Posted: 2021-06-29 04:48 AM . Last Modified: 2024-03-13 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:48 AM . Last Modified: 2024-03-13 01:22 AM
I am interested in automatic shutdown of 2 linux servers that run oracle databases. We have 2-SMT3000RM2U units each with an AP9631 NMC2. Each linux server has a PSU connected to each UPS for redundancy purposes. The challenge is to shut down the oracle instances before the linux servers are given the shutdown control event. I have the scripts necessary to issue the oracle commands needed for shutdown - I am simply confused on which solution to use in order to execute the scripts before a shutdown control event.
Would this be feasible to explore NMC2 + Power Chute Network Shutdown or consider Power Chute Business Edition with Power Chute Agents on each machine?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:48 AM . Last Modified: 2024-03-13 01:22 AM
Hi,
PowerChute Network Shutdown can be configured to listen to up to 4 NMC. We have Application Note 98 on the subject.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:48 AM . Last Modified: 2024-03-13 01:22 AM
Hi,
PowerChute Network Shutdown can be configured to listen to up to 4 NMC. We have Application Note 98 on the subject.