AP7930 web interface - Error: The application was not able to load.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7930 web interface - Error: The application was not able to load.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
cuddylier_apc
Ensign cuddylier_apc
Ensign

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
11
10089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

AP7930 web interface - Error: The application was not able to load.

Hi

My AP7930 has suddenly started showing the following when I try to access the web interface:

Error: The application was not able to load.
 
You are attempting to access an APC device.

There was a problem loading the application. Please login to the device via telnet for more details.

When I login to the PDU via console, this is what it shows:

Stat : P+ N+ A-

I tried connecting to the FTP server but get the following errors:

Windows command prompt FTP client:

150 File status okay; about to open data connection.
Aborting any active data connections...

425 NLST can't open data connection.

Filezilla:

Response: 421 Service not available, closing control connection.

Above is while trying all transfer modes including passive, I presume it's not working partially due to the OS seemingly being messed up.

Any ideas on what I can do to bring the web interface back to life? SSH and Telnet are both dead, despite me enabling each (one at a time).

Thanks

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:33 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
10079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:33 AM . Last Modified: ‎2024-01-31 03:03 AM

Ok, got you. No problem! Glad it is all set now.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
10079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

I'd try the reset button (or remove the power if there's no reset button). If it doesn't work after that, the "format" command will blow away the filesystem (but leave AOS intact). Then configure networking settings. Check if ftp works. If so, grab the latest firmware for your device from APC.com and install it. If not, try eliminating the possibility of a network problem by plugging the AP9630 and your PC into another hub or switch.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
10079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

Just one clarification  voidstar  - this is an AP7930 Rack PDU. I think you had it confused with AP9630 NMC2 so I wanted to comment to clarify for original poster. Too, this means there will be no format option or ability to move it between UPSs.

To the original poster, do you know for sure your FTP data port is open? Typically in this situation, FTP should still be working. The errors you were seeing I've seen if the FTP data port (20) is blocked. It is feasible that it is not working properly due to something else as you suggested but I'd also want to confirm about the FTP data port.

In this situation, we need to figure out how to re-load the application file. Through the serial connection or FTP prompt, do you know which AOS is on the PDU right now? We'll want to load the matching application to see if we can restore the PDU back to the correct state. Worst case, we could try it over a serial connection but hopefully we can get FTP working.

A power cycle (if possible - understand the PDU may have devices plugged in) or a press and release of the pinhole reset button may help so you can try those too. But, we may want to wait and proceed with caution because of the current state of the PDU and not 100% knowing how it got here or if there are other alarms/problems. In rare situations, if there are other problems, rebooting the PDU may cause the outlets to not re-energize after the reboot.

Reply

Link copied. Please paste this link to share this article on your social media post.

cuddylier_apc
Ensign cuddylier_apc
Ensign

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
10079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

On 12/4/2017 5:47 PM, Angela said:

Just one clarification  voidstar  - this is an AP7930 Rack PDU. I think you had it confused with AP9630 NMC2 so I wanted to comment to clarify for original poster. Too, this means there will be no format option or ability to move it between UPSs.

To the original poster, do you know for sure your FTP data port is open? Typically in this situation, FTP should still be working. The errors you were seeing I've seen if the FTP data port (20) is blocked. It is feasible that it is not working properly due to something else as you suggested but I'd also want to confirm about the FTP data port.

In this situation, we need to figure out how to re-load the application file. Through the serial connection or FTP prompt, do you know which AOS is on the PDU right now? We'll want to load the matching application to see if we can restore the PDU back to the correct state. Worst case, we could try it over a serial connection but hopefully we can get FTP working.

A power cycle (if possible - understand the PDU may have devices plugged in) or a press and release of the pinhole reset button may help so you can try those too. But, we may want to wait and proceed with caution because of the current state of the PDU and not 100% knowing how it got here or if there are other alarms/problems. In rare situations, if there are other problems, rebooting the PDU may cause the outlets to not re-energize after the reboot.

Hi Angelaand  voidstarthanks for replying!

I just checked again and it seems the FTP works now strangely.

I see the file apc_hw02_aos_392.bin in the root FTP directory.

Model Number      : AP7930
Serial Number     : ZA0732xxxxxx
Manufacture Date  : 08/10/2007
Hardware Revision : B2
MAC Address       : 00 C0 B7 72 xx xx
 Flash Type        : AMD A29DL322DB

 Name        : aos               Type        : APC OS
 Version     : 392               Sector      : 16
 Date        : 07/06/2016        Time        : 15:12:05
 CRC16       : C3FF
The PDU is in production so can't be powered off, I can try the reset pin though if you think it may work?
Reply

Link copied. Please paste this link to share this article on your social media post.

cuddylier_apc
Ensign cuddylier_apc
Ensign

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
10079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

On 12/4/2017 6:14 PM, Angela said:

I would try loading the 3.9.2 application file to the PDU first. I attached it to this post. Only problem is, the forum blocked it so I renamed it to .jpg. You will want to fix the attachment to be a .bin extension embarassed

You'd want to FTP in, then do 'bin' and 'hash' commands to force binary mode and print hash marks, then 'put' this file (attached). Alternatively, I am sure you can find those same settings with FileZilla if not using a Windows command prompt wink - Make sure to disconnect the FTP session when done and the management interface in the PDU will know to reboot after the file is done loading. Then, check afterwards and see what you get. If you get in, I suggest checking the event log to see if there is any clue to what occurred. The event log is only available when the app is correctly loaded.

If you need more details, look at NMC1 FTP instructions here -> http://www.apc.com/us/en/faqs/FA156047, specific to when it talks about loading the application file. (We don't need to re-load AOS which is the first few steps.)

I loaded the application file and that did the job, thank you!

I checked the event logs and surprisingly there wasn't anything at all referencing an issue with the OS, I do have a lot of near overload errors spamming the logs though so maybe they spammed so much that any other errors got hidden/ran off the end of the log?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
10079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:03 AM

There wouldn't be any messages specifically saying anything with the OS. I'd be looking for frequent "System: Warmstart" or TCP/IP stack failures or something like that. 

Feel free to attach a .txt file of the event log from FTP - you can retrieve event.txt using these instructions (if you need them). http://www.apc.com/us/en/faqs/FA156131 (copy/paste from web is OK too as long as you're showing the full log and I can see it from top to bottom, .txt is nicer format and less work if you can grab it.)

If you want, also remove any private info before posting the log. I'll take a look and see if there is anything in there that looks interesting to see what happened so we can also feel a little better it won't repeat itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

cuddylier_apc
Ensign cuddylier_apc
Ensign

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
10079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

On 12/4/2017 7:44 PM, Angela said:

There wouldn't be any messages specifically saying anything with the OS. I'd be looking for frequent "System: Warmstart" or TCP/IP stack failures or something like that. 

Feel free to attach a .txt file of the event log from FTP - you can retrieve event.txt using these instructions (if you need them). http://www.apc.com/us/en/faqs/FA156131 (copy/paste from web is OK too as long as you're showing the full log and I can see it from top to bottom, .txt is nicer format and less work if you can grab it.)

If you want, also remove any private info before posting the log. I'll take a look and see if there is anything in there that looks interesting to see what happened so we can also feel a little better it won't repeat itself.

I do see warmstart in the event log as it came back to life. I've attached the event.txt

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
10079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:03 AM

Thanks for sharing. That warmstart (soft reboot) is expected so we are OK there.

Is the 12/31/2016 date accurate, meaning was that last year or was that really a day or two ago or what?

I ask because I see this in the log 

12/31/201618:45:03System: File transfer failed.0x000F

But then I also see these, which if the date/time was wrong, I would've expected to see the correct date and time only occur as of these messages where it said it set the time (and newer messages), not way back with the System: Warmstart:

12/04/201719:31:01System: Set Date.0x002112/04/201719:31:01System: Set Time.0x0021

I ask because that File Transfer failed.. well if that was you today or the other day when we were fixing this OK, but if it was someone who attempted a firmware upgrade and it failed, it could've caused this problem.

I see an FTP log in a few minutes before that file transfer failed message..

12/31/201618:43:46System: FTP user 'apc' logged in from 10.10.x.x.0x0016
Reply

Link copied. Please paste this link to share this article on your social media post.

cuddylier_apc
Ensign cuddylier_apc
Ensign

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

0 Likes
0
10077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:19 PM

On 12/4/2017 8:16 PM, Angela said:

Thanks for sharing. That warmstart (soft reboot) is expected so we are OK there.

Is the 12/31/2016 date accurate, meaning was that last year or was that really a day or two ago or what?

I ask because I see this in the log 

12/31/2016	18:45:03	System: File transfer failed.	0x000F

But then I also see these, which if the date/time was wrong, I would've expected to see the correct date and time only occur as of these messages where it said it set the time (and newer messages), not way back with the System: Warmstart:

12/04/2017	19:31:01	System: Set Date.	0x0021
12/04/2017	19:31:01	System: Set Time.	0x0021

I ask because that File Transfer failed.. well if that was you today or the other day when we were fixing this OK, but if it was someone who attempted a firmware upgrade and it failed, it could've caused this problem.

I see an FTP log in a few minutes before that file transfer failed message..

12/31/2016	18:43:46	System: FTP user 'apc' logged in from 10.10.x.x.	0x0016

That date/time was probably from just before I successfully got the new OS uploaded as that date seems to be right before the accurate date/time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
10077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-01-31 03:03 AM

Hmm, OK. So you think when it set the date/time, it truly only had to update the time then? Or did I mis-understand? I think I misunderstood because in your original post, you made it seem like you log into the PDU pretty regularly and there is no way this problem existed for a year.

The only thing I see in the log in general is that failed file transfer. Not seeing anything else helpful.

Basically, when you upload a new .bin file, whether a new AOS or application file, it overwrites the old application file. If that file you chose was wrong or invalid and doesn't pass some checks, the Network Management Card will not transfer it to flash and thus, the app file space is left empty.

What I was suggesting as a possibility was that if someone tried to start a firmware upgrade and it failed for one reason or another, this could've occurred where the app file was wiped as it can't be recovered after a failed transfer. Other than that, not sure what happened based on the log..

Reply

Link copied. Please paste this link to share this article on your social media post.

cuddylier_apc
Ensign cuddylier_apc
Ensign

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:18 PM

0 Likes
0
10077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:32 AM . Last Modified: ‎2024-02-14 10:18 PM

On 12/4/2017 8:32 PM, Angela said:

Hmm, OK. So you think when it set the date/time, it truly only had to update the time then? Or did I mis-understand? I think I misunderstood because in your original post, you made it seem like you log into the PDU pretty regularly and there is no way this problem existed for a year.

The only thing I see in the log in general is that failed file transfer. Not seeing anything else helpful.

Basically, when you upload a new .bin file, whether a new AOS or application file, it overwrites the old application file. If that file you chose was wrong or invalid and doesn't pass some checks, the Network Management Card will not transfer it to flash and thus, the app file space is left empty.

What I was suggesting as a possibility was that if someone tried to start a firmware upgrade and it failed for one reason or another, this could've occurred where the app file was wiped as it can't be recovered after a failed transfer. Other than that, not sure what happened based on the log..

I should have clarified, the previous date/time is wrong so it wasn't really a year ago, I do in deed login relatively regularly, every month or two. I'll just assume it was some sort of firmware issue and hopefully won't see it again.

Thank you once again for all your help, much appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:33 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
10080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:33 AM . Last Modified: ‎2024-01-31 03:03 AM

Ok, got you. No problem! Glad it is all set now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore