Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Graceful shutdown of ESXi VMs and host

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Graceful shutdown of ESXi VMs and host
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
giannis_apc
Crewman giannis_apc
Crewman

Posted: ‎2021-07-08 05:56 AM

0 Likes
3
497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 05:56 AM

Graceful shutdown of ESXi VMs and host

This was originally posted on APC forums on 11/26/2018


Hello all,

Let me describe my issue and what i have done so far.

In our production we have a lot of ESXi hosts and few windows server VMs under them.

I have installed PowerChute Network Shutdown 4.2 for VMware and i installed it as a "Standalone VMware Host."

My first question is: Should i install it in each host or there is the possibility for a central management?

As you understand, i want after a long power outage to graceful shutdown VMs and after that the host.

Let me give you an example to explain further. I have seen that UPS battery lasts about 60 minutes.

I want if power outage is more than 40 minutes, to start shutdown VMs graceful and after this the host. When the power is back again, i want to start host and after that the VMs.

I have seen that there is the option "UPS On Battery" in PowerChute. I suppose that in this field i have to "Enable Shutdown" and add in the "Delay" field 40 minutes. Is that correct?

Is there something else i should configure in PowerChute, UPS Network Management Card 2 and in VMware host or VMs ?

Thank you in advance

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
giannis_apc
Crewman giannis_apc
Crewman

Posted: ‎2021-07-08 05:56 AM

0 Likes
0
497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 05:56 AM

This was originally posted on APC forums on 11/30/2018


Hello,

We have installed vCenter application in one VM.

Each host is connected to it's own UPS because hosts are located to different geographically sites.

In such implementation, can i install one PowerChute Virtual Appliance and manage all the hosts or should i install a PowerChute Virtual Appliance on each host?

Thank you

See Answer In Context

Reply
Share
Replies 3
giannis_apc
Crewman giannis_apc
Crewman

Posted: ‎2021-07-08 05:56 AM

0 Likes
0
497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 05:56 AM

This was originally posted on APC forums on 11/29/2018


Is it possible to have any technical support?

Thank you

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:56 AM

0 Likes
0
496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 05:56 AM

This reply was originally posted by Bill on APC forums on 11/29/2018


Hi,

Sorry for the delayed response. When you need immediate assistance you should contact local support.

On 11/26/2018 6:31 AM, giannis said:

My first question is: Should i install it in each host or there is the possibility for a central management?

Do you have vCenter Server installed and are all the host connected to a single UPS? If so you can install a single instance of PCNS and mange the power down of all hosts. If there is more than a single UPS it is still possible to manage all host from single PCNS however PCNS cannot be running on a VM. It would need to be installed on a standalone Windows Server. Please review Application Note 180. 

If you do not have vCenter Server installed than you should install PCNS VM on each host. 

On 11/26/2018 6:31 AM, giannis said:

I want if power outage is more than 40 minutes, to start shutdown VMs graceful and after this the host. When the power is back again, i want to start host and after that the VMs.

The powering down and starting up of the VMs will depend on if vCenter Server is in use. If vCenter Sever is in use than PCNS will stop and restart the VMs. See PCNS VMware User's Guide page 31 for assistance. If vCenter is not in use than it is the responsibility of the host to stop and restart the VMs. See Schneider Electric FAQ FA159688.

On 11/26/2018 6:31 AM, giannis said:

I have seen that there is the option "UPS On Battery" in PowerChute. I suppose that in this field i have to "Enable Shutdown" and add in the "Delay" field 40 minutes. Is that correct?

Correct. 

Reply
Share
giannis_apc
Crewman giannis_apc
Crewman

Posted: ‎2021-07-08 05:56 AM

0 Likes
0
498
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 05:56 AM

This was originally posted on APC forums on 11/30/2018


Hello,

We have installed vCenter application in one VM.

Each host is connected to it's own UPS because hosts are located to different geographically sites.

In such implementation, can i install one PowerChute Virtual Appliance and manage all the hosts or should i install a PowerChute Virtual Appliance on each host?

Thank you

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc