How to Disable Shutdown Sequence for PowerChute Business Edition

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to Disable Shutdown Sequence for PowerChute Business Edition
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
6
3250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:00 AM

How to Disable Shutdown Sequence for PowerChute Business Edition

I have a Smart UPS 1500 running the PowerChute Business Edition 8.0.1.609.
Today we had a planned power outage. Our server room had a total electrical outgage for 17 secounds until our emergency generator kicked in.

What surprised me was our UPS started a "shutdown process" right away after the main power went down. When I came back from lunch, I noticed the servers and UPS were off.

I am guessing it was too much load for the UPS to handle even though the load is 58% and 19 minutes remaning?

How do I disable the shutdown sequence? I don't think we need to worry with the shutdown sequence since we have emergency generators.

Below is the event log:

11/06/09 12:19:32 Communication Established
11/06/09 12:19:32 Monitoring Started
11/06/09 12:02:40 Monitoring Stopped
11/06/09 12:02:03 Sufficient Runtime Available
11/06/09 12:01:57 Insufficient Runtime Available
11/06/09 12:01:57 Power Restored
11/06/09 12:01:40 Shutdown process started
11/06/09 12:01:40 Low Runtime Remaining
11/06/09 12:01:40 Power Failed
11/06/09 12:01:36 Insufficient Runtime Available


Thanks
Tony

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 1500
  • PowerChute
  • sequence
  • shutdown
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
3249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

Tony,

Are you still facing the same issue? If you are still facing the same issue, let me collect some more information from you to find out if the issue lies with the software or hardware.

What was the UPS runtime and battery charge capacity according to the data logs when you received the Insufficient run time alert? Could you please post the entire data and event logs which was recorded when this occurred?

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

No, I haven't had any problems since that problem on June 11.

I've had 3 power failure since then:
1. June 26, I had 2x power failures that lasted 2 seconds - no problems and no shutdown.
2. July 17, I did a test and pulled the plug for 1 minute - no problems and no shutdown.

I think I might've reduced the "Runtime Remaining Threshold" down to 10 minutes after that June 11 problem. I think originally I had it on 20 minutes or more.

I have no idea why I had 'insufficient runtime available' in the log. The battery is only a couple months old.

Below is my event log
Attached is myData Log

Thanks
Tony

17/07/09 16:20:37 Power Restored
17/07/09 16:19:29 Power Failed
09/07/09 12:17:41 Self Test Passed
09/07/09 12:17:38 Self Test Initiated
26/06/09 06:12:02 Power Restored
26/06/09 06:12:00 Power Failed
26/06/09 05:39:06 Power Restored
26/06/09 05:39:04 Power Failed
25/06/09 12:18:36 Self Test Passed
25/06/09 12:18:32 Self Test Initiated
11/06/09 14:19:51 Battery Charge In Range
11/06/09 14:19:44 Sufficient Runtime Available
11/06/09 12:56:06 Battery Discharged
11/06/09 12:56:00 Insufficient Runtime Available
11/06/09 12:21:36 Sufficient Runtime Available
11/06/09 12:21:24 Insufficient Runtime Available
11/06/09 12:19:32 Communication Established
11/06/09 12:19:32 Monitoring Started
11/06/09 12:02:40 Monitoring Stopped
11/06/09 12:02:03 Sufficient Runtime Available
11/06/09 12:01:57 Insufficient Runtime Available
11/06/09 12:01:57 Power Restored
11/06/09 12:01:40 Shutdown process started
11/06/09 12:01:40 Low Runtime Remaining
11/06/09 12:01:40 Power Failed
11/06/09 12:01:36 Insufficient Runtime Available
04/06/09 11:12:54 Communication Established
04/06/09 11:12:54 Monitoring Started
04/06/09 11:12:41 Monitoring Stopped
04/06/09 11:12:13 Communication Established
04/06/09 11:12:13 Monitoring Started

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

As far as I know, the cause of insufficient runtime would be if the load which is plugged into the UPS is too large to run the battery long enough to allow for shutdown of the operating system. You may need to reduce the load or, if possible, reduce the amount of time it takes to shutdown the operating system. The latter would only be possible if you configured a shutdown delay.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

You should be able to go into Events -> Actions on your PCBE web agent and check any event rows that have the "Shutdown" field marked / bubbled. Then you can click on the link for that event and disable the shutdown sequence starting for that event.

On a side note, can you provide the information on your "Protected System" -> Shutdown Settings menu, as well as any existing settings you did have for an event with a shutdown sequence? You may have had a bad setting configured on the software.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

Thanks for your reply. I double checked my Event Actions and there is nothing enabled under the Shutdown and Command File coloumns. All blank.

I am thinking I should uninstall PCBE and go to the older PCBE version that the UPS came with...


Here is the configuration of my Protected System Shutdown Sequence Summary :



Time Required For Shutdown Sequence 10 Minutes

Low Battery Signal 300 Seconds

Command File Enabled No

OS Shutdown Delay 3 Minutes

OS Shutdown Type Shutdown

Enable OS Reboot Yes

UPS Turn On Battery Capacity 15 %

UPS Turn On Delay 0 Minutes

Enable SMTP E-mail Yes

Enable Notification Yes

Enable Logging Yes

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

Shutdown Sequence Summary
Time Required For Shutdown Sequence 10 Minutes
Low Battery Signal 300 Seconds
Command File Enabled No
OS Shutdown Delay 3 Minutes
OS Shutdown Type Shutdown
Enable OS Reboot Yes
UPS Turn On Battery Capacity 15 %
UPS Turn On Delay 0 Minutes
Enable SMTP E-mail Yes
Enable Notification Yes
Enable Logging Yes

Message was edited by: tony.yung@ualberta.ca

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
3250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:34 AM . Last Modified: ‎2024-03-07 03:00 AM

Tony,

Are you still facing the same issue? If you are still facing the same issue, let me collect some more information from you to find out if the issue lies with the software or hardware.

What was the UPS runtime and battery charge capacity according to the data logs when you received the Insufficient run time alert? Could you please post the entire data and event logs which was recorded when this occurred?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of