I'm looking for a horizontal, 120 volt switched and metered PDU with an L5-20P input and at least sixteen 5-20R or 5-15R outlets. I prefer to avoid a vertical "Zero U" one because I have plenty of horizontal rack space available (2U would be fine), but not much depth.
Does APC sell such a thing? Three are close:
I can't see one that meets all three of the requirements. Am I just missing it?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:58 AM
Angela N. wrote:
Worst case, you could get an AP7902 and modify the plug
Thanks, that's probably a reasonable way to go. (It'll be on a 20 amp breaker.)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:58 AM
I looked at this document which you can do another once over on if you'd like: http://www.apcmedia.com/salestools/JLAE-7DZLEC/JLAE-7DZLEC_R5_EN.pdf
Worst case, you could get an AP7902 and modify the plug after reading the disclaimer here (Can I change the input plug or reduce the cord length on my Rack Power Distribution Unit (Rack PDU) ...) and knowing you'd be de-rating the unit and be subject to the UL modification PDF attached. You'd probably also still need to install it on a 20A circuit/breaker to avoid problems with local code since for the PDU, it would be rated for the 30A.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:58 AM
Angela N. wrote:
Worst case, you could get an AP7902 and modify the plug
Thanks, that's probably a reasonable way to go. (It'll be on a 20 amp breaker.)