Installing AP9630/AP9631 in SUA2200RMI2U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Installing AP9630/AP9631 in SUA2200RMI2U
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

0 Likes
3
1930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

Installing AP9630/AP9631 in SUA2200RMI2U

Hi Guys,

This is my first post on the forum. I have some doubts and i've been trying to search without any luck or I'm just looking at a wrong answer. Hopefully, someone would be able to help me clarify things.

We currently have 2 x SUA2200RMI2U on a production environment. This 2 UPS currently don't have Network Management Card and I plan to install to both of them as this would help me tremendously in managing the status of the UPS and I can gracefully shutdown all our servers.

Here are the questions that I would like to ask:

  1. If I install NMC (AP9630/AP9631) to SUA2200RMI2U, do I need to power off the UPS and disconnect all the Servers or can I just hot-plug the card?
  2. If it is really necessary to power off the SUA2200RMI2U, how do you guys manage the installation on a production environment? Schedule a maintenance and shutdown all the servers?

Any advise/suggestions will be appreciated.

And thanks in advance, Guys.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • ap9630
  • ap9631
  • NMC
  • sua2200rmi2u
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

0 Likes
0
1930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

Hello,

1.) No, you don't need to power anything down.. refer to this knowledge base to support that statement -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156132 You can just go ahead and install your new Network Management Card in the UPS. The only scenario in which I'd exercise caution if there is another problem going on where this could make it worse - i.e. your UPS is in a major fault condition or is smoking, melting, on fire, SmartSlot appears damaged, etc where you probably want to focus on addressing something like that first smile

When you're setting up your Network Management Card, make sure to use the included APC serial cable(s) as we have non-standard cables and connecting a standard cable can cause unpredictable behavior too. This is mostly a concern when customers connect a DB-9 cable to the UPS. The Network Management Card serial cable is not likely something you'll see many other places.

Hope that helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

0 Likes
0
1931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

Hello,

1.) No, you don't need to power anything down.. refer to this knowledge base to support that statement -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156132 You can just go ahead and install your new Network Management Card in the UPS. The only scenario in which I'd exercise caution if there is another problem going on where this could make it worse - i.e. your UPS is in a major fault condition or is smoking, melting, on fire, SmartSlot appears damaged, etc where you probably want to focus on addressing something like that first smile

When you're setting up your Network Management Card, make sure to use the included APC serial cable(s) as we have non-standard cables and connecting a standard cable can cause unpredictable behavior too. This is mostly a concern when customers connect a DB-9 cable to the UPS. The Network Management Card serial cable is not likely something you'll see many other places.

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

0 Likes
0
1927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

Hi Angela,

Thank you so much for the clarification, it's quite a relief.

Before I post this question yesteday, I was reading half-way the same link that you've mentioned but suddenly the page forward me to maintenance page. So since I haven't found any more reference, I registered and post my question here.

Please help me close this post and considered answered.

Again, thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

0 Likes
0
1927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:52 PM . Last Modified: ‎2024-03-01 12:20 AM

No problem - you're very welcome! I also found an outdated reference in an installation guide that I will get updated too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.