Help please - SmartUPS with Powerchute on Windows Server 2016 SNMP with Synology Diskstation

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Help please - SmartUPS with Powerchute on Windows Server 2016 SNMP with Synology Diskstation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
9
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

Help please - SmartUPS with Powerchute on Windows Server 2016 SNMP with Synology Diskstation

Hi everyone,

you guys are my last hope 😉

I use an APC SmartUps 1500 UPS with my Windows Server 2016 and a Synology Disktation.

As the UPS has only one USB cable, I plugged that into my Windows Server (as the Diskstation is only backup) and installed and configured the APC PowerChute Software that allows Windows to recognize the UPS and shutdown the server once the batteries goes low.

Now I want to use the SNMP-feature that Powerchute provides to inform my Diskstation to shut down as well.

So far I have had no luck on connecting my Diskstation to my server via SNMP.

What I did so far:

-Diskstation is logged into the Windows Domain

-Windows Firewall allows all in- and outgoing connections on port 161 UDP (used for SNMP)

-installed the SNMP service on the Windows Server

-configured both PowerChute and Diskstation for hours, see attached pic

aA0GnU2gBQ8ZuRRKEt%2FLPg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngaA0GnU2gBQ8ZuRRKEt%2FLPg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

All I want is for the Powerchute-Software to send a signal to my Synology to tell it to shut down once power goes low.

Hopefully someone more knowledgeable in PowerChute and SNMP can help me out, I'm really lost at why it doens't work....

Thank you!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

Hi Manfred,

The APC solution is to use the network management card (AP9630, AP9631). This works with PowerChute Network Shutdown.

Synology is running third party software called Network UPS Tools. You may be able to run that on your PCs for network shutdown.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

Hi,

I reviewed the Synology Knowledge Base library and did not find any information on how to set up Diskstation as a trap receiver. There is a document that discusses Diskstation Manager communication with SNMP management software. SNMP service (at Control Panel > Terminal & SNMP > SNMP) allows users to monitor Synology NAS with network management software. Currently, SNMPv1, SNMPv2c and SNMPv3 protocols are supported. https://www.synology.com/en-us/knowledgebase/DSM/help/DSM/AdminCenter/system_snmp

My recommendation is to contact Synology Inc Community. Someone in their community may have your answer. https://www.synology.com/en-us/support/community

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

Hi Bill,

thank you for your reply.

I already contacted Synology, they claim it is a problem of configuring the PowerChute software.

Can you take a look at my config and tell me if I set it up correctly?

The bottom right in my screenshot-compilation is from my Synology NAS, where I configured the reception of SNMP.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

Hi,

I am not familiar with how Synology handles SNMP traps however I would expect the system would be listening for traps on port 162 not 161. Port 161 is used for SNMP set, get, walk.

What happens when you press trap receiver test? Do you see an error in PowerChute or does it show as trap sent? If sent does Synology list the test trap as received? 

I tested with PowerSNMP Manager and see the trap sent successfully and received.

OgpgJMi%2Bm%2FYzsCx%2BHUcuSA%3D%3D.pngOgpgJMi%2Bm%2FYzsCx%2BHUcuSA%3D%3D.png

Message details were captured in PowerSNMP

%2FxDgPrrzUNk42eRahHZfiQ%3D%3D.png%2FxDgPrrzUNk42eRahHZfiQ%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:53 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:53 PM

Do I have to set the Powerchute-running machine's IP in every NMS IP/Host name field?

And in "trap receiver" als well? I thought I had to set the Synology's IP as trap receiver.

Is the port in "trap receiver" supposed to be the same as in "miscellaneous"?

I received the same green verification of trap sent, but Synology cannot detect a trap sent, it doens't have this kind of feature.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:53 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:53 PM

Hi,

On 11/15/2018 2:29 PM, Manfred said:

Do I have to set the Powerchute-running machine's IP in every NMS IP/Host name field?

No. The IP can be 0.0.0.0

On 11/15/2018 2:29 PM, Manfred said:

And in "trap receiver" als well? I thought I had to set the Synology's IP as trap receiver

The IP should be the trap receiver so in your case the IP of the Synology system

On 11/15/2018 2:29 PM, Manfred said:

Is the port in "trap receiver" supposed to be the same as in "miscellaneous"?

I do not know what this setting is. PowerChute will send the traps to port 162

On 11/15/2018 2:29 PM, Manfred said:

I received the same green verification of trap sent, but Synology cannot detect a trap sent, it doens't have this kind of feature

You should contact Synology support about this.

Below is what I found in the Synology Knowledge Base https://www.synology.com/en-us/knowledgebase/DSM/help/DSM/AdminCenter/system_hardware_ups

SNMP UPS Support

Your Synology NAS also supports connecting to SNMP (Simple Network Management Protocol) UPS devices. For details regarding hardware installation, please consult the user manual of your SNMP UPS device. Once the Synology NAS has been plugged into the device and connected to the same network, you can follow the steps below to enable UPS support.

To enable SNMP UPS support:

  1. On the UPS tab, check the Enable UPS support checkbox.
  2. Select SNMP UPS from the Network UPS type drop-down menu.
  3. In the SNMP UPS IP address field, enter the IP address of the SNMP UPS device.
  4. Select when the Synology NAS should enter Safe Mode after power failure occurs.
  5. Enter the community string for the SNMP UPS device into the SNMP community field.
  6. Click Apply.

Note:

  • It is strongly recommended to use SNMP UPS for Synology High Availability (SHA) deployments.
  • Synology NAS supports SNMPv1 and SNMPv2c UPS devices.
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

Thank you for the clarification.

Synology support is working on this as well of course.

Just one question left:

in "SNMP Traps" and "Trap Receivers" do I set the port of the Trap Receiver to 162 oder 161?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

Hi,

Traps should use port 162.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

0 Likes
0
8116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

So I finally got an answer from Synology support.

They tell me that my configuration is not supported, only direct USB to Diskstation or APC integrated networks card IN the UPS to Diskstation is ok.

Now I want to try it the other way round, attach the UPS to my Synology via USB; then use the Synology to send traps to Windows.

Can PowerChute work this way, receiving incoming SNMP traps to shutdown?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

0 Likes
0
8117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:16 AM . Last Modified: ‎2024-03-10 11:53 PM

Hi Manfred,

The APC solution is to use the network management card (AP9630, AP9631). This works with PowerChute Network Shutdown.

Synology is running third party software called Network UPS Tools. You may be able to run that on your PCs for network shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore