INROW "Hot Gas Bypass Valve" should it be fully open.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • INROW "Hot Gas Bypass Valve" should it be fully open.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
twin--turbo_apc
Crewman twin--turbo_apc
Crewman

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
9
3716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-02-14 10:19 PM

INROW "Hot Gas Bypass Valve" should it be fully open.

We monitor various data from our 4 In-Row Coolers, recently the "HOT GAS BYPASS" valves have been edging closer to 100%

Does this indicate anything? 

A couple of years ago we had one unit that was stuck at 100%.

Cheers

Rob

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
3714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello. The rack inlet sensor should be placed on the front of the rack next to the cooling unit. It is a 13 foot sensor that usually comes out of the top of the cooling unit and is placed on the front door of the rack next to the unit. It is a black wire with a rubber tip on the end. In HACS mode the unit will not be using the rack inlet sensor to determine if it needs to cool. In HACS the unit will use the return and supply air temperatures to determine if it needs to cool. It is hard to say if this is the best setup for your room. Do you have a HACS containment system in your data center?

Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello. The hot gas bypass opening would not by itself cause any alarm to the unit. The hot gas bypass is used by the units in low load situations to protect the compressor from slugging. If you are in the northern hemisphere and winter is approaching, the load will usually go down slightly due to it being colder outside. This would cause the hot gas bypass to open up more to protect the compressor. If you would like to attach the data logs on the unit(s) we can take a look at them and make sure the pressures and temperatures look good.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

twin--turbo_apc
Crewman twin--turbo_apc
Crewman

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-02-14 10:19 PM

It is getting colder, but the "Monitoring" has been the same thresholds for ~3 years and only this year does it seem to be creating many more alerts. 

what's the easiest way to export the group data logs?

Thanks

Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello. The Best way to get the full logs is to perform a Get data.txt through ftp. You can also copy them off the web interface.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

twin--turbo_apc
Crewman twin--turbo_apc
Crewman

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-02-14 10:19 PM

Uploaded, not sure if it includes all group data.

Thanks

Rob

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello. From the data logs the Hot Gas Bypass is opening because of a low load in the room. The unit is only seeing between 2.7-4 kw of load. This is very close the the minimal load the unit can handle. The Hot Gas Bypass is opening to allow the unit to run at these low loads and protect the compressor. This is normal operation for this unit at those loads. The data in the rest of the logs all look good. The pressures and temps are all in normal ranges. It is just the low load causing the Hot Gas to open.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

twin--turbo_apc
Crewman twin--turbo_apc
Crewman

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-02-14 10:19 PM

So which temperature sensor is the most important one to monitor? we have 10 racks ( 2 with a Symmetra UPS ) but only 4 equipment racks with sensors flipped to the cold side doors?

Thanks

Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello. This does depend on the setup and environment of the room. Generally the main one to look at is the rack inlet sensor as the main goal of the cooling unit is to provide cool air to the intake of your servers. You will have to be careful that the sensors are not picking up the heat from the servers or any other heat sources that may give higher readings then what the intake air actually is.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

twin--turbo_apc
Crewman twin--turbo_apc
Crewman

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

Where is the rack inlet located?

If we try to put the system in into 3+1 rather than 4 active the temperature creeps up.

It's presently set in "HACS" is that best, I know it's difficult t comment without seeing the layout of the Isle and the specific heat loading in each cabinet.

Thanks

Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
3715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello. The rack inlet sensor should be placed on the front of the rack next to the cooling unit. It is a 13 foot sensor that usually comes out of the top of the cooling unit and is placed on the front door of the rack next to the unit. It is a black wire with a rubber tip on the end. In HACS mode the unit will not be using the rack inlet sensor to determine if it needs to cool. In HACS the unit will use the return and supply air temperatures to determine if it needs to cool. It is hard to say if this is the best setup for your room. Do you have a HACS containment system in your data center?

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore