[Help] SUA2200RM2U turns off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • [Help] SUA2200RM2U turns off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
7
2616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

[Help] SUA2200RM2U turns off

Hi everyone i have an APC SUA2200RM2U that turns off if i connect the serial cable to my pc, it also has an usb port but.,..instead of that, it has an ethernet port !...but it's not woking or maybe needs a configuration, i don't know..,.

Can someone could help me at this.

Thank you in advance

Best Regards

Felipe

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • hardware
  • help
  • issue
  • management
  • network
  • off
  • PowerChute
  • poweroff
  • problem
  • rj45
  • serial
  • shutdown
  • software
  • sua2200rm2u
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
0
2615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

Yes, you can use AP9619 with this UPS. If you review the user's guide for the UPS, it will instruct you to braindead this UPS but I never do that unless there is a concern that the UPS is damaged prior to installing. 99.9% of the time, it is OK to hot swap without risk. I would just proceed with installing the card hot.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
0
2615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

Hi

check for software power chute you install in your computer option for shutdown Necessary the shutdown time not more the backup time and calibration your ups

note if your UPS is old that mean backup time is less than time for shutdown

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
0
2615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

Hello,

APC's serial cable is proprietary - a standard USB cable connected to the UPS will most likely turn it off. If this is not an APC serial cable, part number 940-0024 or 940-1524 (which comes with the UPS), then you need to track one down. You can verify the cable part number on one of the DB-9 connectors.

Also, the USB cable that comes with the UPS is an RJ-45 to USB cable, part number AP9827.

Basically, you need to track down the correct cables here. And you can only use USB OR serial connection. If you use USB, you may need to braindead your USB to reset the UPS communications to get serial working (which I can help with).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
0
2615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

Hi, i get the AP9827 and the 940-0024 but is not working.

The UPS is not turning off anymore but i can not see the PowerChute interface. I have installed the PowerChute Personal Edition.

Please help me.

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
0
2615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

OK well PowerChute personal edition is not the correct software. Uninstall that and you need to download and install PowerChute business edition agent. Before you install it, pick either USB or serial. If you choose serial and it doesn't work, you may need to reset/braindead your UPS but we can try that only if it doesn't work.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
0
2615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

Ok i will do that. I have a management card AP9619 and it is compatibilty with the UPS, can i plug the card into the UPS if is ON or should i turn OFF and disconnect every single load?, if i do not do that, the card could not response or might could die ?

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
0
2615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

you can connect your cart if your UPS is ON

your card will working good

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

0 Likes
0
2616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:54 AM . Last Modified: ‎2024-03-13 12:19 AM

Yes, you can use AP9619 with this UPS. If you review the user's guide for the UPS, it will instruct you to braindead this UPS but I never do that unless there is a concern that the UPS is damaged prior to installing. 99.9% of the time, it is OK to hot swap without risk. I would just proceed with installing the card hot.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore