AOS firmware versions

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AOS firmware versions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:24 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
3
7132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:24 AM . Last Modified: ‎2024-03-18 11:30 PM

AOS firmware versions

Hello APC team,

I have 2 switched IPDU models;

AP7911A, which uses: Network Management Card AOS v3.7.4
(highest firmware supported version: 3.9.2)

AP7920B, which uses: Network Management Card AOS v6.4.6
(highest firmware supported version: 6.5.6)

  1. Is it possible for me to downgrade the AP7920B to version 3.7.4? If yes, where can I download that firmware?
  2. Is there an overview matrix of supported AOS for these two models?
  3. Is it possible to upgrade the AP7911A (or its B equivalent) to AOS 6.4.6 or the latest AOS 6.5.6? (My guess is; No)
  4. Where can I read the differences between all AOS firmwares? I only found separate changelogs.

Thank you for your help!

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:24 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
7131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:24 AM . Last Modified: ‎2024-03-18 11:30 PM

Hi Kevin,

I don't know if we have a single document that will answer your question but I'll explain best I can.

Basically, we have two major hardware/firmware platforms available referred to as Network Management Card 1 (NMC2) and Network Management Card 2 (NMC2). NMC1 had versions 1.X, 2.X, and 3.X over the years and has been phased out over the years as NMC2 was released almost 10 years ago now. NMC2 has had 5.X and 6.X firmware versions.

These products, like with a Rack PDU you have are embedded into the unit or with UPS's, are sometimes a SmartSlot card option you can purchase.

NMC1 and NMC2 are two totally different firmware and hardware platforms so the firmware is not interchangeable. With Rack PDUs specifically, we had AP7XXX models (some had A at the end of their SKU, like the AP7911A if a product change was made for whatever reason, maybe due to UL change. When AP7XXX models were upgraded from NMC1 to NMC2, a B was added to the end of their SKU if they weren't replaced by an AP8XXX next generation model already.

Also in general, the AOS is the APC Operating System. It contains all the specific functions for the system level of the product, such as HTTP/HTTPS, SCP, NTP, FTP, Email, etc. It is paired with an application file for whatever device you have so that the NMC can "talk" to the particular device. You can never upgrade just an AOS separately (unfortunately).

To answer your questions:

  1. Is it possible for me to downgrade the AP7920B to version 3.7.4? If yes, where can I download that firmware?
    • No, you cannot load NMC1 firmware on an NMC2 product.
  2. Is there an overview matrix of supported AOS for these two models?
    • I don't think so. It should be generally understood the differences I mentioned above so 1.X, 2.X, and 3.X firmware works with AP7XXX (or AP7XXXA) series and AP7XXXB models use 5.X or the modern 6.X firmware.
  3. Is it possible to upgrade the AP7911A (or its B equivalent) to AOS 6.4.6 or the latest AOS 6.5.6? (My guess is; No)
    • No. Unfortunately the NMC module in the AP7XXX is not field replaceable or upgradeable so you have to swap the entire Rack PDU to a different model.
  4. Where can I read the differences between all AOS firmwares? I only found separate changelogs.
    • Because of what I explained above, you'll only be able to find release notes for AOS/APP pairs, depending on what AOS is paired with a particular application version. There have been quite a few versions released but we can probably find old release notes online or through the archive.

If you're looking for general NMC1 vs. NMC2 differences, there are several. Here is what I know off the top of my head:

NMC2 has all new features like:

  1. On-board firewall
  2. SMTP email authentication and with SSL/TLS
  3. multiple users of each type with simultaneous login (advanced user management in general)
  4. faster hardware
  5. Of course some general bug and cybersecurity updates/features.
  6. Ability to download log files in .tar format for support

Between AOS 3.7.4 and AOS 3.9.2 for your AP7911A, we fixed and added support for TLS 1.0 and then I think there are a few other little bug fixes like with SNMP communication from what I recall.

Hope this helps. Let me know if you have any other specific questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:24 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
7132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:24 AM . Last Modified: ‎2024-03-18 11:30 PM

Hi Kevin,

I don't know if we have a single document that will answer your question but I'll explain best I can.

Basically, we have two major hardware/firmware platforms available referred to as Network Management Card 1 (NMC2) and Network Management Card 2 (NMC2). NMC1 had versions 1.X, 2.X, and 3.X over the years and has been phased out over the years as NMC2 was released almost 10 years ago now. NMC2 has had 5.X and 6.X firmware versions.

These products, like with a Rack PDU you have are embedded into the unit or with UPS's, are sometimes a SmartSlot card option you can purchase.

NMC1 and NMC2 are two totally different firmware and hardware platforms so the firmware is not interchangeable. With Rack PDUs specifically, we had AP7XXX models (some had A at the end of their SKU, like the AP7911A if a product change was made for whatever reason, maybe due to UL change. When AP7XXX models were upgraded from NMC1 to NMC2, a B was added to the end of their SKU if they weren't replaced by an AP8XXX next generation model already.

Also in general, the AOS is the APC Operating System. It contains all the specific functions for the system level of the product, such as HTTP/HTTPS, SCP, NTP, FTP, Email, etc. It is paired with an application file for whatever device you have so that the NMC can "talk" to the particular device. You can never upgrade just an AOS separately (unfortunately).

To answer your questions:

  1. Is it possible for me to downgrade the AP7920B to version 3.7.4? If yes, where can I download that firmware?
    • No, you cannot load NMC1 firmware on an NMC2 product.
  2. Is there an overview matrix of supported AOS for these two models?
    • I don't think so. It should be generally understood the differences I mentioned above so 1.X, 2.X, and 3.X firmware works with AP7XXX (or AP7XXXA) series and AP7XXXB models use 5.X or the modern 6.X firmware.
  3. Is it possible to upgrade the AP7911A (or its B equivalent) to AOS 6.4.6 or the latest AOS 6.5.6? (My guess is; No)
    • No. Unfortunately the NMC module in the AP7XXX is not field replaceable or upgradeable so you have to swap the entire Rack PDU to a different model.
  4. Where can I read the differences between all AOS firmwares? I only found separate changelogs.
    • Because of what I explained above, you'll only be able to find release notes for AOS/APP pairs, depending on what AOS is paired with a particular application version. There have been quite a few versions released but we can probably find old release notes online or through the archive.

If you're looking for general NMC1 vs. NMC2 differences, there are several. Here is what I know off the top of my head:

NMC2 has all new features like:

  1. On-board firewall
  2. SMTP email authentication and with SSL/TLS
  3. multiple users of each type with simultaneous login (advanced user management in general)
  4. faster hardware
  5. Of course some general bug and cybersecurity updates/features.
  6. Ability to download log files in .tar format for support

Between AOS 3.7.4 and AOS 3.9.2 for your AP7911A, we fixed and added support for TLS 1.0 and then I think there are a few other little bug fixes like with SNMP communication from what I recall.

Hope this helps. Let me know if you have any other specific questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:24 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
7129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:24 AM . Last Modified: ‎2024-03-18 11:30 PM

Hello Angela,

Thank you very much for your detailed and thorough answer, it quickly helped me move forward!

Reply

Link copied. Please paste this link to share this article on your social media post.

Marvin1
Marvin1
Cadet

Posted: ‎2025-03-21 08:13 AM

0 Likes
0
2426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-21 08:13 AM

Hi thanks for this intersting support. I have also a 2018's AP7920B pdu and i'm facing an issue regarding the firmware update. Where can i find the 6.5.6 release ? The only one found is the 7.1.4 and it's doesnt work. thanks in advance for your support.

BR 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore