Is it possible that the UPS takes the load also when it is in Bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is it possible that the UPS takes the load also when it is in Bypass
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
121
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
idanst_apc
Crewman idanst_apc
Crewman

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
3
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

Is it possible that the UPS takes the load also when it is in Bypass

Hi 

I have APC Symmetra PX 100kW Scalable to 100kW, with 5 modules. 

the UPS suddently move to bypass and after few hours come back to normal

we suspcet that event when we get the bypass alert it is still available and when there is a power failure it goes to on battery with out the shutting the server down. is it possible?

sometimes the UPS goes to by pass due to "In bypass in response to the UPS front-panel or a user-initiated software
command, typically for maintenance" although nobody touches it and some time due to overload which we dont understand why it happen

As3aR8inxfnGkuOD0mPzPA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegAs3aR8inxfnGkuOD0mPzPA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Attachments
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi Idan,

I had to inquire with our 3 phase support team in EMEA for help with this. If you have further time sensitive questions along the same lines, I'd suggest you contact the local technical support office in your area.

Will it possible to replace the power module rack SYCF40KH with power module rack’s SYCF48KH that I have in stock, use only new power modules with 16KVA capacity (SYPM10K16H) and continue to use the same batteries and battery rack (SYCFXR8)? 

The answer is: Unfortunately the older XR frame designed for the Symmetra PX products (specifically 20/40

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi,

Can you provide the full event.txt, data.txt, and config.ini files for review please? That will also share with me the firmware version on your Management Card in the UPS.

Also, I am curious to know what firmware version is on your UPS. Could you check under the UPS->Intelligence System and tell me what's under there for firmware version?

With that information, hopefully we can better tell what is going on exactly. I'd also verify there is nothing physically connected to the UPS serial port(s).

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
idanst_apc
Crewman idanst_apc
Crewman

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

Hi 

I will try to collect the info you got but I now understand that the UPS has problem and I have some spares in stock. so the following question is much urgent 

My UPS has  a power module rack SYCF40KH and Batteries Rack SYCFXR8

Will it possible to replace the power module rack SYCF40KH with power module rack’s SYCF48KH that I have in stock, use only new power modules with 16KVA capacity (SYPM10K16H) and continue to use the same batteries and battery rack (SYCFXR8)?

Best Regards

Idan

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi Idan,

I had to inquire with our 3 phase support team in EMEA for help with this. If you have further time sensitive questions along the same lines, I'd suggest you contact the local technical support office in your area.

Will it possible to replace the power module rack SYCF40KH with power module rack’s SYCF48KH that I have in stock, use only new power modules with 16KVA capacity (SYPM10K16H) and continue to use the same batteries and battery rack (SYCFXR8)? 

The answer is: Unfortunately the older XR frame designed for the Symmetra PX products (specifically 20/40

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of