Incorrect date when first starting ups smt1500rmi2u
Showing results forΒ
Did you mean:Β
  • Incorrect date when first starting ups smt1500rmi2u
VAM
VAM
Cadet
Posted: β€Ž2025-04-08 01:26 AM
615
Good afternoon
At the first launch, I mistakenly confirmed the default date. Now the "Today's date" parameter (maybe "Battery installation date") is the "Date of manufacture of the device". Can you tell me how to re-enter this parameter? That is, to set the current date in the device?
(Reset to factory settings did not help)
Kirk
Posted: β€Ž2025-04-08 04:46 AM
585
You can disconnect the battery cartridge and wait for the system to declare a battery fault.
Wait another ten seconds than reconnect the battery cable.
The system will prompt you to confirm a new battery cartridge has been installed. Toggle from No to Yes and enter the month / year and hit enter.
Questions Ask - If not, and this solved your problem. Please mark this reply as a solution to help the next person asking the same. πŸ‘
Kirk
586
VAM
VAM
Cadet
Posted: β€Ž2025-04-08 07:28 AM
In response to Teken
551
Thanks!
Let me clarify:
in other words, the date that I was supposed to keep when I first turned on the UPS refers only to the date when the battery was installed?
Or is this information also necessary to set the current time of the device itself?
Kirk
Posted: β€Ž2025-04-09 05:23 AM
In response to VAM
If the unit has a NMC installed than the date can be entered. If there is no NMC installed the date applies to battery installation date.
Both would be the same (Install / Battery) during the installation of the unit when it was unboxed.
Β