Issues with AP9630 and PCNS 2.2.4

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Issues with AP9630 and PCNS 2.2.4
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:56 PM . Last Modified: ‎2024-03-07 02:17 AM

0 Likes
1
774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:56 PM . Last Modified: ‎2024-03-07 02:17 AM

Issues with AP9630 and PCNS 2.2.4

I thought I might save someone some trouble by reporting my experience installing this card and software under Windows 2000 Server for the first time.

The documentation supplied with the card is incomplete. In particular, there is a vague reference to "turning off ac and dc power" before installation, with no mention about just how to do that. It took a kbase search to finally find the procedure to turn off dc power.

In my configuration, the Device IP Wizard was unable to find the NMC2 card. I tried it from Windows XP and Windows 2000 Server. After reading this forum, I'm thinking that it is possible that the issue is that cards are now being shipped with the IP method set to Manual, so the new card comes up with no IP address. Hard to know, but the procedures in the docs caused me a lot of frustration. I finally configured the card with the supplied serial link and could finally access it from a web browser.

PCNS 2.2.4 - I spent the better part of two days getting this to work and the nicest thing I have to say is that the installation program is fairly decent. The software as installed never worked - never. I tried several of my servers and had identical results on all of them. The symptom was that the login screen would come up, I'd put in the user name and password, hit login and get the login screen again. Yes, I had the user name and password correct and they matched the login data on the card. I got no help from "support" on this issue.

After poking around in the PCNS program files directory, I found the EventLog.txt file and realized that the PCNS service was connecting to the card just fine. I also found gui.cmd and gui.std. Gui.std lauches the java app using http on port 3052 where gui.cmd usess https on port 6547. Changing gui.cmd to look like gui.std finally made the app login properly. I've no dea why this fixes things, some stupid java-thing I guess.

Beyond that, I had the same confusion as several others on this forum aobut just what the heck the shutdown setup settings really do. I'm still not clear about the delay settings on the card vs the ones in PCNS. Based on what I've seen on the forum and what I've seen in the documentation, I'm still not sure how all of that stuff works. It's pretty clear to me from my tests that the "on battery" event gets sent from the UPS to PCNS right away.

The main thing that really got me in trouble is the default setting in the PCNS Configure Shutdown menu of "Shutdown the UPS after the shutdown finishes". The default is that is checked (shutdown the UPS). This got me in real trouble during my testing since there are several servers on this UPS. I was trying to see if the server where I had PCNS installed would really shutdown. I set the PCNS shutdown time delay to a minute or so and pulled the plug on the UPS for a few minutes, then plugged it back in. Sure enough, the test server shutdown. I never expected the entire UPS to shutdown a short time later taking the other servers down. I'm now VERY careful about that check-box!

I'd appreciate hearing from anyone else, especially someone who can explain the port 6547 vs 3052 thing.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:56 PM . Last Modified: ‎2024-03-07 02:17 AM

0 Likes
0
774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:56 PM . Last Modified: ‎2024-03-07 02:17 AM

I thought I might save someone some trouble by reporting my experience installing this card and software under Windows 2000 Server for the first time.

The documentation supplied with the card is incomplete. In particular, there is a vague reference to "turning off ac and dc power" before installation, with no mention about just how to do that. It took a kbase search to finally find the procedure to turn off dc power.

In my configuration, the Device IP Wizard was unable to find the NMC2 card. I tried it from Windows XP and Windows 2000 Server. After reading this forum, I'm thinking that it is possible that the issue is that cards are now being shipped with the IP method set to Manual, so the new card comes up with no IP address. Hard to know, but the procedures in the docs caused me a lot of frustration. I finally configured the card with the supplied serial link and could finally access it from a web browser.

PCNS 2.2.4 - I spent the better part of two days getting this to work and the nicest thing I have to say is that the installation program is fairly decent. The software as installed never worked - never. I tried several of my servers and had identical results on all of them. The symptom was that the login screen would come up, I'd put in the user name and password, hit login and get the login screen again. Yes, I had the user name and password correct and they matched the login data on the card. I got no help from "support" on this issue.

After poking around in the PCNS program files directory, I found the EventLog.txt file and realized that the PCNS service was connecting to the card just fine. I also found gui.cmd and gui.std. Gui.std lauches the java app using http on port 3052 where gui.cmd usess https on port 6547. Changing gui.cmd to look like gui.std finally made the app login properly. I've no dea why this fixes things, some stupid java-thing I guess.

Beyond that, I had the same confusion as several others on this forum aobut just what the heck the shutdown setup settings really do. I'm still not clear about the delay settings on the card vs the ones in PCNS. Based on what I've seen on the forum and what I've seen in the documentation, I'm still not sure how all of that stuff works. It's pretty clear to me from my tests that the "on battery" event gets sent from the UPS to PCNS right away.

The main thing that really got me in trouble is the default setting in the PCNS Configure Shutdown menu of "Shutdown the UPS after the shutdown finishes". The default is that is checked (shutdown the UPS). This got me in real trouble during my testing since there are several servers on this UPS. I was trying to see if the server where I had PCNS installed would really shutdown. I set the PCNS shutdown time delay to a minute or so and pulled the plug on the UPS for a few minutes, then plugged it back in. Sure enough, the test server shutdown. I never expected the entire UPS to shutdown a short time later taking the other servers down. I'm now VERY careful about that check-box!

I'd appreciate hearing from anyone else, especially someone who can explain the port 6547 vs 3052 thing.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:56 PM . Last Modified: ‎2024-03-07 02:17 AM

0 Likes
0
775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:56 PM . Last Modified: ‎2024-03-07 02:17 AM

I thought I might save someone some trouble by reporting my experience installing this card and software under Windows 2000 Server for the first time.

The documentation supplied with the card is incomplete. In particular, there is a vague reference to "turning off ac and dc power" before installation, with no mention about just how to do that. It took a kbase search to finally find the procedure to turn off dc power.

In my configuration, the Device IP Wizard was unable to find the NMC2 card. I tried it from Windows XP and Windows 2000 Server. After reading this forum, I'm thinking that it is possible that the issue is that cards are now being shipped with the IP method set to Manual, so the new card comes up with no IP address. Hard to know, but the procedures in the docs caused me a lot of frustration. I finally configured the card with the supplied serial link and could finally access it from a web browser.

PCNS 2.2.4 - I spent the better part of two days getting this to work and the nicest thing I have to say is that the installation program is fairly decent. The software as installed never worked - never. I tried several of my servers and had identical results on all of them. The symptom was that the login screen would come up, I'd put in the user name and password, hit login and get the login screen again. Yes, I had the user name and password correct and they matched the login data on the card. I got no help from "support" on this issue.

After poking around in the PCNS program files directory, I found the EventLog.txt file and realized that the PCNS service was connecting to the card just fine. I also found gui.cmd and gui.std. Gui.std lauches the java app using http on port 3052 where gui.cmd usess https on port 6547. Changing gui.cmd to look like gui.std finally made the app login properly. I've no dea why this fixes things, some stupid java-thing I guess.

Beyond that, I had the same confusion as several others on this forum aobut just what the heck the shutdown setup settings really do. I'm still not clear about the delay settings on the card vs the ones in PCNS. Based on what I've seen on the forum and what I've seen in the documentation, I'm still not sure how all of that stuff works. It's pretty clear to me from my tests that the "on battery" event gets sent from the UPS to PCNS right away.

The main thing that really got me in trouble is the default setting in the PCNS Configure Shutdown menu of "Shutdown the UPS after the shutdown finishes". The default is that is checked (shutdown the UPS). This got me in real trouble during my testing since there are several servers on this UPS. I was trying to see if the server where I had PCNS installed would really shutdown. I set the PCNS shutdown time delay to a minute or so and pulled the plug on the UPS for a few minutes, then plugged it back in. Sure enough, the test server shutdown. I never expected the entire UPS to shutdown a short time later taking the other servers down. I'm now VERY careful about that check-box!

I'd appreciate hearing from anyone else, especially someone who can explain the port 6547 vs 3052 thing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.