How to connect more than one APC Smart UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to connect more than one APC Smart UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:10 PM . Last Modified: ‎2024-03-06 11:21 PM

0 Likes
5
5101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:10 PM . Last Modified: ‎2024-03-06 11:21 PM

How to connect more than one APC Smart UPS

Hi

I need help ....my environment is:

I have a Rack with some servers running in it.

Inside this rack there is 2 APC Smart UPS 2200VA ( SMT2200RMI2U ) .

Because all the servers have 2 power unit, I connected each servers to both the UPS (to have redundancy).

With this working configuration, I'm able, to supply electrical power to the servers for 20-25 minutes (after that the UPS goes shutdown).

I need to double this time (more or less).

I need to buy 2 new APC Smart UPS ( I.E.)  5000 VA and replace my 2 APC SMT2200RMI2U , or

can I do something else?

Can I , for example , buy again 2 SMT2200RMI2U to put together with the 2 SMT2200RMI2U present now?

Thanks.

Pierluigi

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • SMT2200RMI2U
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:11 PM . Last Modified: ‎2024-03-06 11:21 PM

0 Likes
0
5102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:11 PM . Last Modified: ‎2024-03-06 11:21 PM

Hi Bill and Voidstar

Thanks. I understood. I don't want to use an  un-supported configuration ( plug a SMT into another in an electric way not supported)

I know now there is SMX version that allow to extend the battery pack.

Anyway, I'm going to buy 2 new SMT to use as  Voidstart said.

It is for our present configuration the best ( I think) as I don't have to throw away my 2 SMT to buy new SMX.

Thanks you both for the help.

Have a nice day.

Pierluigi

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:10 PM . Last Modified: ‎2024-03-06 11:21 PM

0 Likes
0
5102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:10 PM . Last Modified: ‎2024-03-06 11:21 PM

Hi,

To increase the runtime of a SMT2200RMI2U you must decrease the load. So if you add additional UPS and remove some load from the existing UPS and place that load on the new UPS the runtime on the existing UPS will increase. Another option is to replace the existing SMT2200 with SMX2200 Smart-UPS you have the option of adding external battery packs that will increase the available runtime. 

If you replace the existing SMT2200 with Smart-UPS 5000 you will also need to change the incoming AC connection. A Smart-UPS 5000 requires larger input to accommodate the larger output. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:10 PM . Last Modified: ‎2024-03-06 11:21 PM

0 Likes
0
5102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:10 PM . Last Modified: ‎2024-03-06 11:21 PM

Hi Bill

Thank you for your information.

But can I add addition external battery (another SMT2200) to the existent SMT2200 ?

I mean if I can connect a new SMT2200 to the existing SMT2200 using the Outlets number six in the image (so I can extend the time) or I can do this type of connection only with the SMX2200 model ( that means to me I have to buy all new things).

Thanks in advance if you can reply me.

Pierluigi

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:10 PM . Last Modified: ‎2024-03-06 11:21 PM

0 Likes
0
5102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:10 PM . Last Modified: ‎2024-03-06 11:21 PM

Hi,

You could plug 1 SMT2200 into another so that when AC is cut the first in the chain will power the second until its battery/s die but that is not a supported configuration and it may violate local electric code. We offer SMX Smart-UPS to allow user that need extended runtime the ability to add external battery pack to increase the runtime. 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 10:11 PM . Last Modified: ‎2024-03-06 11:21 PM

0 Likes
0
5102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:11 PM . Last Modified: ‎2024-03-06 11:21 PM

If you buy two new SMT2200, I would plug them into separate outlets (not on the UPS) and split your servers between the 2 old and 2 new UPSes. That lowers the load on each UPS and increases runtime. On the other hand, Bill's solution using SMXs instead would allow you to rack fewer UPSes, use less outlets, and be able to scale runtime up as desired by purchasing more batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:11 PM . Last Modified: ‎2024-03-06 11:21 PM

0 Likes
0
5103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:11 PM . Last Modified: ‎2024-03-06 11:21 PM

Hi Bill and Voidstar

Thanks. I understood. I don't want to use an  un-supported configuration ( plug a SMT into another in an electric way not supported)

I know now there is SMX version that allow to extend the battery pack.

Anyway, I'm going to buy 2 new SMT to use as  Voidstart said.

It is for our present configuration the best ( I think) as I don't have to throw away my 2 SMT to buy new SMX.

Thanks you both for the help.

Have a nice day.

Pierluigi

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore