Posted: 2023-01-30 10:42 AM
How to upgrade firmware or patch PDU against Ripple20 Treck TCP/IP Stack Vulnerabilities?
I have spent the last hour digging around on Schneider's horrible website trying to find a firmware update or patch for my APC AP8641 rack PDUs. They show up on nessus scans as vulnerable to Ripple20 due to their Treck TCP/IP Stack.
This web page seems to indicate that there is a firmware or OS update/patch for my model (AP86XX series PDU) that fixes these vulnerabilities. But they don't link to the patch. The links there to the release notes & presumably to the update/patch are dead links. (Nice work Schneider!)
https://www.apc.com/us/en/faqs/FA410359/
So I search their online support/documentation. No luck there either. The only download available for my model AP8641 is a security wizard CLI, which is great if I wanted to change the certificates or SSH keys. But that's NOT going to update the vulnerable TCP/IP stack.
Is there a patch for this vulnerability? If so why doesn't it come up when you search your support site? And an even better question: why doesn't this ridiculously overpriced powerstrip have an auto-update feature? A $5 Raspberry Pi Zero does. Why doesn't my $2,500 PDU?
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-15 10:34 AM
Any updates on this?
Adding in some "Top Experts" for assistance.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-15 12:54 PM
The 7.0.8 firmware can be downloaded at
The security handbook can be downloaded at
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-15 02:08 PM
I noticed that when the PDU turns on, outlets that were previously set to 'off' turn back 'on'. How can I keep these outlets off during a power cycle? @BillP
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-15 03:33 PM
In the Outlet Configuration I found a option to keep the Outlet from turning back on after the PDU has a power cycle event.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-05 08:24 PM
Looks like all the helpful inks in this posting are enow 404. I have been clicking around in the APC site for 30 min to find the firmware update for the AP8641 PDU.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-06 04:13 AM
You may use this APC Resource Link and scroll to the very bottom:
If this resolves your question please do mark this as a solution. So it may help the next person asking the same.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-19 08:40 AM
I looked and searched that page and am not finding information about updating the firmware.
I have received an email from support with a link, but it is kinda sad that I have to do the whole email dance just to find the instructions and files.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-20 03:12 AM
I don’t understand the firmware is literally at the very bottom of the page in the link.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-21 06:23 AM
Download it, extract it, execute it, follow the prompts.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-21 11:05 PM
Had to keep scrolling past the Documentation to get to the very bottom.