Is it possible to stagger the restart of servers using PCNS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is it possible to stagger the restart of servers using PCNS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:36 PM

0 Likes
9
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:36 PM

Is it possible to stagger the restart of servers using PCNS

as of right now I think I have the PCNS clients shutting down properly, but when power is restored every machine in the racks are booting at the same time, including switches. I would like to stagger the reboots and give the switches a couple of minutes to initialize prior to the servers begning their reboot process. I thought maybe creating an execute command file event on power restore and the putting a delay prior to executing a "do nothing" command file might do it, but I am not sure and I dont see a good way to test that configuration.

We are experiencing a lot of power failures due to construction in the building and I would really like to get this addressed.

Thank you for any help.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

Good point voidstar. I forgot - SMT and SMX Smart UPS provide switched outlet groups and have similar functionality to outlets on a switched rack PDU except they are in a group.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:36 PM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:36 PM

Power Restored refers to when it is restored to the UPS, not the server so that wouldn't help you out. PCNS only deals with a shutdown in general.

To be honest, I feel like a Switched Rack PDU is your best bet and basically what the product is for. You can do what you asked for and stagger power on/off/reboot delays for each outlet. Our Switched Rack PDUs are here -> Switched Rack PDU - Product Information and we also have some Switched with Metering By Outlet if you wanted that (Metered-by-Outlet Rack PDU - Product Information).

Lastly, if you go to testdrive.apc.com, you can log into some of our Rack PDUs to check them out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:36 PM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:36 PM

Thank you for the response Angela. The Power restored I am refering do is an event on the client side. If it means when power is restored to the UPS then why is the event configurable on the client (i.e. execute command file)? How can the client do anything at the time power is restored to the UPS because technically the client doesnt get power until AFTER power is restored to the UPS, especially if you have things like minimum battery charge set at 5% set at the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:36 PM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:36 PM

Hi Matt

Let me give you an example on what I mean because I think there is some confusion.

UPS has 30 minutes of runtime. PCNS at default configuration to shutdown when UPS reaches low battery (by default with 2 mins runtime remaining)

10:00 -  AC power lost, UPS goes to battery, PCNS sees the event that UPS went to battery power (which is in a message from the UPS Network Management Card in the UPS)

10:20 - AC power restored. UPS is online (notified by UPS NMC again). PCNS client has not begin a shutdown yet since power loss was only 20 minutes. So, PCNS does not need to shutdown the system since power is restored and battery is charging.

Thus, when PCNS never is forced to shutdown the system, you could see power restored since PCNS monitors input status to the UPS among other events.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:32 PM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:32 PM

That makes sense. Although it seems a fairly small application window for an event.

So i guess I will refer to your first response as your recommendations on how to address my need to control reboots.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:32 PM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:59 AM . Last Modified: ‎2024-03-05 10:32 PM

Not a problem but that is what the event is for. Some UPSs may have a large runtime i.e. several hours so when the power comes back on, perhaps a command file is executed to send a message via messenger service or to do something else. So, not many users use it but that is what its there for.

Let me know if you have any switched rack PDU questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

Actually Angela, we do have 2 metered PDUs already. Can those be configured to stagger reboots?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

0 Likes
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

Unfortunately no. One of the main differences on Metered and Switched is individual outlet control and the functionality that comes along with that. Switched does encompass the ability of the metered though.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

0 Likes
0
1069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

If using a SMX or SMT UPS, perhaps put the servers on a separate outlet group for the switches, and set a power on delay. Or with any UPS, plug the switches and servers into separate UPSes with different on delays.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:00 AM . Last Modified: ‎2024-03-05 10:32 PM

Good point voidstar. I forgot - SMT and SMX Smart UPS provide switched outlet groups and have similar functionality to outlets on a switched rack PDU except they are in a group.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of