I'll damage my SURT10000XLT if I setup it on a 240VAC Input circuit?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • I'll damage my SURT10000XLT if I setup it on a 240VAC Input circuit?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
3
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

I'll damage my SURT10000XLT if I setup it on a 240VAC Input circuit?

Hi people!

I'm new setting up No-Breaks, and i have a few questions....

I'll damage my SURT10000XLT if I setup it on a 240VAC Input circuit? (APC Smart-UPS RT 10000VA 208V)

I'm afraid if it works with 240vac range...

Thanks so much!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 02:00 AM

SURT10000XLT is designed for use in the US primarily with 208V or 240V with two phases and a ground on the input. It comes pre-set for 208V though and it's required that you log into it and change the output to 208V or else you'll be inputting 240V and outputting 208V which is not good practice and could damage your equipment.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

Pretty sure you won't cause damage as the spec on this says its for 200 - 240 VAC but I defer to APC for the last word. The issue may be what output voltage you get (or need): the APC web page for its say its configurable for 208 or 240 out, but not what input voltage that refers to. IE if you put 240 in, can you configure for 208 or 240 out and vice-versa  (208 in allows both 208 or 240 out) ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 02:00 AM

Yep thats true, i've readed the manuals and get the same doubt...

As for the input voltage, the manual says input 200-240, but the web page says the input voltage 208vac in its name..

i get worried because my nobreak is malfunctioning... with "inverter fault" error, so i dont know if have damaged the nobreak powering it up with the 240vac circuit, when installed it...

should i have bought the XLI model maybe? Or this error nothing has with it and the UPS came malfunctioning from the vendor?

i Have another surt10000XLT new that i can use, but i'm fearing if i can safely try to use it too smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
1545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 02:00 AM

SURT10000XLT is designed for use in the US primarily with 208V or 240V with two phases and a ground on the input. It comes pre-set for 208V though and it's required that you log into it and change the output to 208V or else you'll be inputting 240V and outputting 208V which is not good practice and could damage your equipment.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore