How Do I Make The APC SU2200 Time Set via NTP?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How Do I Make The APC SU2200 Time Set via NTP?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:23 AM

0 Likes
5
4071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:23 AM

How Do I Make The APC SU2200 Time Set via NTP?

Hi,

I am trying to get NTP on my SU2200 with an NMC to work. I have the latest firmware on the NMC. Using the serial port, I can configure NTP with any number of known good NTP servers only to get errors that the NTP server addresses are bad. I can, of course, set the time manually with no problem. Any ideas on where to start looking? Thanks in advance!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

0 Likes
0
4070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

you're welcome πŸ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

0 Likes
0
4070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

what NTP server are you trying to type in? an IP address or a FQDN? is the NMC accepting it as a valid server and just not updating or does it not allow you to set the specific server information in primary/secondary? do you get any error message?

i know generally with these you may need to give it a few minutes to allow it to perform the update.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

0 Likes
0
4070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

Hi, I am trying to use servers like (USNO) 192.5.41.42 and others like 72.8.140.240. I cannot enter FQDN although I tried and got an error when trying to save the information. The NMC is accenting the IP addresses.

When I try and set the time "now" using NTP I get the error message: Last update failed - bad server address. This happen no matter what IP address I put in.

Do you have specific IP addresses that work for you? Maybe you can share them with me. Additionally, I have two NAS units on the network that update via NTP using FQDN information.

Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

0 Likes
0
4069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

first thing i may do is reboot your NMC under administration->General->reset/reboot and choose reboot management interface. see if the behavior changes.

i tried 72.8.140.240 on my NMC running the same firmware and got update successful and the IP was accepted without issue.

just to confirm, i selected the radio button on "synchronize with NTP server" and then pasted the IP in the primary server field and left secondary as 0.0.0.0. i also made sure my timezone was set correctly and then i selected the box that said update now. it came back almost immediately.

i might also try to ping from your card which is a utility available from the telnet interface under Network->ping utility and see if you can ping any of these addresses. are you able to try that?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

0 Likes
0
4069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

Hi and thanks for pointing me in the right direction. I am not an IT guy or a network person so my understanding of setting up a network is limited. Anyway, I could not ping the time server per your suggestion initially. I was looking at some of the network and/or TCP/IP settings and noticed that I did not have a default gateway set. So I set that and all is well. Thanks again for all your support!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

0 Likes
0
4071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:48 AM . Last Modified: β€Ž2024-03-13 01:22 AM

you're welcome πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore