Input Current for SRT10KRMXLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Input Current for SRT10KRMXLI
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:14 PM . Last Modified: ‎2024-03-06 11:18 PM

0 Likes
5
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:14 PM . Last Modified: ‎2024-03-06 11:18 PM

Input Current for SRT10KRMXLI

Hi,

Can someone advice me what is the input current required for SRT10KRMXLI UPS? We have 3 phase 20amps, does it sufficient for this model of UPS? Thank you.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:18 PM

0 Likes
0
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:18 PM

Bill,

     Thanks for sharing the installation guide.In deep wee have refereed to this spec but we are not sure which column of information to read.   We currently runs on 3 phase 20 A single feed, we would like to get your technical expertise to assist us to confirm that our current socket (3 phase 20 A) is sufficient to support SRT10KRMXLI UPS we plan to purchase. According to the spec, it stated “Current Full Load (nominal)” is 18 A and “External Input Circuit Breaker Mains (typical)” is 80 A, we are not sure what is the different of those 2 reading indicating about. Our electrician wants us to confirm that the input current required is the reading out from “Current Full Load (nominal)” is 18 A and not  “External Input Circuit Breaker Mains (typical)” is 80 A. Thank you for your advice.

 

 Question

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:18 PM

0 Likes
0
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:18 PM

Kelly,

The installation guide list the required input and wiring.

http://www.apcmedia.com/salestools/SCON-9DETDD/SCON-9DETDD_R3_EN.pdf?sdirect=true

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:18 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:18 PM

Bill,

     Thanks for sharing the installation guide.In deep wee have refereed to this spec but we are not sure which column of information to read.   We currently runs on 3 phase 20 A single feed, we would like to get your technical expertise to assist us to confirm that our current socket (3 phase 20 A) is sufficient to support SRT10KRMXLI UPS we plan to purchase. According to the spec, it stated “Current Full Load (nominal)” is 18 A and “External Input Circuit Breaker Mains (typical)” is 80 A, we are not sure what is the different of those 2 reading indicating about. Our electrician wants us to confirm that the input current required is the reading out from “Current Full Load (nominal)” is 18 A and not  “External Input Circuit Breaker Mains (typical)” is 80 A. Thank you for your advice.

 

 Question

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:17 PM

0 Likes
0
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:17 PM

If your electrician needs to ask that then it is time to employ a new electrician.

Reply

Link copied. Please paste this link to share this article on your social media post.

prince213_apc
Lieutenant prince213_apc
Lieutenant

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:17 PM

0 Likes
1
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:15 PM . Last Modified: ‎2024-03-06 11:17 PM

You need to fit 80A MCB's or 80A 4 pole MCB at distribution board. The 18A showing there is the typical load current which can range from 18A to around 54A. 8OA is the peak current which should not be exceeded in any case.

Reply

Link copied. Please paste this link to share this article on your social media post.

TellItLikeItIs_apc
Ensign TellItLikeItIs_apc
Ensign

Posted: ‎2022-06-25 11:00 PM

In response to prince213_apc
0 Likes
0
1422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-25 11:00 PM

It’s a shame that some forum users don’t want to help others to learn.

 

This UPS can be supplied by either a single or 3 phase electrical supply. If supplied by a 3 phase supply, the load on each phase will be a maximum as was suggested (in the order of 20 Amps per phase). The supply becomes an issue if the UPS develops an internal fault and needs to switch to static bypass. When the UPS is in static bypass all of the input load switches to one phase (usually L1 depending how the UPS has been wired ). The supply would then be overloaded and trip.

 

your electrician may be very good but it sounds like he is not familiar with UPS’s or at least this model. I would suggest you use someone who is competent (has the necessary knowledge skills and experience of how to install and commission) this UPS. The individual should be able to demonstrate they have been trained by Schneider on this product and have experience of installing the same - this should not be their first time. They should also be able to commission the UPS correctly including updating the UPS firmware and configuring the network management card for you. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of