Help! Single phase to three-phase converter on UPS output?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Help! Single phase to three-phase converter on UPS output?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
blackyman7_apc
blackyman7_apc
Cadet

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:44 AM

0 Likes
3
4424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:44 AM

Help! Single phase to three-phase converter on UPS output?

Hey team! I have a single-phase output UPS that I need to power a three-phase input DC supply. It's going to cost me way too much to replace either of the units. How practical would it be for me to add a 1-phase to 3-phase converter between my UPS and DC supply? I know I stand to lose ~1/3 capacity on the converter; are there any other considerations I'm overlooking? Do any of you have a good schematic that shows standard converter electronics?

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:44 AM

0 Likes
0
4419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:44 AM

On 12/12/2020 6:42 PM, Mitchel said:

any considerations I might be overlooking.

Voltage. 3 Phase is 120 degrees separated whereas your single phase voltage will translate directly through the converter. If you were in Australia for example, on 230V mains you'd normally have a nominal 415V three phase. Using a converter you get 230V 3 phase. You'll need to look carefully at the output of the converter to make sure it's what you really need. Additionally, the cheap-mid market converters tend to have really poor input power factor with direct rectified mains rather than using a PFC boost converter, so you'll want to make sure the UPS is happy with that.

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
modesta_apc
modesta_apc
Cadet

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:44 AM

0 Likes
0
4417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:44 AM

The intent is to go with an off-the-shelf item.

The Ultimate Problem I need to solve is as stated: I have a 1 phase output from my UPS, but it needs to supply a three phase load.

Plan: buy a 1-to-3 phase converter to solve the problem. Having never used one before I was looking for a circuit diagram to better understand what I'm putting into my system. Also looking for any practical advice on using a 1-to-3 phase converter - any considerations I might be overlooking.

Thanks!

upsers

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:44 AM

0 Likes
0
4420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:44 AM

On 12/12/2020 6:42 PM, Mitchel said:

any considerations I might be overlooking.

Voltage. 3 Phase is 120 degrees separated whereas your single phase voltage will translate directly through the converter. If you were in Australia for example, on 230V mains you'd normally have a nominal 415V three phase. Using a converter you get 230V 3 phase. You'll need to look carefully at the output of the converter to make sure it's what you really need. Additionally, the cheap-mid market converters tend to have really poor input power factor with direct rectified mains rather than using a PFC boost converter, so you'll want to make sure the UPS is happy with that.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:42 AM

0 Likes
0
4416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:42 AM

On 5/1/2021 12:35 PM, Patricia said:

What's the probability that it will work completely fine without any issues in it.

About the same probability you'd come back after 24 hours and insert a spam link in your post. Oh, gee. Look at that!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore