How to replace the APC network management card AP9631 on Smart-UPS RT 15000 XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to replace the APC network management card AP9631 on Smart-UPS RT 15000 XL
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:23 AM

0 Likes
4
12527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:23 AM

How to replace the APC network management card AP9631 on Smart-UPS RT 15000 XL

Hi All,

I Need to replace a network management card on the working UPS.

But I don't know if I should to turn off the UPS in order to replace the Network Card.

Could somebody provide me an instructions? or forward to the Manual on the APC page?

Thank you

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:22 AM

0 Likes
0
12515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:22 AM

I would just not even worry about it for your UPS and go ahead and remove/install the Network Management Card. As long as the UPS is operating properly and there are no faults, there is virtually no risk.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:23 AM

0 Likes
0
12515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:23 AM

Hi Andrey,

It's always safest to remove power completely from the unit before removing and replacing the NMC.  I believe APC even says to power the system down, including removal of AC, disconnecting the batteries, and "brain deading" (holding down the power on button until a click is heard) the unit.

That being said, I personally have replaced and installed NMCs without removing power with no ill effects.  It all depends on how much risk you are willing to accept.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:23 AM

0 Likes
0
12515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:23 AM

Larger UPS models like this offer hot swappable SmartSlot accessories.

The Network Management Card itself is made to be hot swappable but it just generally depends on the UPS type. To be completely honest, I think majority of modern UPS models that support SmartSlot accessories are technically hot swappable but my personal belief is that they really just haven't updated the documentation to clarify and err on the side of caution.

I also can't remember the last time I actually "braindead" the UPS to install a SmartSlot accessory (which is yes, powering down the UPS completely and removing AC power and then depending on the model, removing the battery or discharging the capacitors). Other UPSs also say to put the UPS into bypass to install/remove an accessory and then take it out of bypass when you install or remove it.

I would only suggest caution when you have other problems that may warrant a judgement call, such as a UPS with a fault or weird scenario where installing a Network Management Card would cause more problems or potentially damage the management card itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:22 AM

0 Likes
0
12516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:22 AM

That is what I found in the NMC installation guide:

You do not need to turn off power for a Symmetra UPS.

Step 1: Turn off power (Smart-UPS)

Caution: Damage to the UPS or the Network Management Card

can result if you do not remove all AC and DC power from a

Smart-UPS.

What does it mean for my case?

Will be enough just put the UPS in bypass mode? Or is there any manual especial for my UPS system?

I don't have a powerOFF button on my APC Smart-UPS RT 15000 XL. I can only shutdown APC via management display.

After powering OFF should I also unplug the battery pack from UPS? or just the shutdowning will be enough?


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:22 AM

0 Likes
0
12516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:47 AM . Last Modified: ‎2024-03-12 03:22 AM

I would just not even worry about it for your UPS and go ahead and remove/install the Network Management Card. As long as the UPS is operating properly and there are no faults, there is virtually no risk.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of