SRT3000: scheduled self test power cycles attached servers

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT3000: scheduled self test power cycles attached servers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
2
652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

SRT3000: scheduled self test power cycles attached servers

today something strange occurred:
on a 3 month old (new) UPS during a scheduled self test both dell R430 servers that are attached to it lost power for a few seconds
the UPS webinterface (equipped with NMC) logs show test passed:
    00:20:31    Device    UPS: Self-Test started by automatic timer.
    00:20:52    Device    UPS: Self-Test passed.
no other relevant warnings or errors can be seen in the UPS log

the drac logs from both R430 servers show 2 entries each: one with power lost and 4 seconds later there is a power restored event
there is no data connection between the server and the ups, the drac logs are from sensors inside the power supplies. The servers each have 2 redundant power supplies which were (unfortunately) both connected to the UPS (probably within the same outlet group).

The UPS is a Smart-UPS SRT 3000 in green mode with a typical load of 12% VA in a A/C controlled dust free area with above average power grid (located in western europe)

According to FAQ & google a self test should not power cycle the devices behind the UPS, and all prior automated self tests did not cause that behaviour.

Since owning the UPS no power outage occurred, and I do not think that I ever tested the device without A/C power

Could that be a defective UPS? Any advice? I've never experienced a defective APC unit in my 20 years so I also have no clue about warranty or being eligible for support - I just bought the unit and did not care about service contracts

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:57 AM

0 Likes
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:57 AM

My only other thought, if it is possible to check, would be to verify that any attached device shows this behavior. Meaning if you plug in a clock radio or something basic (that supports the plug types on the UPS), does the same thing occur?

SRT is an online UPS so it should not have any transfer time - which transfer to battery which can cause problems for certain types of equipment but that should not be the case here...

I know you have redundant power supplies and don't expect you to check this necessarily and put your load at risk but I was wondering if the UPS was causing the server to power down vs. reboot which I would think you can only tell if you try with a single power supply. Or might see with another device you can try to plug in as I had suggested.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

Defiantly a faulty UPS, you need to check if it is in warranty as support will probably arrange a swap if new batteries do not help. I think it is 3 years on the UPS and 2 on the battery.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:57 AM

0 Likes
0
652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:57 AM

My only other thought, if it is possible to check, would be to verify that any attached device shows this behavior. Meaning if you plug in a clock radio or something basic (that supports the plug types on the UPS), does the same thing occur?

SRT is an online UPS so it should not have any transfer time - which transfer to battery which can cause problems for certain types of equipment but that should not be the case here...

I know you have redundant power supplies and don't expect you to check this necessarily and put your load at risk but I was wondering if the UPS was causing the server to power down vs. reboot which I would think you can only tell if you try with a single power supply. Or might see with another device you can try to plug in as I had suggested.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of