How to get manual IP address to take

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to get manual IP address to take
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
19
9358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

How to get manual IP address to take

I just added a network card to my APC UPS.  I successfully logged in to it and changed the IP address to my liking. I was warned that I needed to reboot.  (I have an opinion on any software that requires you to reboot to change the IP address. And software that doesn't tell you beforehand). It was exceptionally inconvenient at that point.  The next day I did a planned shutdown of my servers and a full-power-down of the UPS, just like when I installed the card.  I thought that would be equivalent to a reboot.  Apparently not.

I managed to connect to it via the serial port and see:

Active IPv4 Settings

--------------------

  Active IPv4 Address:          0.0.0.0

  Active IPv4 Subnet Mask:      0.0.0.0

  Active IPv4 Gateway:          0.0.0.0

Manually Configured IPv4 Settings

---------------------------------

  IPv4:                 enabled

  Manual Settings:      enabled

  IPv4 Address:         192.168.7.242

  Subnet Mask:          255.25.255.0

  Gateway:              192.168.7.1

  MAC Address:          00 C0 B7 85 05 C7

  Domain Name:          example.com

  Host Name:            apc8505C7

I don't see any commands that reboot the card or activate the assigned IP.  How does one work the magic?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

It's a Smart-UPS 2200. About:

Model Number:           AP9630

Serial Number:          ZA1411031484

Hardware Revision:      05

Manufacture Date:       03/18/2014

MAC Address:            00 C0 B7 85 05 C7

Management Uptime:      0 Days 0 Hours 1 Minute

Application Module

---------------

Name:                   sumx

Version:                v6.0.6

Date:                   Apr  5 2013

Time:                   11:25:39

APC OS(AOS)

---------------

Name:                   aos

Version:                v6.0.6

Date:                   Apr  5 2013

Time:                   10:36:37

APC Boot Monitor

---------------

Name:                   bootmon

Version:                v1.0.2

Date:                   Jan 21 2010

Time:                   13:35:57

The eventlog showed me the real (first) problem; the IP address should have been 251, there's already a 252 on the network.  So I changed that and now I get on the serial interface:

Active IPv4 Settings

--------------------

  Active IPv4 Address:          192.168.7.251

  Active IPv4 Subnet Mask:      255.255.255.0

  Active IPv4 Gateway:          192.168.7.1

And in the initial screen I see "Stat : P+ N4+ N6+ A+". The Web command shows the usual ports 80 and 443. I can ping it from this computer. But in Network Shutdown I get "Cannot connect to http://192.168.7.251:80"  and the Device IP Configuration Utility does not see it.


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 19
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

HI, in order to figure out what's going on it would be helpful to post the exact model # of your ups (or at least its "Family" eg "Smart-UPS RT" or "Symmetra") and the model and firmware revision of the network card.

...off the top of my head though, for many ups families, powering down the UPS does not completely remove power to the network card unless the batteries are physically disconnected as well...eg Smart-UPS still power the network card when switched off and batteries are connected.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

I have a feeling the card has a problem because you made a typo in your subnet mask. Note you have 255.25.255.0. I say that because it will put the gateway to 0.0.0.0 too for this type of thing sometimes (Why is my Network Management Card's default gateway showing as 0.0.0.0 under Current IPv4 settings? ...), depending on what particular configuration is and what is incorrect. You could just fix it with tcpip -s 255.255.255.0 without having to also do the IP and gateway again and then do the reboot command.

If that simple change does not fix it, can you give me the output of the eventlog command (at least the recent applicable events) and about so I can see what firmware you have? I believe you have v6 firmware based on the output I can see of the tcpip command but just double checking.

For network settings typically, you can manually issue the reboot command to activate these settings (which only reboots the card, not the UPS) and then also, it should've rebooted automatically for these pending changes when your session ended. Also, when you turn your UPS off, the Network Management Card does not lose power until the UPS has been braindead which will happen when the UPS is without AC power for 8-10 minutes and capacitors have discharged. Only then, when the UPS brains are completely dead, will the accessory in the SmartSlot be turned off. So, I don't know if in you're scenario, that state happened.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

I just added a network card to my APC UPS.  I successfully logged in to it and changed the IP address to my liking. I was warned that I needed to reboot.  (I have an opinion on any software that requires you to reboot to change the IP address. And software that doesn't tell you beforehand). It was exceptionally inconvenient at that point.  The next day I did a planned shutdown of my servers and a full-power-down of the UPS, just like when I installed the card.  I thought that would be equivalent to a reboot.  Apparently not.

I managed to connect to it via the serial port and see:

Active IPv4 Settings

--------------------

  Active IPv4 Address:          0.0.0.0

  Active IPv4 Subnet Mask:      0.0.0.0

  Active IPv4 Gateway:          0.0.0.0

Manually Configured IPv4 Settings

---------------------------------

  IPv4:                 enabled

  Manual Settings:      enabled

  IPv4 Address:         192.168.7.242

  Subnet Mask:          255.25.255.0

  Gateway:              192.168.7.1

  MAC Address:          00 C0 B7 85 05 C7

  Domain Name:          example.com

  Host Name:            apc8505C7

I don't see any commands that reboot the card or activate the assigned IP.  How does one work the magic?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

Neither Firefox nor Explorer can connect to ports 80 or 443.  FileZilla (FTP) reports ""ECONNREFUSED - Connection refused by server" on port 21. Telnet works and gives me the same interface as the serial port. No proxies nowhere.

Now it's worse.  I tried "resetToDef -p keepip" and I can't log in on telnet or serial:

User Name : apc

Password  : ***

User Name : apc

Password  : ***

... ad infinitum

This is really frustrating.  I've been networking for too many years and I've never seen such a crummy kludge. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

It's a Smart-UPS 2200. About:

Model Number:           AP9630

Serial Number:          ZA1411031484

Hardware Revision:      05

Manufacture Date:       03/18/2014

MAC Address:            00 C0 B7 85 05 C7

Management Uptime:      0 Days 0 Hours 1 Minute

Application Module

---------------

Name:                   sumx

Version:                v6.0.6

Date:                   Apr  5 2013

Time:                   11:25:39

APC OS(AOS)

---------------

Name:                   aos

Version:                v6.0.6

Date:                   Apr  5 2013

Time:                   10:36:37

APC Boot Monitor

---------------

Name:                   bootmon

Version:                v1.0.2

Date:                   Jan 21 2010

Time:                   13:35:57

The eventlog showed me the real (first) problem; the IP address should have been 251, there's already a 252 on the network.  So I changed that and now I get on the serial interface:

Active IPv4 Settings

--------------------

  Active IPv4 Address:          192.168.7.251

  Active IPv4 Subnet Mask:      255.255.255.0

  Active IPv4 Gateway:          192.168.7.1

And in the initial screen I see "Stat : P+ N4+ N6+ A+". The Web command shows the usual ports 80 and 443. I can ping it from this computer. But in Network Shutdown I get "Cannot connect to http://192.168.7.251:80"  and the Device IP Configuration Utility does not see it.


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

Ok, this is good progress.

So, outside of network shutdown, does putting the IP address in the browser work at all (maybe trying different browsers)? I'd also verify if any proxy server settings could be interfering. Can you try telnet or FTP to see if those work? You could also try a direct connection to it via a crossover ethernet cable if you cannot get to it from any computer to see if that works.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

Don't shoot the messenger but v6.0.6 has several issues that we are aware of and working on a release for next month. One of those issues revolves around the reset to defaults not working properly. Did you have a different username/password before upgrading to v6? (or did your card come with v6)? Basically, because of some differences between v5 and 6, this can happen. More info here -> v6.X.X Network Management Card 2 "Reset All" or "Reset to Defaults" Command Does Not Work | FAQs | S.... I would actually recommend we get you to 6.1.1 eventually which is out and fixes three critical issues that you may also encounter. Info here -> Network Management Card 2 Firmware v6.X.X FAQ/Upgrade Issues | FAQs | US

I promise it will get better embarassed

If this were me, and to save time if you can do it, I would just format this card (wipe it COMPLETELY besides firmware) since you have serial access and blow everything away, reconfigure the IP and anything else, and just go ahead and try again. To format, since you cannot log in (where there is typically a CLI command to format), then press and hold the pinhole reset button on the front of the card for 20 seconds. I would hold the paperclip device or whatever you use to press the pinhole reset button to the top edge of the card (if it is installed horizontally in your UPS) or to the right I think if it is vertical to best align the paper clip. It should "pulse" green if you're doing it right and making contact with the little button and then release when it turns orange. Then, it should be reset, you'll be able to log in, and then re-do TCP/IP, reboot it, and see if you can get in.

Again, format wipes everything in flash - so any current settings you may have put on there. I think to avoid further frustration with any of these problems, it will be the best option cry

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

The card came with the firmware it has.  I did not change the card username or password from the default apc. 

I tried the password recovery using the reset button, described on page 4 of the manual.  No effect.

I've reset many a router with the reset button and this looks about the same.  I tried it three times holding the button down for 40 counted seconds.  Every time both lights turned off while the paperclip was in.  When I released it the lower orange light came on solid, then flashing,, then the upper light flashed green/orange for a few seconds, then went to solid green.  It had no effect any of the three times. Still cannot communicate with the card by any means


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

I can feel the button actuating, but no lights are on while it's actuated.  I've tried all sorts of different angles and wiggling with no effect. This baby's locked solid.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

Did you see the correct LED combination when doing the reset of the password? You press it once, within 5-7 seconds (which feels like forever) then the LEDs start alternating green and orange then you press it again and the LED goes off? Then get to log in again within 30 seconds with apc/apc? That definitely should work and I'd want to know if the LEDs responded accordingly. I also don't think it'd hurt to take out the card and look at the reset button to make sure it is not loose or anything.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

Green goes out, orange flashes, orange turns off.  On the second press orange flashes then green comes on. Never any alternating green/orange.

The manual that came with the card states that removal or insertion of the card requires shutting down the servers that are on the UPS and removing UPS power completely.  Are you a representative of APC stating officially that I can ignore the manual?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

Yes, here is more updated information -> http://www.schneider-electric.com/support/index?page=content&country=US〈=en&id=FA156132

And we're talking about the status LED, right, the one next to checkmark and X? The combination does not sound right or we are looking at the wrong LED.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:57 AM . Last Modified: ‎2024-03-05 12:04 AM

So my card shipped with an out-of-date manual.  Heckuva job, APC. And I can't remove the coin battery.

There are only two freakin' LEDs on the back of the card, one is orange and one is orange/green.  Of course I'm talking about the one next to the checkmark and X.  And the combination is wrong but the card is still inaccessible.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:04 AM

59 MB movie: MEGA

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:04 AM

Off to the dentist.  No more physical interactions till Monday.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:04 AM

0 Likes
0
9353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:04 AM

The coin battery is not removable, you're right. And it only keeps the date and time, no settings, so it shouldn't be a worry.


Thank you for the video but the procedure was done wrong from what I saw embarassed

You're pressing it too early for the second press and also when the link LED comes back on after the first press which is incorrect. Press it the first time, watch the status LED (yes, with the checkmark and the X) - it will go out as I saw in the video it did properly, and when that one comes back on alternating rapidly green/orange as it did towards the end of the video, which will take 5-7 seconds, press the reset button a second time. The link LED comes back on almost immediately (maybe a half second) after the first press so just ignore that. If it is also easier, you can remove the network cable temporarily. With what I saw in the video, you're just telling the card to reboot twice in a row because of the incorrect timing.

If you're interested, I can give you a call Monday and walk through it with you or help with anything else once we get past the password reset.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:03 AM

0 Likes
0
9351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:03 AM

OK, it's Monday.  I realized I rushed the password reset in the video.  So I tried again, and waited until the green/orange flashing, and it worked.  I'm in.

For a short time.  I issued the eventlog command and it froze.  I had to pull the card to un-freeze it.  And then I had to do the password reset again. I finally figured out that I had to do the password reset *every* *time* I want to log in.  Anyhoo, I reserved the desired IP address at the DHCP server, did a format and reboot and now I can connect. And I haven't needed to do a password reset.

Of course the card is not visible in Device IP Configuration or Power Chute Network Shutdown. That's far too much to ask.

And just for lagniappe, it's crashing approximately every four minutes.  The green LED goes off, then comes on flashing green/orange and when I log in the uptime is zero days zero hours zero minutes.

This is not getting better.  Has anyone anywhere anytime actually gotten this POS to work?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:03 AM

0 Likes
0
9353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:03 AM

The password reset only resets the credentials temporarily back to apc/apc. You are supposed to log in, then use the user command to reset and save them to what you want so that you don't have to do the procedure every time.

Did the reboot loop start after you configured one specific thing? It sounds like you formatted but didn't do much else configuration so I just want to verify if the card reboots with little configuration beyond you setting it for DHCP or after you re-did most of your configuration. If you just want to get on with this, I can also provide an older firmware v5.1.7, if you want to try that to see if it helps so you can just move on with using the card.

If you still want to use this firmware, then it'd be helpful if you can do the logzip command (or go to About->Support in the web) and generate the logs and download them and provide them to me so I can see about the reboot. If you do it via logzip command, you'll issue that command, then go to the FTP interface and the /dbg directory and retrieve debug_ZAXXXXXXXXX.tar or whatever the file name is there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:03 AM

0 Likes
0
9353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:58 AM . Last Modified: ‎2024-03-05 12:03 AM

The reboot loop started after I did the format.  It set itself to use DHCP. All I've changed since then is the domain name and time.

Please remember that the web interface and FTP do not work.  Filezilla:

Status:    Connecting to 192.168.7.251:21...

Status:    Connection established, waiting for welcome message...

Error:    Connection timed out

Error:    Could not connect to server

Status:    Waiting to retry...

Status:    Connecting to 192.168.7.251:21...

Error:    Connection timed out

Error:    Could not connect to server

Status:    Connecting to 192.168.7.251:21...

Status:    Connection established, waiting for welcome message...

Error:    Connection timed out

Error:    Could not connect to server

Status:    Waiting to retry...

Status:    Connecting to 192.168.7.251:21...

Error:    Connection timed out

Error:    Could not connect to server


WinSCP doesn't work either. 


But I managed to screencap quite a bit of the log.   MEGA


We could try the firmware if it takes less than four minutes to install.  Otherwise I bet it'll crash in the middle. jfleming at bptc.com.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of