Translate to:
Please select
  • English (English)
  • French (Français)
  • German (Deutsch)
  • Indonesian (Bahasa Indonesia)
  • Italian (Italiano)
  • Portuguese (Português)
  • Russian (Русский)
  • Spanish (Español)
  • Thai (ไทย)
  • Turkish (Türkçe)
  • Vietnamese (Tiếng Việt)
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Hi everybody!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
Enter a search word
    Turn off suggestions

    Didn't find what you were looking for? Explore advanced search

    Enter a search word
      Turn off suggestions

      Didn't find what you were looking for? Explore advanced search

      Enter a user name or rank
        Turn off suggestions

        Didn't find what you were looking for? Explore advanced search

        Enter a search word
          Turn off suggestions

          Didn't find what you were looking for? Explore advanced search

          Enter a search word
            Turn off suggestions

            Didn't find what you were looking for? Explore advanced search

            cancel
            Turn on suggestions
            Showing results for 
            Show  only  | Search instead for 
            Did you mean: 
            Important Note
            • Home
            • Schneider Electric Community
            • APC UPS, Critical Power, Cooling and Racks
            • APC UPS Data Center & Enterprise Solutions Forum
            • Hi everybody!
            Options
            • Mark Topic as New
            • Mark Topic as Read
            • Float this Topic for Current User
            • Bookmark
            • Subscribe
            • Mute
            • Printer Friendly Page
            Invite a Co-worker
            Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
            You have entered an invalid email address. Please re-enter the email address.
            This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
            Please enter email address
            Send Invite Cancel
            Invitation Sent
            Your invitation was sent.Thanks for sharing Exchange with your co-worker.
            Send New Invite Close
            Top Experts
            User Count
            BillP
            Administrator BillP Administrator
            5060
            voidstar_apc
            Janeway voidstar_apc
            196
            Teken
            Spock Teken
            136
            Erasmus_apc
            Sisko Erasmus_apc
            112
            View All

            Free

            English

            Data Center Certified Associate Exam Development Path

            Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

            4.0
            Register Browse SE University

            Invite a Colleague

            Found this content useful? Share it with a Colleague!

            Invite a Colleague Invite
            Back to APC UPS Data Center & Enterprise Solutions Forum
            Start a Topic
            Anonymous user
            Not applicable

            Posted: ‎2021-06-26 12:41 AM . Last Modified: ‎2024-03-19 02:52 AM

            0 Likes
            0
            405
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-26 12:41 AM . Last Modified: ‎2024-03-19 02:52 AM

            Hi everybody!

            Hi everybody!
            I'm from viet nam. Very happy to join this forum. Always get help and be able to add more friends!
            Thank you everyone for reading!

            Labels
            • Labels:
            • General Questions & Suggestions
            Reply

            Link copied. Please paste this link to share this article on your social media post.

            • All forum topics
            • Previous Topic
            • Next Topic
            Replies 0

            You’ve reached the end of your document

            WHAT’S NEXT?

            Ask our Experts

            Didn't find what you are looking for? Ask our experts!

            My Dashboard

            Check out the new Feeds and activities that are relevant to you.

            To The Top!

            Forums

            • APC UPS Data Center Backup Solutions
            • EcoStruxure IT
            • EcoStruxure Geo SCADA Expert
            • Metering & Power Quality
            • Schneider Electric Wiser

            Knowledge Center

            Events & webinars

            Ideas

            Blogs

            Get Started

            • Ask the Community
            • Community Guidelines
            • Community User Guide
            • How-To & Best Practice
            • Experts Leaderboard
            • Contact Support
            Brand-Logo
            Welcome to Schneider Electric Community!
            Forum-Icon

            You have two options to continue your visit.

            LOGIN / Register

            Why logging in?
            • You enable the complete set of features available, such as posting, sharing, subscribing, private messaging and more.
            • You unlock the access to the whole content that Schneider Electric Community has to offer, including the gated items and the special events.
            And it’s free of charge!!!

            OR

            Continue as a guest

            Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

            Welcome!

            Welcome to your new personalized space.

            of 1

            Explore
            Translating the page…
            The page is currently translating. Please wait.
            Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.