Posted: 2022-04-13 03:49 AM
Hi,
I want to install PCNS v4.x on a server running Hyper-V 2016 (core). This is a stand-alone server, i.e., not clustered.
When I read the installation instructions, they advise that . . .
"The Remote Server Administration Tools must be installed for Hyper-V and Failover Clustering.
The PowerChute PowerShell scripts will not work correctly (for either VM migration or VM
shutdown) if these are not installed."
Running the PowerShell command as advised "Get-Module -ListAvailable"
Indicates that Hyper-V components are there . .
Binary 2.0.0.0 Hyper-V {Add-VMAssignableDevice, Add-VMDvdDrive, Add-VMFibreChanne...
Binary 1.1 Hyper-V {Add-VMDvdDrive, Add-VMFibreChannelHba, Add-VMHardDiskDriv...
But "Failover Clusters" is not. Based on the instruction above, it seems that the this is needed for VM Shutdown to work?
Assuming that is the case (?), can someone please give me a pointer on how to install the Cluster component on a Hyper-V (core) server, i.e., the correct way to install this component on a server without a GIU please?
regards
Dave
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-04-15 10:44 AM
You do not need to install failover clustering if you will not be utilizing migration.
If you want to install it
See Microsoft documentations
https://docs.microsoft.com/en-us/windows-server/failover-clustering/create-failover-cluster
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-04-15 10:44 AM
You do not need to install failover clustering if you will not be utilizing migration.
If you want to install it
See Microsoft documentations
https://docs.microsoft.com/en-us/windows-server/failover-clustering/create-failover-cluster
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.