on battery event.
2. Empirically calculate remaining UPS uptime after ESXs shutdown (t1). Set this time - 2 minutes at NetApp as shutdown trigger (t2).
3. Set (t1 + 2 (for safety) + 2 (NetApp shutdown) + 2(for safety)) (t3) as shutdown delay in Win2k3 PCNS and also set here to shut down UPS after OS shutdown.
It is approximately 10-12 minutes in total.
The main problem in this scenario is that t2 is difficult to calculate. I see that runtime remining (RR) now is 29 minutes. I heard that RR is slightly different when online and immediately after power failure. Also battery life time will be increased after ESXs shutdown. Skew in t2 also produces skew in t3. And finally I should always recalculate this time when I add new hardware, or load on existing hardware is increased.
Is there any more simple and robust way to do this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:24 AM . Last Modified: 2024-03-07 11:06 PM
Hi,
Let me first apologize. I do not posess the knowledge about your setup of servers with data storage seperate to be able to fully assist you in this manner. That is why my recommendations are so skewed.
As far as your last question, if a shutdown is initiated and power returns to the UPS, it will continue with the shutdown, then reboot itself and bring everything back up (the catch-22 there is if the bios and power supplies are configured to power up upon having power restored to them).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Vasiliy,
I apologize for the turnaround in receiving a response from someone here on the boards. While it seems you have quite the complicated scenarion on your hands, I did want to have one statement clarified before recommending anything.
You had stated you wanted all of your equipment, UPS included, to power down IMMEDIATELY after a UPS: On Battery event has started. However, you then go into runtime calculations of over 30 minutes to keep some equipment that was mentioned as part of "all equipment" online. If you're worried about overheating since the Cooling units go off, why would you continue to run equipment that's going to generate excess heat back into the room around the products? That seems to contradict what you're trying to accomplish.
Any clarification would be appreciated.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Unfortunately, to myself, it seems like a "skew" that is unavoidable. I cant think of another way to do this personally other than calculating and testing 😕
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:07 PM
I still hope to see any recommendations from The Notorious K... 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:06 PM
Sorry that you were expecting a reply from me. Angela jumped in on this and I thought that she provided good enough information to relay.
As I stated before, there's only a Tier 1 shutdown available for PCNS and UPS. Outside of command files, there's no way to do any other types of shutdowns, and all of these would have to be tested in your scenario, which is dealing with a non-linear load, so the calculations that you get the first time, may not be the same the second, third or fourth.
I apologize that there's no easy solution for this. But the APC Software doesn't really go beyond a Tier 1 setup.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:06 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:06 PM
Thanks for your reply Kevin.
But your answer is totally unclear for me.
there's only a Tier 1 shutdown available for PCNS and UPS
So firstly what do you mean 'Tier 1' here? Tier 1 = servers? Tier 2 = storage?
Secondly I think that term 'tier' is not appropriate here. UPS and PCNS don't deal with tiers at all. They deal only with configurable delays and appliances where PCNS is set up. If you mean that I can't shutdown storage from PCNS, surely I know it.
Outside of command files, there's no way to do any other types of shutdowns
Do you mean with this phrase that the only way for me is to write a command file on ESX servers to shutdown storage?
But the most confusing thing for me is: *"Why there is no standart solution for this scenario when almost all mid-range to high-end datacenter designs apply storage?"* What do they do? Hire night technician?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:06 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:06 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:06 PM
As for why there's no standard? I'm not sure. But because the software can only shutdown an OS, I believe that's why we made the command file an available option.
Maybe I understood something wrong but command file is not an option in my situation. ESX server interact with storage even if all VMs are shut down. AFAIK script executes before initiating OS (ESX in my case) shutdown. So if I'll execute script which should shut down storage before storage is logically detached from ESX (I suppose it occurs at some of the last steps of OS shutdown sequence) I'll face data corruption.
So the only way is to implemet custom shell script and insert it at the end of ESX shutdown process. Could you confirm or deny my assumption?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:06 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:23 AM . Last Modified: 2024-03-07 11:06 PM
OMG, I suppose I have invented a solution.
1. On battery event occured. Start ESXs shutdown with 1 min delay for example (to prevent shutdown in the case of short power outages). At the end of each ESX shutdown sequence initiate corresponding storage shutdown (ESX 1 shuts down Storage 1, ESX 2 shuts down Storage 2). Disappearance of Storage 2 to ESX 1 (and vice versa) is not a problem 'cause storage is in active/active cluster. I mentioned it before.
2. The main poin here is not to shutdown management server immediately. I can shut down it after UPS battery is totally exhausted. There is nothing really hot there in contrast with storage enclosures. So I don't need to calculate all these 'one delay plus another and so on'. When battery is exhausted I shut down management server + UPS.
But there is another problem. What if power is restored after servers and storage is shut down but before management server becomes down? I suppose that management server shutdown is canceled but storage and servers left in down condition.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:24 AM . Last Modified: 2024-03-07 11:06 PM
Hi,
Let me first apologize. I do not posess the knowledge about your setup of servers with data storage seperate to be able to fully assist you in this manner. That is why my recommendations are so skewed.
As far as your last question, if a shutdown is initiated and power returns to the UPS, it will continue with the shutdown, then reboot itself and bring everything back up (the catch-22 there is if the bios and power supplies are configured to power up upon having power restored to them).