The SU5000R5T-TF3 is listed as a 208V Input and 120/208V Output. This raises several questions:
1) Since it has a 3-blade input plug (NEMA L3-30P), I'm assuming this is a single phase supply, fed from a 2-pole circuit breaker on a 3-phase building supply. The 3rd blade would need to be ground. Is this correct?
2) It lists output availability as 120/208V. The 120V is covered by the NEMA 5-15R and NEMA L5-20R receptacles. Since the 208V output receptacles have only 3 blades (L6-20R), I'm assuming they are also 208V single phase only (2-hot blades and a ground blade). Is this correct?
If I need a true 3-phase 208Y/120 output, what is the closest APC model that would have around 5000 VA capacity range? Ideally, I'd prefer a rack-mount unit, but this might not be available.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
The SU5000R5T-TF3 is listed as a 208V Input and 120/208V Output. This raises several questions:
1) Since it has a 3-blade input plug (NEMA L3-30P), I'm assuming this is a single phase supply, fed from a 2-pole circuit breaker on a 3-phase building supply. The 3rd blade would need to be ground. Is this correct?
2) It lists output availability as 120/208V. The 120V is covered by the NEMA 5-15R and NEMA L5-20R receptacles. Since the 208V output receptacles have only 3 blades (L6-20R), I'm assuming they are also 208V single phase only (2-hot blades and a ground blade). Is this correct?
If I need a true 3-phase 208Y/120 output, what is the closest APC model that would have around 5000 VA capacity range? Ideally, I'd prefer a rack-mount unit, but this might not be available.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
The SUA2200 and SUA2200RM2U both come standard with a NEMA 5-20P as the units' standard input plug.
Are there options for using a NEMA 5-15P?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
tm13play,
The 2200 VA unit use a NEMA 5-20P because a 15A plug cannot achieve 2200VA, and therefore requires the 20A plug and power source. If you only have NEMA 5-15 Receptacles available, the largest UPS you can use on each 15A circuit would be any 1500VA SmartUPS.
-Mike
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
The SU5000R5T-TF3 is listed as a 208V Input and 120/208V Output. This raises several questions:
1) Since it has a 3-blade input plug (NEMA L3-30P), I'm assuming this is a single phase supply, fed from a 2-pole circuit breaker on a 3-phase building supply. The 3rd blade would need to be ground. Is this correct?
2) It lists output availability as 120/208V. The 120V is covered by the NEMA 5-15R and NEMA L5-20R receptacles. Since the 208V output receptacles have only 3 blades (L6-20R), I'm assuming they are also 208V single phase only (2-hot blades and a ground blade). Is this correct?
If I need a true 3-phase 208Y/120 output, what is the closest APC model that would have around 5000 VA capacity range? Ideally, I'd prefer a rack-mount unit, but this might not be available.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of