Condensate leak

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Condensate leak
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:30 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
7
1836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:30 AM . Last Modified: ‎2024-01-31 03:04 AM

Condensate leak

Good DAy, 

i am having an issue, i have an ACRC100 unit and condensate is somehow getting on the base of the unit around the condensate pan and draining to floor, the condensate pan does not seem to have any cracks, the floats are sealed, the side panel does not have any water marks to say condensate is running down the door and getting to the base of the unit, the pump hose does not have any leaks. Does anyone have any suggestions as to what could be the cause if this or if they anyone have any similar experiences?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
1836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello. The only water in this unit should be coming from the condensate from the coil while cooling. If the pan is not cracked, you can check the txv and distributor tubes to make sure they are not creating condensate. You have already checked the insulation on the pipes which is good. The only other parts is the condensate lines and pumps to make sure they are not leaking. These are the only sources of water in this unit.

Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:30 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
1835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:30 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello Terrence. If the water is pooling around the condensate pan, this most likely means there is a small crack in the pan. Make sure to pull one of the bottom fans in the front of the unit to check the front side of the condensate pan for cracks as well. If you find one, dry out the pan and use some water sealant to seal the crack.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
1836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

I removed the entire unit from the row and inspected the condensate pan, no crack of any sort was found, three different persons inspected the pan and nothing was found wrong with the pan. We found one or two spots that the internal insulation is a little loose and condensate is forming, these points were sealed but a definite point of how the water is getting to the base of the unit could not be determined.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
1837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

Hello. The only water in this unit should be coming from the condensate from the coil while cooling. If the pan is not cracked, you can check the txv and distributor tubes to make sure they are not creating condensate. You have already checked the insulation on the pipes which is good. The only other parts is the condensate lines and pumps to make sure they are not leaking. These are the only sources of water in this unit.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
1835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

thanks, condensate pump and lines were checked as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
1835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

We had a possibly similar issue many years back where water was found in the bottom of 2 of our servers. We discovered that the condensate pan of the A/C unit located in the ceiling of the server room was not draining. But it was not overflowing and we found no leakage on the rack or any other piece of equipment in the room. But the humidity was very high. We did not have a sensor at the time.

My theory on the issue is that the humidity in the room was high enough that the pressure difference in front of the fans caused condensation to form inside the server.

Temperature is a much stronger influence on condensation but pressure also has an affect. Normally any condensation caused by pressure drop would evaporate when the temperature comes up a bit. Only in a server, in a server room, could the temp remain constant enough and the fans strong enough for this to happen.

In response to this incident I changed the temp setting for the server room from 60 to 65 degrees and we added a dehumidifier and put a temp and humidity sensor on the rack. The human body senses low temp and high humidity as the same as a slightly higher temp and lower humidity so you can't necessarily trust your senses. I also believe that an extra cool server room will draw humidity from the rest of the building.

Brian

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
1835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

Good Day, 

That sounds interesting, i will check into this and monitor the humidity levels in the room, i will get back to you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

0 Likes
0
1835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:31 AM . Last Modified: ‎2024-01-31 03:04 AM

Another note is that the 2 servers were identical and had the loudest fans in the room.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore