APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Hello;
Please support me:
I have a UPS with NMC2 included. I logged in NMC2 via web-interface:
- Remaining time (UPS): 1h20min
- How do I configure in NMC2 to shutdown UPS after 5 mins ? (Note: do NOT use PCNS)
The scenario is:
When power supply is cut off, after 5 mins, the UPS shuts itself down automatically.
Thank you.
SURT.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Hi,
Is the model of the Smart-UPS SURT, SRT, or SURTD? If the model is SURT then I apologize but the outlet group information I provided earlier is not available on the model. The only way to get a SURT model Smart-UPS to power down after being on battery for 5 minutes is through a software application running on a computer system.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Hello;
Who can support me ?
Regards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
you probably got no answer because it is in the instructions.
Configuration > Outlet Groups in the NMC then choose your shutdown options.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Hi,
For more information on this open the NMC web interface and go to Configuration - Outlet Groups then select help. the load shedding section discusses how to power down the UPS / outlet group/s
Configuration:Outlet Groups | |
Outlet Group Settings: Click the name of an outlet group (the default name or, if already configured, the configured name) to configure or change the following parameters for the outlet group: | |
Name | A descriptive name for the outlet group (for example, a description of the devices connected to this outlet group). The name is displayed with the outlet group number wherever the interface displays that outlet group number. |
Sequencing | Use these settings to define how the UPS responds to a command issued by a user. For more sequencing information refer to Switched Outlet Groups on SMT and SMX Smart-UPS. |
Power Off Delay | When this outlet group is on, it waits this delay before turning off when "Off with Delay," "Reboot with Delay," or "Shutdown with Delay, AC Restart" is selected as the action for this outlet group. (During a delayed reboot, the outlet group then waits the number of seconds configured as Reboot Duration and Power On Delay before it turns on.) |
Reboot Duration | When this outlet group is on, it uses this delay as follows:
|
Power On Delay | When this outlet group is off, it waits this delay before turning on when "On with Delay," "Reboot" (with or without delay), or "Shutdown, AC Restart" (also with or without delay) is selected as the action for this outlet group. |
Minimum Return Runtime | UPS must be able to provide battery power for this long before turning the outlet back on after a power failure. This can be used to ensure that attached loads have enough time to safely shut down if AC utility power fails again. For example, if the minimum returnruntime were 50 seconds:
|
Load Shedding |
Use these settings to automatically shut down an outlet in response to one or more conditions. To enable a condition, mark its checkbox and configure its value; you can enable multiple conditions.
If you use PowerChute Network Shutdown (PCNS) on this outlet, be sure "Skip outlet off delay" is not checked so that PCNS clients can safely shutdown. Also, each PCNS client has its own set of conditions that may be configured to start a shutdown. |
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Thank you for your supports.
Please make me clearly, why configurating outlet groups makes UPS shutdown ? My mean is when I turn UPS on, and then unplug, after 5 min., I want the UPS off automatically.
BRs;
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: 2024-03-18 03:41 AM
Hi,
Is the model of the Smart-UPS SURT, SRT, or SURTD? If the model is SURT then I apologize but the outlet group information I provided earlier is not available on the model. The only way to get a SURT model Smart-UPS to power down after being on battery for 5 minutes is through a software application running on a computer system.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.