APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
I'm looking at buying another UPS and bouncing between another Symmetra or a Smart.
I thought I had a clue what I was doing until I looked at our existing Symmetra and got myself all confused.
Our Symmetra is a 6K with 3 power modules and 4 batteries.
I look at the website and it tells me the output is 34% of the Watts in both N+0 and N+1 (23% of the VA). And it's going at 6.7Amps.
I know enough to know that just because my server says it has an 850W power supply doesn't mean it will actually pull that much - so in saying that.
We have a 6509 in it with a 1300W power supply (the 6509 reports it's using 706 watts at 16.8A).
A 6509-E with a 6000W power supply (reports 1936W at 46.1A).
And 3 servers each with an 850W power supply.
Running with what I know (the Cisco equipment) I should be pulling at least 2642W (63% of the Symmetra max) at 62.9A (well above the 6.7 the Symmetra is reporting).
Every once in a while (once a month in the dead of night) I get a notice that the Symmetra spikes for 2 seconds over capacity. I'll buy into that if it is really running in the 80% usage all the time... but not 35% all the time.
Anyone have a clue what I'm missing?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
I'm looking at buying another UPS and bouncing between another Symmetra or a Smart.
I thought I had a clue what I was doing until I looked at our existing Symmetra and got myself all confused.
Our Symmetra is a 6K with 3 power modules and 4 batteries.
I look at the website and it tells me the output is 34% of the Watts in both N+0 and N+1 (23% of the VA). And it's going at 6.7Amps.
I know enough to know that just because my server says it has an 850W power supply doesn't mean it will actually pull that much - so in saying that.
We have a 6509 in it with a 1300W power supply (the 6509 reports it's using 706 watts at 16.8A).
A 6509-E with a 6000W power supply (reports 1936W at 46.1A).
And 3 servers each with an 850W power supply.
Running with what I know (the Cisco equipment) I should be pulling at least 2642W (63% of the Symmetra max) at 62.9A (well above the 6.7 the Symmetra is reporting).
Every once in a while (once a month in the dead of night) I get a notice that the Symmetra spikes for 2 seconds over capacity. I'll buy into that if it is really running in the 80% usage all the time... but not 35% all the time.
Anyone have a clue what I'm missing?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:17 PM . Last Modified: 2024-03-15 04:10 AM
I'm looking at buying another UPS and bouncing between another Symmetra or a Smart.
I thought I had a clue what I was doing until I looked at our existing Symmetra and got myself all confused.
Our Symmetra is a 6K with 3 power modules and 4 batteries.
I look at the website and it tells me the output is 34% of the Watts in both N+0 and N+1 (23% of the VA). And it's going at 6.7Amps.
I know enough to know that just because my server says it has an 850W power supply doesn't mean it will actually pull that much - so in saying that.
We have a 6509 in it with a 1300W power supply (the 6509 reports it's using 706 watts at 16.8A).
A 6509-E with a 6000W power supply (reports 1936W at 46.1A).
And 3 servers each with an 850W power supply.
Running with what I know (the Cisco equipment) I should be pulling at least 2642W (63% of the Symmetra max) at 62.9A (well above the 6.7 the Symmetra is reporting).
Every once in a while (once a month in the dead of night) I get a notice that the Symmetra spikes for 2 seconds over capacity. I'll buy into that if it is really running in the 80% usage all the time... but not 35% all the time.
Anyone have a clue what I'm missing?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.