General configuration question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • General configuration question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
6
649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

General configuration question

I have read the tech documents and watched the youtube videos and I just want to clearify my understanding on how PowerChute in a VMware vCenter enviroment works.  Please correct me if I am wrong.

I have a single Smart-UPS SMT1500RM2UNC.  This will be controlling two host servers that are running VMware.  I am running the PowerChute virtual appliance to control the PowerChute events.

From what it sounds like...when a power issue occurs and the server begin to run off battery power, the UPS immediately begins the shutdown delay counter and then begins the processes of shutting down the VMs on the hosts machines.


Is there a way to say...begin VM shutdown when UPS has 15min of power remaining or to do this...do I have to set the delay time to however many sec I think the battery will last?
I also see the events configuration with a below thresh hold event.  If I set this to 15min remaining...does this just shut down the host machine or will this shutdown the VMs before shutting down the host?

Ideally what I would like to happen is power is lost, battery kicks in, everything runs normally until 15min of battery are left > begin VM shutdown > VMs off, begin host shutdown,,,>,,, power restored > I suspect host will have to be manually powered on > VMware will autostart VMs again when host boots up.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:06 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:06 AM . Last Modified: ‎2024-03-11 12:15 AM

Thank you for the reply.  I think I am almost finished setting up, but I have one more questions.

The check box to enable the VM shutdown processes states the following when you hover over it:
"When a critical UPS event occurs select this option to gracefully shutdown the virtual machine".

What is considered the critical event in this scenario....would the critical event be when the unit goes to battery backup OR is the critical even when the run time remaining countdown expires?

All the documentation I seem to read indicates that when the unit switches to battery this is considered a critical event hence this would kick off the shutdown processes even if there is plenty of battery time left.  I just want to make sure the processes is not shutting anything off too soon.

Thanks for all the help.  I created an official ticket trying to get these questions answered and that has been a black hole to nothing-ville.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

Hi,

Are you running vCenter Server to control the 2 ESXi hosts? 

On 10/11/2018 9:40 AM, Michael said:

Is there a way to say...begin VM shutdown when UPS has 15min of power remaining or to do this...do I have to set the delay time to however many sec I think the battery will last?

Yes. You can set the delay in the PowerChute web interface under Configure Events -  Runtime remaining below threshold If you set that for 900 seconds when the UPS has 15 minutes of runtime remaining the shutdown process will begin. You will also need to configure VM shutdown. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

But what is the proper way (or where do you set the configuration) to configure the VM shutdown to begin when 15min are left on the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

Hi,

You did not answer the question. Are you running vCenter Server. That makes a difference as to how the VMs are powered down. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:06 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:06 AM . Last Modified: ‎2024-03-11 12:15 AM

Im sorry...I did not notice the question above the quote.

Yes.  I am running vCenter 6.7 with two physical host machines.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:06 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:06 AM . Last Modified: ‎2024-03-11 12:15 AM

Hi,

The recommendation is to install the PowerChute virtual appliance (VM) on one of the hosts and configure it with vCenter Server. See the PCNS installation guide and Application Note 180. The PCNS VM can be downloaded from this link https://www.apc.com/us/en/tools/download/software_comp.cfm?sw_sku=SFPCNS42-V

You should configure PCNS to start the shutdown process when the runtime remaining falls below 15 minutes (900 seconds). That will be found in the PCNS web interface under Configure Events. Under the heading of Virtulization Setting configure VM shutdown and VM start up. Also configure vCenter shutdown. Under the heading of host protection you should add the 2 host to the powered by list. When the process starts the VMs will be commanded down. PCNS will wait the VM shutdown delay and then if vCenter is a VM it will be powered down. After PCNS wait the vCenter shutdown delay the hosts will be powered down. 

As for start up, if the BIOS of the servers are configured properly the hosts will start when AC is restored. PCNS will then be started and it will start the VMs. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:06 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:06 AM . Last Modified: ‎2024-03-11 12:15 AM

Thank you for the reply.  I think I am almost finished setting up, but I have one more questions.

The check box to enable the VM shutdown processes states the following when you hover over it:
"When a critical UPS event occurs select this option to gracefully shutdown the virtual machine".

What is considered the critical event in this scenario....would the critical event be when the unit goes to battery backup OR is the critical even when the run time remaining countdown expires?

All the documentation I seem to read indicates that when the unit switches to battery this is considered a critical event hence this would kick off the shutdown processes even if there is plenty of battery time left.  I just want to make sure the processes is not shutting anything off too soon.

Thanks for all the help.  I created an official ticket trying to get these questions answered and that has been a black hole to nothing-ville.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of