How to recover from a lost password for the ACRP101

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to recover from a lost password for the ACRP101
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:07 AM . Last Modified: ‎2024-03-18 03:47 AM

0 Likes
3
2395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:07 AM . Last Modified: ‎2024-03-18 03:47 AM

How to recover from a lost password for the ACRP101

I have a ACRP101 unit that I have lost the apc password to. I was so excited to see in the documentation, steps to reset back to the default apc|apc... Unfortunately, following the steps I am not able to get the password reset. HT connects, I see the Username prompt, flick the power for a second and press return until i get a username prompt... trying apc | apc fails to login.

Anyone have an idea where I am going wrong in this password reset steps or have experienced this as well and recovered the default password.

Thanks!
Todd

__________________________________________________________________________________
__________________________________________________________________________________

Here are the steps from the Operations Manual for InRow RP DX

How to Recover From a Lost Password
You can use a local computer, a computer that connects to the Network Management Card or other
device through the serial port to access the control console.
1. Select a serial port at the local computer, and disable any service that uses that port.
2. Connect the APC modem cable (APC part number 940-0103) to the selected port on the computer and to the serial port at the InRow RP
(use the DB-9 connector on the front of the electrical panel).
3. Run a terminal program (such as HyperTerminal) and configure the selected port as follows:
– 9600 bps
– 8 data bits
– no parity
– 1 stop bit
– no flow control
4. Press ENTER on the computer, repeatedly if necessary, to display the User Name prompt.
If you are unable to display the User Name prompt, verify the following:
– The serial port is not in use by another application.
– The terminal settings are correct as specified in step 3.
– The correct cable is being used as specified in step 2.
5. Switch the main breaker to OFF. Wait one second. Switch the main breaker to ON.
Note: If you wait too long to return power to the Cooling Unit, you must repeat step 5.
6. Press ENTER as many times as necessary to redisplay the User Name prompt, then use the default,
apc, for the user name and password. (If you take longer than 30 seconds to log on after the User
Name prompt is redisplayed, you must repeat step 5 and log on again.)
7. From the Control Console menu, select System, then User Manager.
8. Select Administrator, and change the User Name and Password settings, both of which are
now defined as apc. Select Accept Changes to store the new user name and password values.
9. Press CTRL+C, log off, reconnect any serial cable you disconnected, restart any service you
disabled, reinstall the lower air filter, and replace the rear panel.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 05:07 AM . Last Modified: ‎2024-03-18 03:47 AM

0 Likes
0
2395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:07 AM . Last Modified: ‎2024-03-18 03:47 AM

The one part they don't mention is that besides only accepting the default apc/apc password for 30 seconds after starting up, it also only happens every other time you reset the device. If you look at the LEDs on the ethernet port, during one startup they will flash orange/green and the next time you startup, they will be off. The apc/apc default only works when the ethernet LEDs are off during startup.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 05:07 AM . Last Modified: ‎2024-03-18 03:47 AM

0 Likes
0
2396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:07 AM . Last Modified: ‎2024-03-18 03:47 AM

The one part they don't mention is that besides only accepting the default apc/apc password for 30 seconds after starting up, it also only happens every other time you reset the device. If you look at the LEDs on the ethernet port, during one startup they will flash orange/green and the next time you startup, they will be off. The apc/apc default only works when the ethernet LEDs are off during startup.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:08 AM . Last Modified: ‎2024-03-18 03:47 AM

0 Likes
0
2395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:08 AM . Last Modified: ‎2024-03-18 03:47 AM

Thanks Voidstar!

This was the answer, you have to remove the cover on my model to see the ethernet connectivity lights but the second flick of the main breaker allowed the password to be reset.

APC...please update your documentation, this is too easy an issue to have jack with incomplete steps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:08 AM . Last Modified: ‎2024-03-18 03:46 AM

0 Likes
0
2395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:08 AM . Last Modified: ‎2024-03-18 03:46 AM

Hello
We have an APC Inrow RP and I've forgotten the password to enter the management console, the recovery process step by step guide on APC did, unfortunately, the result reached. Please help me

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore