Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-01 04:25 AM . Last Modified: 2024-03-05 02:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:25 AM . Last Modified: 2024-03-05 02:19 AM
Hello all,
Can anyone please explain how and what should be configured to automatically shutdown a server that is connected to a Smart UPS 2200 (with APC network Interface Card 2 build in) ?
Has additional software has to be installed on the server for this to work?
Also, for this to work is it necessary to connect the UPS not only to the network but also direct to the attached server with the serial/usb cable?
Hope to hear soon.
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:25 AM . Last Modified: 2024-03-05 02:19 AM
I am assuming you have a UPS Network Management Card 2 (and not APC Network Interface 2)?
Your options for graceful shutdown are:
OR
If you have a Network Management Card already, you can just utilize that. Then you won't have the cable limitation. And you cannot do both methods at a time.
Here are some helpful PDFs:
http://www.apcmedia.com/salestools/SJHN-8SBETY/SJHN-8SBETY_R0_EN.pdf
http://www.apcmedia.com/salestools/SJHN-8SBETY/SJHN-8SBETY_R0_EN.pdf
Essentially, if you install PowerChute successfully and don't do any other configuration (which there are shutdown options you can do), the client will shutdown when the UPS is almost out of battery power.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:25 AM . Last Modified: 2024-03-05 02:19 AM
I am assuming you have a UPS Network Management Card 2 (and not APC Network Interface 2)?
Your options for graceful shutdown are:
OR
If you have a Network Management Card already, you can just utilize that. Then you won't have the cable limitation. And you cannot do both methods at a time.
Here are some helpful PDFs:
http://www.apcmedia.com/salestools/SJHN-8SBETY/SJHN-8SBETY_R0_EN.pdf
http://www.apcmedia.com/salestools/SJHN-8SBETY/SJHN-8SBETY_R0_EN.pdf
Essentially, if you install PowerChute successfully and don't do any other configuration (which there are shutdown options you can do), the client will shutdown when the UPS is almost out of battery power.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.