I have recently completed a installation for APC SRT5KXLI with 3 SRT192BP. The hand wiring was completed to the main power. But after powering on the UPS i see the UPS is displaying a red alert after a few mins and shwing up a message called Replace All RBCs. The Event log shows RBC needs Replacement Event Code 181. Does this shows a problem with the UPS or the problem with the Batteries. this is totally a new installlation. I have disconnected the battery from the SRT192BP too.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
i have the same issues with this APC UPS model.. It can run only with two battery packs.. If i add more the error you said occurs..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Sir I have contacted and emailed the local Tech support engineer here in Riyadh Saudi Arabia and his advised was to Update the firmware of the UPS. And it seems my problem worsened. I have followed the steps on upgrading the firmware of APC UPS SRT5KLXI with three battery packs connected to the UPS. The firmware has been updated from UPS 4.0 to UPS 4.1. We have updated the UPS thru USB connection using firmware upgrade wizard. We followed what was instructed on the manual on how to update firmware.
After the update there's no more error indicating at the UPS with three battery packs connected to it. When we look at the Run time of the UPS with the same load as with before with two battery packs which was 1hr 35mins now it is down to 14mins. Then we look at the Menu/status/battery it doesn't detect the battery packs anymore. The UPS is now running with its internal battery packs even if i have connected three battery packs as of the moment.
Can you please give another solution for my problem.. It is really frustrating and the thought that it would be OK.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
i have the same issues with this APC UPS model.. It can run only with two battery packs.. If i add more the error you said occurs..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Hi,
There should be a grounding cable the came with the battery packs. Be sure the cable has been connected to each battery pack and the ground is good.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Hello sir.. by means of grounding like an actual earth grounding? Will be the Cabinet rack grounding suffice? I will try to connect the third battery pack with all its grounding connected. Thank you sir..
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Hello,
It's been some time i had this issue. I remember I had connected the ground wire between the battery packs and the UPS. I raised the issue with APc and took itto the service center. If i remember correctly, the battery packs were replaced and also ups board was also changed.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Hi,
What are the serial numbers of the UPS and battery packs?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Sir These are the serial numbers of the UPS and battery packs.There are three battery packs, two are connected to the UPS and One battery pack is not connected at the UPS due to "sys error 0800". Thank you sir..
One (1) APC SRT SRT5KLXI 5kVA 230V
S/N: AS1613170530
Date installed: September 2016
Two (2) SRT192BP
S/N: 7S1550L00808
7S1608L01127
Date Installed: September 2016
Not connected
One (1) SRT192BP
S/N: 5s1418T21042
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:10 PM . Last Modified: 2024-03-06 11:22 PM
Sir I have contacted and emailed the local Tech support engineer here in Riyadh Saudi Arabia and his advised was to Update the firmware of the UPS. And it seems my problem worsened. I have followed the steps on upgrading the firmware of APC UPS SRT5KLXI with three battery packs connected to the UPS. The firmware has been updated from UPS 4.0 to UPS 4.1. We have updated the UPS thru USB connection using firmware upgrade wizard. We followed what was instructed on the manual on how to update firmware.
After the update there's no more error indicating at the UPS with three battery packs connected to it. When we look at the Run time of the UPS with the same load as with before with two battery packs which was 1hr 35mins now it is down to 14mins. Then we look at the Menu/status/battery it doesn't detect the battery packs anymore. The UPS is now running with its internal battery packs even if i have connected three battery packs as of the moment.
Can you please give another solution for my problem.. It is really frustrating and the thought that it would be OK.