How to install NMC2 (AP9631) in Symmetra PX 48kW All-in-one UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to install NMC2 (AP9631) in Symmetra PX 48kW All-in-one UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

0 Likes
4
2696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

How to install NMC2 (AP9631) in Symmetra PX 48kW All-in-one UPS

I've recently acquired and Network Management Card 2 and I want to install it in a Symmetra PX. I acquired this card because 1) I want to use the external temperature sensor 2) I want to connect it to the dry contact I/O accessory to connect it to my 3rd party environment monitoring system. The UPS already pre-installed with a network management interface (the one with the RJ45 for LAN connection, DB-9 connector and RJ45 connection for the LCD display) located on the top slot of the left column (3 vertical slots available). I've installed the AP9631 on the top slot and middle slot of the right column and can access the NMC2 and assign the IP address. However, an error came up "lost the local network management interface to ups communication" and I can get no other parameter readings (i.e. temp, voltage, etc). This appear on both the preinstalled network interface card and the NMC2. When I took out the NMC2, the pre-installed card connection to the UPS is restored. Any ideas of how to get it to work? Do i need to upgrade / downgrade the NMC2 firmware?

This is the NMC2 details:

Hardware Factory
Model Number: AP9631
Serial Number: ZA1215011080
Hardware Revision: 05
Manufacture Date: 04/04/2012
MAC Address: 00 C0 B7 61 57 38
Management Uptime: 0 Days 0 Hours 4 Minutes


Application Module
Name: sumx
Version: v5.1.7
Date: Dec 1 2011
Time: 13:01:45




APC OS (AOS)
Name: aos
Version: v5.1.7
Date: Nov 22 2011
Time: 09:53:57




APC Boot Monitor
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 48kw
  • ap9631
  • nmc2
  • px
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

0 Likes
0
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

sure - in FA156047 that i mentioned, use the manual FTP instructions for NMC2 and it will allow you to do it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

0 Likes
0
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

Hi there,

My NMC2 firmware is already v5.1.6, when I tried to upgrade using the sy3p514 firmware, the utility produces an error saying downgrading AOS is not allowed? any clues to overcome this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

0 Likes
0
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

I don't know whether multiple management cards are supported in the Symmetra PX - that's outside my experience as an end user.

However, I do see that your AP9631 has the "sumx" application module (for Smart-UPS and Matrix models). I believe the application module you need is "sy3p" for the Symmetra PX ("sy" for other Symmetra models). You'll need to update the firmware on the AP9631 for it to understand the Symmetra. Whether that will solve the issue with 2 management cards, I don't know - we'll have to wait for someone from APC to respond.

Edited to add: Upon looking at your picture, I see you have a number of blank filler covers missing. For optimal cooling, you want to install blanks wherever needed (this would include battery / power module slots as well as the management slots). This will also reduce any electrical interference (emitted or received). This has nothing to do with the issue you're having, but I thought I should mention it.

Message was edited by: Terry Kennedy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

0 Likes
0
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

yes, terry is correct. you have the wrong application module installed on the card. you do need sy3p application for symmetra 3 phase. this can be solved with a simple firmware upgrade. just go to http://www.apc.com/tools/download/index.cfm and look for Firmware Upgrades - Network Management Card and look for the latest release of SFSY3P514 I believe it is.

instructions on updating firmware are located in our knowledge base (www.apc.com/site/support/index.cfm/faq/) in article FA156047.

as far as the install order, take a look here: http://www.apcmedia.com/salestools/ASTE-6Z5QFC_R1_EN.pdf

FYI - up to (2) NMC's may be installed into one UPS. the install order does matter when you have multiple accessories.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

0 Likes
0
2696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:56 AM . Last Modified: ‎2024-03-06 12:05 AM

sure - in FA156047 that i mentioned, use the manual FTP instructions for NMC2 and it will allow you to do it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore