How to enter configuration mode on Smart-UPS C1000

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to enter configuration mode on Smart-UPS C1000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
17
7596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

How to enter configuration mode on Smart-UPS C1000

My new SMC1000 unit works fine, except that I can't seem to get to Configuration Mode. Pressing and holding down the Mute and Menu buttons causes the unit to go on battery power for a short while.

But then pressing the Menu button (immediately, I understand about not waiting 15 seconds) merely cycles the display among

Events

Estimated run time

Load in watts

Load %

Load in VA

Out amps

Out volts

Out Hz

In volts

At a minimum, I want to dim the LCD display; but I'd like really to be able to use the full set of configuration options. Would appreciate advice on how to do that.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

Hmm, I replied, but I don't see it..

Anyway, I am glad you got it upgraded.

By the way, SMC1000 filename is just a coincidence. The filenames actually go by the "ID" we give units to determine what they are beyond the SKU the customer references. SMC1000 and SMC1005 file names actually refer to ID 1000 and ID 1005. Your unit is an ID1005 and there are other SMC models that are ID1000 that would use the other file.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 17
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

My new SMC1000 unit works fine, except that I can't seem to get to Configuration Mode. Pressing and holding down the Mute and Menu buttons causes the unit to go on battery power for a short while.

But then pressing the Menu button (immediately, I understand about not waiting 15 seconds) merely cycles the display among

Events

Estimated run time

Load in watts

Load %

Load in VA

Out amps

Out volts

Out Hz

In volts

At a minimum, I want to dim the LCD display; but I'd like really to be able to use the full set of configuration options. Would appreciate advice on how to do that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

This might be a firmware issue that I'll have to double check on.

Can you tell me what firmware is on this UPS? I think you'll have to get that via PowerChute if you have that going/installed since this UPS cannot report it via its display unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

Ok, well what we are thinking is this may be an issue in the older UPS 09.3 firmware. I know you just bought this to replace your Back UPS and UPS firmware 09.8 is the current for this UPS per How do I update the firmware of my SMT, SMX, or SMC series Smart-UPS? | FAQs | Schneider Electric US

So what I am wondering if you can do is use the firmware upgrade wizard in that article (which tells you the firmware when you connect to your UPS before you start), tell me what the firmware is first or note it) and if anything, a firmware upgrade should fix this. When you upgrade, your UPS output will need to turn off so plan accordingly and I'd suggest we remove anything from the UPS that won't be OK if we turn it off (like your computer). If it is already at UPS 09.8 for the version when you start, I need to know that so I can say there is still an issue somehow with UPS 09.8 and look at it further.

In regards to your serial number, I'll need to know it specifically if you look at it and it is something that does not begin with like XX1330 or newer (13 indicating 2013 build year and 30 indicating week 30). I'd be concerned if you bought a new UPS and it was not manufactured within the last 3-4 months since the typical lead time from manfacturing to user is around 3-4 months via reputable distributors or APC direct.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

Per the paper record of the QA test run October 18 2013 on this unit, the serial number starts with AS1342, so it looks like it was built and tested last October.

I'm guessing I need to reattach the USB cable to run the firmware app; will try to do that this weekend.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

According to the "wizard", the firmware versions are

UPS 09.6

MCU 02.0

UBL 01.2

MBL 02.0

The firmware upgrade to 9.8 looks somewhat disruptive (since everything is now plugged into the UPS, including some devices that get very cranky if they lose power), and all I want to do is use the configuration options. So I'm thinking that unless 9.6 is defective in some way, it might be a simpler alternative to find the documentation for it and use that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

Or can I do the configuration changes via the PowerChute software?  That would probably be the most convenient and least disruptive approach if available.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

Yes, well the issue is what you were doing should bring up configuration mode. And yes, the firmware upgrade can be disruptive - as I noted, it will require the UPS output to be turned off. Our best bet long term would be to upgrade to UPS 09.8 to see if the buttons still do not work but in the short term, PowerChute Business Edition should allow you to configure most items if not more than the front panel.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

ronks:

I also experienced the exact same thing as you. The firmware upgrade proceeded to begin and then out of nowhere this Windows driver started installing, which did complete successfully. But, it interrupted the firmware upgrade and caused it to fail. Windows then asked me to restart, which I did. It should be noted that this driver notification occurred within the first 10% of sending the file to the UPS. I had no choice but to abandon the firmware upgrade, reboot and try again. I believe APC Support should investigate this as it is not good.

I was able to power-on the UPS again (the firmware process powered it down), re-run the firmware upgrade process and this time the firmware upgraded successfully. However, I should note that I still saw the driver installed AGAIN even after the second go-around on the firmware upgrade. But, for whatever reason, the driver install did not interrupt the firmware upgrade process.

I'm at rev 09.8 now. So, now I just have to figure out how to auto-DIM the LCD panel...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

I have a few questions so we can ask someone to investigate

  • Can you give specifics of what version of Windows OS you're using where you saw this behavior?
  • And you downloaded the version of the Firmware Upgrade Wizard in the knowledge base available today?
  • This was via USB?
  • Did you happen to see any details about what driver was trying to install itself?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

I wouldn't discount the possibility that I'm just doing something wrong.  😕

Still, I held down the Mute and Display buttons, and all that happened was that the UPS went to battery for a few seconds (according to the panel display).

And I see that holding down Display for a few seconds toggles between Auto Dim and panel always on.

But about PowerChute Business Edition on my CD; I'm unclear if I need to install all three of the Agent, the Server, and the Console components.

I have one UPS powering one Windows PC; which components are appropriate for this setup?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

I will check my unit again tomorrow to see what it does. I had asked someone more familiar with the unit last time who had known of a problem with getting into configuration mode and that it sounded likely it was not working.

For your set up - you can just use the PowerChute Business Edition Agent.

Once you install it, I think it puts a shortcut on your start menu but if not (incase that's just PowerChute Network Shutdown), just go to a web browser on your computer and access the Agent service via https://127.0.0.1:6547 or http://127.0.0.1:3052. There will be a web page you can log into with the username and password you set up in the installation process.

Let me know if you have trouble.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

Thanks! I see that the PowerChute software lets me adjust transfer voltage levels, power-quality sensitivity, and alarm muting if I want to. From the 2011 edition of the SMC1000 user manual, I found how to auto-dim the LCD display (which is actually the one thing I was after). The only missing adjustment is toggling "Green Mode", which I can probably live without, since I don't know what an AVR component is. Other than that, "Configuration Mode" seems to be just a way of grouping the options.

My guess is that all the settings are really available, but I don't have the right documentation for the 09.6 release of the firmware. Obtaining that seems simpler than doing a firmware upgrade to 9.8; do you know if it's available?  Or if there is some other reason to upgrade?  Given the hinky nature of the user guides, I'm not sure an upgrade would resolve the issue and I could end up with a very large corded doorstop if anything goes wrong.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

I really suggest considering updating the firmware. I'll explain.

From what I understand, UPS 9.6 has a few different issues and we'd really recommend updating to avoid them. The regular user's guide supposedly focuses at UPS 09.8 and then the manual addendum focuses on UPS 09.8 changes (all at http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SMC1000&tab=documentation).

Now, it is true you can do all of this via PowerChute and if you want to do that, that's fine too. If you follow the instructions and the firmware upgrade does not work, then don't worry about it and I'll take care of it wink

The struggle I have is UPS 09.6 is old news in development so I can't find much out about it and everything is for UPS 09.8. For instance, apparently they changed how you get to Configuration mode.

P.S. AVR is Automatic Voltage Regulation. Disabling green mode has no benefit unless you have a lot of THD (Total Harmonic Distortion) or a heavy load because it can reduce transfer times to battery by ~1ms - so the typical user does not need to disable this.

Let me know if you have further questions. I think your best bet is to upgrade now and then you'll be all set and things are more stable.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

OK, I am persuaded. I'll look into the logistics of the upgrade this week. I assume that everything now on the UPS will need to be unplugged during the process.

Poking around in the 9.8 release notes, I see one of the changes from 9.6 is "To Implement Configuration mode on the LCD", which explains the discrepancy.

(I have to say it is a little odd for a brand new unit to come with an older release of firmware, though. Somebody should have a word with the factory.)

Thanks for your assistance with this.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

You're welcome. Depending on the time frame of release, sometimes they will re-upgrade them or let the user do it since these are field upgradable. I am just speaking from dealing with UPS Network Management Cards. What we do there is release the firmware, then for brand new units being manufactured, they get flashed with the latest but we don't go back and re-open boxes and reflash ones that were already made since the user is able to. I understand what you mean though but at least we can upgrade it cool

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
7595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

OK, done. The upgrade for some reason required SMC1005UPS_09-8.enc and rejected SMC1000UPS_09-8.enc even though the unit is a SMC1000. Then it ran for about 15 minutes, and failed, saying it could not establish communication with the unit and I now had firmware level (    ). Not so good. But I noticed that a driver was installed to Windows in the middle of the upgrade, so I just reran it and it completed successfully. I'll leave out the details of crawling under the desk unplugging and replugging everything. Anyway, it is now at 9.8 and the "Configuration mode" works as advertised. Time to break out the champagne.  🙂  

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
7596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

Hmm, I replied, but I don't see it..

Anyway, I am glad you got it upgraded.

By the way, SMC1000 filename is just a coincidence. The filenames actually go by the "ID" we give units to determine what they are beyond the SKU the customer references. SMC1000 and SMC1005 file names actually refer to ID 1000 and ID 1005. Your unit is an ID1005 and there are other SMC models that are ID1000 that would use the other file.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore