How best to deal with NMC SSL certificate expiration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How best to deal with NMC SSL certificate expiration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
marting
Lieutenant JG marting
Lieutenant JG

Posted: ‎2022-03-09 11:30 AM . Last Modified: ‎2025-08-11 03:55 AM

0 Likes
9
14801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-09 11:30 AM . Last Modified: ‎2025-08-11 03:55 AM

How best to deal with NMC SSL certificate expiration

We have several hundred APC devices across many sites and started switching from HTTP/telnet to HTTPS/SSH a while back (apparently two years ago).

 

What we started seeing recently is not being able to get to certain devices via HTTPS.  Tried both via StruxureWare DCE and a standard browser.

Thankfully, SSH still worked on these devices and I was able to enable HTTP and do some more investigation on this.

 

It looks like the certificates that were created by the devices when HTTPS was initially enabled had a 2-year lifespan and are starting to expire...

 

It looks like I can work around this by deleting the certificate which forces creation of a new one on NMC reboot but that one looks to have a lifespan of only 1 year.

 

Needless to say, doing this process on all our devices once a year is not going to be sustainable.

 

Has anyone found a good way of dealing with this?

 

I found this thread about bulk-creating CSRs and then bulk-uploading certs.  Is this the easiest way to deal with this?

Was not expecting to have to go through this type of project 2 years after we enabled HTTPS...

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
  • NMC
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-03-10 01:25 PM

0 Likes
0
14750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-10 01:25 PM

@marting 

 

You should upgrade the cards to firmware 7.0.4 to resolve the issue. 

If the UPS are Smart-UPS go to

https://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v7-0-4-Firmware-for-Smart-UPS-Ga...

If the UPS is a Symmetra 3 phase go to 

https://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v7-0-4-Firmware-for-Symmetra-1-P...

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PERI
Crewman PERI
Crewman

Posted: ‎2022-05-27 06:16 AM

In response to RicR
0 Likes
3
14349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-27 06:16 AM

This worked for us:

 

cd ssl

delete defaultcert.p15

reboot

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Matt-B
Lieutenant JG Matt-B Lieutenant JG
Lieutenant JG

Posted: ‎2022-03-09 11:39 AM

0 Likes
6
14788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-09 11:39 AM

Hello,

 

The expiration date has since been updated in v7.x firmware to be 2035 for self signed certificates - more info in the KB article here: https://www.apc.com/us/en/faqs/FAQ000233142/

 

All you would need to do is upgrade the firmware, then delete the cert and reboot the NMC. When the card turns back on, the newly generated certificate will be valid until 2035. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

marting
Lieutenant JG marting
Lieutenant JG

Posted: ‎2022-03-09 02:54 PM

In response to Matt-B
0 Likes
0
14772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-09 02:54 PM

Thanks, that's great news!

 

I know I can push out the updated firmware via StruxureWare but...  is there any way to automate the deletion of the existing SSL certificate across many devices?

 

StruxureWare supports running custom console commands across many devices so if there is a console command that could be run to do this, I could do it that way.


Also open to other options!

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-03-10 01:25 PM

0 Likes
0
14751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-10 01:25 PM

@marting 

 

You should upgrade the cards to firmware 7.0.4 to resolve the issue. 

If the UPS are Smart-UPS go to

https://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v7-0-4-Firmware-for-Smart-UPS-Ga...

If the UPS is a Symmetra 3 phase go to 

https://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v7-0-4-Firmware-for-Symmetra-1-P...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RicR
RicR
Cadet

Posted: ‎2022-05-03 12:17 PM

In response to Matt-B
0 Likes
4
14550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-03 12:17 PM

Deleting the Cert and rebooting is fairly simple unless you have 250 devices.  We have both NMC2 and NMC3 devices. Looking for the most efficient way to automate the process as much as possible.  I have been looking at scripting the commands through CLI but having trouble with deleting the existing certificate.
Any suggestions on the best way to update this many devices?  

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PERI
Crewman PERI
Crewman

Posted: ‎2022-05-27 06:16 AM

In response to RicR
0 Likes
3
14350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-27 06:16 AM

This worked for us:

 

cd ssl

delete defaultcert.p15

reboot

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

marting
Lieutenant JG marting
Lieutenant JG

Posted: ‎2023-05-22 09:30 AM

In response to PERI
1 Like
2
11591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-22 09:30 AM

Thanks @PERI !

 

Was able to bulk-deploy that to our devices using the Custom Command function in SNMP Device Configuration in DCE (after upgrading firmware).

Reply

Link copied. Please paste this link to share this article on your social media post.

EPacey
EPacey
Cadet

Posted: ‎2024-06-24 12:02 PM

In response to marting
0 Likes
1
6206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 12:02 PM

Hi Marting,

 

Could you share the steps you used to bulk-deploy the custom command?

 

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

marting
Lieutenant JG marting
Lieutenant JG

Posted: ‎2024-07-01 09:44 AM

In response to EPacey
0 Likes
0
6057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-01 09:44 AM

In DCE:

 

  • Device > APC SNMP Device Configuration
  • User Configuration...
  • Select the devices you want to target
  • Click Add Custom Command and add in each of the commands in PERI's post
  • Click Finish to deploy

I would test on one or two devices to make sure you have the process down before mass-deploying.

Reply

Link copied. Please paste this link to share this article on your social media post.

tcrowe
Crewman tcrowe
Crewman

Posted: ‎2024-07-02 07:57 AM

0 Likes
0
6018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-02 07:57 AM

There are a few ways to deploy SSL certs.

We're using a powershell script via SSH. You'll need the Posh-ssh module.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore