How long can I store a new UPS with its battery installed?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How long can I store a new UPS with its battery installed?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
4
4787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

How long can I store a new UPS with its battery installed?

Hi.  I recently purchased several UPS units with batteries installed.  Is it safe for me to store them this way for a year?  Hope to get some informed opinions on this question.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:55 PM

0 Likes
0
4785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:55 PM

You can charge the batteries outside the UPS. The companies that actually manufacture the batteries (CSB, BB, etc.) provide charging specifications and you can obtain a charger that complies with those specs. Note that those chargers are for single batteries and most APC models except the smallest have multiple batteries inside, so you would need to remove the batteries and charge them individually. That (and voiding the warranty) is likely why APC recommends using the UPS to charge the batteries. Just remember to use the UPS battery disconnect after you charge them, or the UPS will run them down because it thinks it is in standby mode.

Anecdote (of the "you should NOT do this" variety): After Hurricane Sandy, my main server racks which are powered by a Symmetra RM, would not power up. The power was out for nearly 2 weeks and the UPS batteries were completely discharged after 5 hours or so of battery operation. Since an APC UPS won't turn on without at least one good battery pack, I had to remove all of the SYBT2 battery packs from the UPS and XR frames (just pulling them out far enough to disconnect them), then disassemble one SYBT2 and charge the 10 individual 12V batteries one at a time using a car battery charger. I put the batteries back in the SYBT2 and then put it back in the Symmetra and started it up. It finished charging the batteries in that first pack, and then I reinstalled the other 11 SYBT2, one at a time, waiting for each to charge before installing the next one. That got me back up and running with UPS protection. I could have run in bypass mode, but that wouldn't have provided UPS protection (after the power came back, it was unreliable for another week or so while the utility continued to make repairs), and not all APC models have a manual bypass switch.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
0
4785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:56 PM

Hello,

For extended storage, it is recommended to disconnect the battery to avoid unnecessary discharge (new UPS units are shipped with their internal batteries disconnected). You can find more, UPS range specific information in the following knowledge base article: http://www.apc.com/ca/en/faqs/FA156516/

In short, APC Batteries should be charged to 100% within 6 months of purchase. If the batteries are to be stored for an extended period of time after that, the following procedures are recommended in order to keep the batteries from discharging beyond the safe limit: 

  • If the ambient temperature during storage is - 15°C to + 30°C (+ 5°F to + 86°F), perform a full recharge cycle at least every six months.
  • In environments where the ambient temperature is + 30°C to + 45°C (+ 86°F to + 113°F), perform a full recharge cycle at least every three months.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
0
4785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:56 PM

Thank you.  I do have batteries that I will be storing over a period of time.  Can I obtain a device other than a UPS to charge the batteries every six months?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
0
4785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:56 PM

Hi,

APC batteries are designed to be used in their respective compatible UPS models. APC UPS units feature firmware controlled charging, where the charger can be boosted, or trimmed, depending on the current battery charge level, environmental temperature, battery capacity, etc. I would only recommend recharging the batteries using the compatible UPS that battery is intended for. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:55 PM

0 Likes
0
4786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 AM . Last Modified: ‎2024-03-17 11:55 PM

You can charge the batteries outside the UPS. The companies that actually manufacture the batteries (CSB, BB, etc.) provide charging specifications and you can obtain a charger that complies with those specs. Note that those chargers are for single batteries and most APC models except the smallest have multiple batteries inside, so you would need to remove the batteries and charge them individually. That (and voiding the warranty) is likely why APC recommends using the UPS to charge the batteries. Just remember to use the UPS battery disconnect after you charge them, or the UPS will run them down because it thinks it is in standby mode.

Anecdote (of the "you should NOT do this" variety): After Hurricane Sandy, my main server racks which are powered by a Symmetra RM, would not power up. The power was out for nearly 2 weeks and the UPS batteries were completely discharged after 5 hours or so of battery operation. Since an APC UPS won't turn on without at least one good battery pack, I had to remove all of the SYBT2 battery packs from the UPS and XR frames (just pulling them out far enough to disconnect them), then disassemble one SYBT2 and charge the 10 individual 12V batteries one at a time using a car battery charger. I put the batteries back in the SYBT2 and then put it back in the Symmetra and started it up. It finished charging the batteries in that first pack, and then I reinstalled the other 11 SYBT2, one at a time, waiting for each to charge before installing the next one. That got me back up and running with UPS protection. I could have run in bypass mode, but that wouldn't have provided UPS protection (after the power came back, it was unreliable for another week or so while the utility continued to make repairs), and not all APC models have a manual bypass switch.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore