Completely "turn off" UPS instead of "power off" outlets. Is it possible to do this remotely?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Completely "turn off" UPS instead of "power off" outlets. Is it possible to do this remotely?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
10
27518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

Completely "turn off" UPS instead of "power off" outlets. Is it possible to do this remotely?

Hi.

Has APC Smart UPS capability to completely turn of UPS system via command set (serial or TCP/UDP)?.I means input and output of UPS will be entirely lost. I can imagine UPS outlets can be power off and on, that is fine, however I try to be sure whether it can be possible to turn off UPS itself.

Note: "completely turn off" means UPS is ready to be transported to anywhere or be stored, like emergency hard button (EPO) is pressed.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
27501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

"After 9 minutes of both power failure and output off, the UPS becomes "brain dead" and stops powering the Network Management Card so it can no longer be remotely commanded. Once power returns, the UPS will leave the "brain dead" state and resume charging the battery."


At this moment, (I mean MAINS came back, and UPS is charging battery), a HW "ON/Test" switch/button on UPS must be pressed to turn it on again as I guess. Remotely turning it on can not be performed, like Network Management Card, due to energy absence.


My question at this point is that APC UPSs have opportunity to carry this HW "ON/Test" switch/button to connector panel as a dry contact which can be opened/closed from a remote site (may be over a relay)? Assume that UPS is installed into a cabinet (where access to UPS is not easy) and the control of this cabinet  have to be done via a control panel (remote site).





See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

I'm not clear on why the UPS needs to be completely off. Right now they're designed on the assumption that complete turnoff is only required for:

1) EPO and

2) maximizing battery runtime during a power outage.

What that second point means is you can turn the output off, disconnect the power plug, and the UPS will turn off after nine minutes.

For transport or storage, SmartUPSes have a battery disconnect that should be pulled. The battery will discharge faster if not disconnected, even when the UPS is completely off. And if you also disconnect the power cord, the UPS will be completely off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

About the existing UPS; If you only turn outputs off, UPS FANS (this is an online UPS) are still working, which means that power consumption is still going on. In case off MAINS is available, as you said, they are functional forever. In this case UPS is in charge mode, so there is no problem.

At this moment, if MAINS is disconnected, FANS still continue to operate forever and don't turn off. Since FANS are still consumpting power, UPS will became discharged after some moment. This causes UPS to be not able to turn on again, because UPS has a property to close itself forever if charge value is below of some percentage (as I remember this value is %25 of full charge)


As I understood, APC UPS has property to completely shut down itself after 9 min, if there is no MAINS power. This can solve my problem.


What about this 9 min? At any instance in this duration, can it be possible to turn on and off UPS again, Assume that UPS has already turned off, MAINS has been disconnected and 5 minutes have already passed. At this moment, if MAINS is re-connected again, will UPS start to be charging and supply power for the system? Is it correct?



Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

erdemk wrote:

At this moment, if MAINS is disconnected, FANS still continue to operate forever and don't turn off. Since FANS are still consumpting power, UPS will became discharged after some moment. This causes UPS to be not able to turn on again, because UPS has a property to close itself forever if charge value is below of some percentage (as I remember this value is %25 of full charge)


Okay, so your concern is that without a command to turn the UPS off, it will fully discharge itself during a power outage. Makes sense. Has this happened?


As I understood, APC UPS has property to completely shut down itself after 9 min, if there is no MAINS power. This can solve my problem.


Right. After 9 minutes if there is no MAINS power and the output is off. We call this state "brain dead".


What about this 9 min? At any instance in this duration, can it be possible to turn on and off UPS again, Assume that UPS has already turned off, MAINS has been disconnected and 5 minutes have already passed. At this moment, if MAINS is re-connected again, will UPS start to be charging and supply power for the system? Is it correct?

During the 9 minutes, the UPS' output can be commanded back on by the Network Management Card. After 9 minutes of both power failure and output off, the UPS becomes "brain dead" and stops powering the Network Management Card so it can no longer be remotely commanded. Once power returns, the UPS will leave the "brain dead" state and resume charging the battery. Whether the UPS output also turns back on to supply power for the system depends on whether the output was "turned off" or "shutdown".

UPS output turn off => UPS output does not automatically turn back on

UPS output shutdown / reboot w/ ac present => UPS output turns back on when power returns and battery has charged enough to meet the minimum runtime setting.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

If mains has been restored somehow, perhaps a different switch - so the UPS is not braindead anymore because AC is present and it comes to life - then yes, we offer dry contacts in a few different forms - depending on the UPS model, it probably has an RJ-45 or DB-9 serial port that could be used. If a Network Management Card is present, preferably AP9631, you can add an AP9810 dry contact accessory to it. Lastly, we offer another full featured dry contact card with many more input contacts and outputs that purely just does dry contacts (AP9631).

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

erdemk wrote:

"After 9 minutes of both power failure and output off, the UPS becomes "brain dead" and stops powering the Network Management Card so it can no longer be remotely commanded. Once power returns, the UPS will leave the "brain dead" state and resume charging the battery."


At this moment, (I mean MAINS came back, and UPS is charging battery), a HW "ON/Test" switch/button on UPS must be pressed to turn it on again as I guess. Remotely turning it on can not be performed, like Network Management Card, due to energy absence.

As Angela mentioned, once MAINS comes back, the UPS is no longer "brain dead" and should be able to be commanded by the NMC. And also, if the output was shutdown (not turned off), then once the battery is sufficiently charged, the output will turn back on automatically.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:01 AM

Hi.

Has APC Smart UPS capability to completely turn of UPS system via command set (serial or TCP/UDP)?.I means input and output of UPS will be entirely lost. I can imagine UPS outlets can be power off and on, that is fine, however I try to be sure whether it can be possible to turn off UPS itself.

Note: "completely turn off" means UPS is ready to be transported to anywhere or be stored, like emergency hard button (EPO) is pressed.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

Case 1: MAINS on, UPS on, UPS outputs on: Load is supplied, power on mode

Shutdown process started.

Case 2: MAINS on, UPS on, UPS outputs off: Load is not supplied, shutdown mode.

Power on process started.

Case 3: MAINS on, UPS on, UPS outputs on: Load is supplied, power on mode.

MAINS disconnected

Case 4: MAINS off, UPS on, UPS outputs on: Load is supplied, power on mode.

Shutdown process started

Case 5: MAINS off, UPS on, UPS outputs off: Load is not supplied, shutdown mode.

UPS will turn off (brain dead) after 9 min. No problem during turn off mode.

Case 6: MAINS on, UPS off, UPS outputs off: Load is not supplied, turn off mode.

Power on process started.

Problem!!!! HW turn on switch/button must be pressed...

Is it possible to add such a dry contact on UPS connector panel to be able to immediately turn on and delayed shutdown UPS via a hw switch?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

It depends on the UPS models - some have an EPO to do this with, some do not. Through the management card, the most you can do is turn off the output.

Most offer a DB-9 or RJ-50 style serial port where you can turn the output off at a minimum. Dry contacts are also an option.

If you turn the output off (the outlets) via one of the methods I noted and cut the upstream power to the UPS, this condition (what we call braindead) will also occur within to 8-10 minutes of the UPS sitting with no AC input.

If you have a specific model/SKU, I can tell you for sure what capability it supports.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
27500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

erdemk wrote:

Case 4: MAINS off, UPS on, UPS outputs on: Load is supplied, power on mode.

Shutdown process started

Okay, since this is a "Shutdown" and not "Turn off", the output will turn back on once MAINS is on and the battery is sufficiently charged.

Case 5: MAINS off, UPS on, UPS outputs off: Load is not supplied, shutdown mode.

UPS will turn off (brain dead) after 9 min. No problem during turn off mode.

Case 6: MAINS on, UPS off, UPS outputs off: Load is not supplied, turn off mode.

Power on process started.

If MAINS is on and the EPO has not been triggered, then the UPS will be on. So case 6 should be:

Case 6: MAINS on, UPS on, UPS outputs off while runtime < minimum return runtime. Load is not supplied.

... after charging battery so runtime > minimum return runtime ...

Case 7: MAINS on, UPS on, UPS outputs on. Load is supplied.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

0 Likes
0
27502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:41 AM . Last Modified: ‎2024-03-05 02:00 AM

"After 9 minutes of both power failure and output off, the UPS becomes "brain dead" and stops powering the Network Management Card so it can no longer be remotely commanded. Once power returns, the UPS will leave the "brain dead" state and resume charging the battery."


At this moment, (I mean MAINS came back, and UPS is charging battery), a HW "ON/Test" switch/button on UPS must be pressed to turn it on again as I guess. Remotely turning it on can not be performed, like Network Management Card, due to energy absence.


My question at this point is that APC UPSs have opportunity to carry this HW "ON/Test" switch/button to connector panel as a dry contact which can be opened/closed from a remote site (may be over a relay)? Assume that UPS is installed into a cabinet (where access to UPS is not easy) and the control of this cabinet  have to be done via a control panel (remote site).





Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of