Galaxy 5000 Error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Galaxy 5000 Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 06:17 AM . Last Modified: ‎2024-03-19 12:20 AM

0 Likes
1
1877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:17 AM . Last Modified: ‎2024-03-19 12:20 AM

Galaxy 5000 Error

Dear Sirs,

we are having the following errors reported on our Galaxy 5000 UPS.

Could you be kind and advice implications and the meaning of these?

Some of the errors are while the systems is running on utility mains, noting that the mains is fed via parallel transformers OR parallel generators

03/19/2014 17:08:21 ;Battery operation mode : CHARGE ;Battery ;STATUS;11;25;1;4125;1
03/19/2014 17:08:21 ;Battery charger state RUNNING ;Chopper ;State;7;0;0;2084;1
03/19/2014 17:08:11 ;Load on AC normal YES ;Load ;State;4;0;0;2069;1
03/19/2014 17:08:11 ;PFC state RUNNING ;PFC ;State;6;0;0;2050;1
03/19/2014 17:08:11 ;Battery operation mode : STANDBY ;Battery ;STATUS;11;25;0;4125;1
03/19/2014 17:08:11 ;Load on battery NO ;Load ;State;4;0;0;2070;0
03/19/2014 17:08:10 ;AC normal fault (Disappear) ;Normal AC ;Fault;2;1;0;118;1
03/19/2014 17:08:10 ;AC normal frequency out of tolerance (Disappear) ;Normal AC ;Fault;2;1;0;34;1
03/19/2014 17:08:05 ;AC normal voltage loss(fast detection) (Disappear) ;Normal AC ;Fault;2;1;0;225;1
03/19/2014 17:08:05 ;AC normal voltage out of tolerance (Disappear) ;Normal AC ;Fault;2;1;0;226;1
03/19/2014 17:07:53 ;AC normal voltage out of tolerance (Appear) ;Normal AC ;Fault;2;1;1;226;1
03/19/2014 17:07:52 ;AC normal voltage loss(fast detection) (Appear) ;Normal AC ;Fault;2;1;1;225;1
03/19/2014 17:07:51 ;AC normal voltage loss(fast detection) (Disappear) ;Normal AC ;Fault;2;1;0;225;1
03/19/2014 17:07:51 ;AC normal low voltage (Disappear) ;Normal AC ;Fault;2;1;0;224;1
03/19/2014 17:07:51 ;AC normal low voltage (Appear) ;Normal AC ;Fault;2;1;1;224;1
03/19/2014 17:07:51 ;AC normal voltage out of tolerance (Disappear) ;Normal AC ;Fault;2;1;0;226;1
03/19/2014 17:06:19 ;AC normal frequency out of tolerance (Appear) ;Normal AC ;Fault;2;1;1;34;1
03/19/2014 17:06:19 ;AC normal voltage out of tolerance (Appear) ;Normal AC ;Fault;2;1;1;226;1
03/19/2014 17:06:19 ;Load on battery YES ;Load ;State;4;0;0;2070;1
03/19/2014 17:06:19 ;Load on AC normal NO ;Load ;State;4;0;0;2069;0
03/19/2014 17:06:19 ;PFC state STOP ;PFC ;State;6;0;0;2050;0
03/19/2014 17:06:19 ;Battery operation mode : DISCHARGE ;Battery ;STATUS;11;25;0;4125;1
03/19/2014 17:06:19 ;Battery charger state STOP ;Chopper ;State;7;0;0;2084;0
03/19/2014 17:06:19 ;AC normal fault (Appear) ;Normal AC ;Fault;2;1;1;118;1
03/19/2014 17:06:19 ;AC normal voltage loss(fast detection) (Appear) ;Normal AC ;Fault;2;1;1;225;1

---------------------------------------------------------------------------------------------------------------------------------------------------------------------------

03/14/2014 13:05:45 ;Battery operation mode : CHARGE ;Battery ;STATUS;11;25;0;4125;1
03/14/2014 13:05:45 ;Battery charger state RUNNING ;Chopper ;State;7;0;0;2084;1
03/14/2014 13:05:36 ;Inverter / AC bypass synchronization fault (Disappear) ;Inverter ;Fault;1;1;0;98;1
03/14/2014 13:05:35 ;Load on AC normal YES ;Load ;State;4;0;0;2069;1
03/14/2014 13:05:35 ;PFC state RUNNING ;PFC ;State;6;0;0;2050;1
03/14/2014 13:05:35 ;Battery operation mode : STANDBY ;Battery ;STATUS;11;25;0;4125;1
03/14/2014 13:05:35 ;Load on battery NO ;Load ;State;4;0;0;2070;0
03/14/2014 13:05:34 ;AC normal fault (Disappear) ;Normal AC ;Fault;2;1;0;118;1
03/14/2014 13:05:34 ;AC normal frequency out of tolerance (Disappear) ;Normal AC ;Fault;2;1;0;34;1
03/14/2014 13:05:34 ;synchronization source fault (Disappear) ;Installation ;Fault;9;1;0;249;1
03/14/2014 13:05:34 ;AC bypass frequency out of tolerance (Disappear) ;Bypass AC ;Fault;3;1;0;70;1
03/14/2014 13:05:30 ;AC bypass voltage loss (fast detection) (Disappear) ;Bypass AC ;Fault;3;1;0;127;1
03/14/2014 13:05:30 ;AC bypass voltage out of tolerance (Disappear) ;Bypass AC ;Fault;3;1;0;227;1
03/14/2014 13:05:29 ;AC normal voltage loss(fast detection) (Disappear) ;Normal AC ;Fault;2;1;0;225;1
03/14/2014 13:05:29 ;AC normal voltage out of tolerance (Disappear) ;Normal AC ;Fault;2;1;0;226;1
03/14/2014 13:05:29 ;AC normal frequency out of tolerance (Appear) ;Normal AC ;Fault;2;1;1;34;1
03/14/2014 13:05:29 ;AC bypass frequency out of tolerance (Appear) ;Bypass AC ;Fault;3;1;1;70;1
03/14/2014 13:05:29 ;AC normal voltage out of tolerance (Appear) ;Normal AC ;Fault;2;1;1;226;1
03/14/2014 13:05:29 ;synchronization source fault (Appear) ;Installation ;Fault;9;1;1;249;1
03/14/2014 13:05:29 ;AC bypass voltage out of tolerance (Appear) ;Bypass AC ;Fault;3;1;1;227;1
03/14/2014 13:05:29 ;AC normal fault (Appear) ;Normal AC ;Fault;2;1;1;118;1
03/14/2014 13:05:29 ;AC bypass voltage loss (fast detection) (Appear) ;Bypass AC ;Fault;3;1;1;127;1
03/14/2014 13:05:29 ;AC normal voltage loss(fast detection) (Appear) ;Normal AC ;Fault;2;1;1;225;1
03/14/2014 13:05:28 ;synchronization source fault (Disappear) ;Installation ;Fault;9;1;0;249;1
03/14/2014 13:05:28 ;AC bypass frequency out of tolerance (Disappear) ;Bypass AC ;Fault;3;1;0;70;1
03/14/2014 13:05:28 ;AC normal fault (Disappear) ;Normal AC ;Fault;2;1;0;118;1
03/14/2014 13:05:28 ;AC normal frequency out of tolerance (Disappear) ;Normal AC ;Fault;2;1;0;34;1
03/14/2014 13:05:24 ;AC bypass voltage loss (fast detection) (Disappear) ;Bypass AC ;Fault;3;1;0;127;1
03/14/2014 13:05:24 ;AC bypass voltage out of tolerance (Disappear) ;Bypass AC ;Fault;3;1;0;227;1
03/14/2014 13:05:23 ;AC normal voltage loss(fast detection) (Disappear) ;Normal AC ;Fault;2;1;0;225;1
03/14/2014 13:05:23 ;AC normal voltage out of tolerance (Disappear) ;Normal AC ;Fault;2;1;0;226;1
03/14/2014 13:02:29 ;AC bypass frequency out of tolerance (Appear) ;Bypass AC ;Fault;3;1;1;70;1
03/14/2014 13:02:29 ;synchronization source fault (Appear) ;Installation ;Fault;9;1;1;249;1
03/14/2014 13:02:29 ;AC bypass voltage out of tolerance (Appear) ;Bypass AC ;Fault;3;1;1;227;1
03/14/2014 13:02:29 ;Inverter / AC bypass synchronization fault (Appear) ;Inverter ;Fault;1;1;1;98;1
03/14/2014 13:02:29 ;AC bypass voltage loss (fast detection) (Appear) ;Bypass AC ;Fault;3;1;1;127;1

----------------------------------------------------------------------------------------------------------------------

04/14/2014 08:41:52  Inverter ON UPS general     Command
04/14/2014 07:53:49  Abnormal load voltage (Disappear) Battery         Fault
04/14/2014 07:53:49  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/14/2014 07:52:50  Abnormal load voltage (Appear) Battery         Fault
04/14/2014 07:52:49  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/14/2014 07:51:49  Abnormal load voltage (Disappear) Battery         Fault
04/14/2014 07:51:48  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/14/2014 07:50:49  Abnormal load voltage (Appear) Battery         Fault
04/14/2014 07:50:48  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/14/2014 07:46:49  Abnormal load voltage (Disappear) Battery         Fault
04/14/2014 07:46:48  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/14/2014 07:44:49  Abnormal load voltage (Appear) Battery         Fault
04/14/2014 07:44:48  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/14/2014 07:43:48  Abnormal load voltage (Disappear) Battery         Fault
04/14/2014 07:43:48  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/14/2014 07:41:49  Abnormal load voltage (Appear) Battery         Fault
04/14/2014 07:41:48  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/14/2014 07:40:49  Abnormal load voltage (Disappear) Battery         Fault
04/14/2014 07:40:48  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault

------------------------------------------------------------------------------------------------------

04/13/2014 15:53:54  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/13/2014 15:53:54  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/13/2014 15:53:53  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/13/2014 15:53:53  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/13/2014 15:53:50  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/13/2014 15:53:50  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/13/2014 15:53:48  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/13/2014 15:53:48  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault

-----------------------------------------------------------

04/12/2014 03:44:39  AC Bypass out of tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:41:44  Bypass AC source phase sequence check done Bypass AC sourc State
04/12/2014 03:41:44  Load on Bypass UPS general     State
04/12/2014 03:41:44  Bypass AC source voltage outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:41:44  Normal AC source voltage outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:41:44  AC Normal voltage extinction detection (Disappear) Normal AC sourc Fault
04/12/2014 03:41:44  Downgraded Normal AC source (Disappear) Normal AC sourc Fault
04/12/2014 03:41:44  Normal AC source voltage outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:41:44  Downgraded Normal AC source (Disappear) Normal AC sourc Fault
04/12/2014 03:41:44  Normal AC source frequency outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:41:44  Normal AC source voltage outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:41:44  AC Bypass out of tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:41:44  Bypass AC source frequency outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:41:43  Bypass AC source frequency outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:41:39  UPS on Bypass Inverter        State
04/12/2014 03:41:39  Rectifier OFF Rectifier       State
04/12/2014 03:41:39  Inverter off Inverter        State
04/12/2014 03:41:39  PFC Thermal sensor fault on battery (Appear) Rectifier       Fault
04/12/2014 03:41:38  Load not protected Load            State
04/12/2014 03:41:38  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:41:38  System global alarm (Major fault) (Appear) UPS general     Fault
04/12/2014 03:41:38  Load thermal overload (Appear) UPS general     Fault
04/12/2014 03:41:38  PFC Thermal sensor fault (Appear) Rectifier       Fault
04/12/2014 03:41:38  Load on battery(Disappearance) UPS general     State
04/12/2014 03:39:32  Low battery warning Battery         State
04/12/2014 03:39:27  Bypass AC source voltage outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:39:27  Downgraded Normal AC source (Disappear) Normal AC sourc Fault
04/12/2014 03:39:27  Downgraded Normal AC source (Disappear) Normal AC sourc Fault
04/12/2014 03:39:27  Normal AC source voltage outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:39:27  Bypass AC source phase sequence check done(Disappearance) Bypass AC sourc State
04/12/2014 03:39:27  UPS unsynchronized with AC Bypass UPS general     State
04/12/2014 03:39:27  AC Normal voltage extinction detection (Appear) Normal AC sourc Fault
04/12/2014 03:39:27  Normal AC source frequency outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:39:26  Bypass AC source frequency outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:39:26  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:39:26  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:39:26  AC Bypass out of tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:39:26  Bypass AC source frequency outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:39:26  Load on battery UPS general     State
04/12/2014 03:39:10  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:39:10  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:39:06  Load on battery(Disappearance) UPS general     State
04/12/2014 03:39:05  Bypass AC source phase sequence check done Bypass AC sourc State
04/12/2014 03:39:05  UPS synchronized with AC Bypass UPS general     State
04/12/2014 03:39:05  Bypass AC source voltage outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:39:05  AC Normal voltage extinction detection (Disappear) Normal AC sourc Fault
04/12/2014 03:39:05  Normal AC source voltage outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:39:05  Normal AC source frequency outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:39:05  AC Bypass out of tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:38:57  Bypass AC source voltage outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:38:57  Downgraded Normal AC source (Disappear) Normal AC sourc Fault
04/12/2014 03:38:57  Bypass AC source phase sequence check done(Disappearance) Bypass AC sourc State
04/12/2014 03:38:57  Downgraded Normal AC source (Disappear) Normal AC sourc Fault
04/12/2014 03:38:57  Normal AC source voltage outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:38:57  UPS unsynchronized with AC Bypass UPS general     State
04/12/2014 03:38:57  Normal AC source frequency outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:38:56  AC Normal voltage extinction detection (Appear) Normal AC sourc Fault
04/12/2014 03:38:56  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:38:56  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:38:56  AC Bypass out of tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:38:56  Load on battery UPS general     State
04/12/2014 03:34:16  Low battery warning(Disappearance) Battery         State
04/12/2014 03:34:15  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:34:15  Load on battery(Disappearance) UPS general     State
04/12/2014 03:34:14  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:34:14  Bypass AC source phase sequence check done Bypass AC sourc State
04/12/2014 03:34:14  UPS synchronized with AC Bypass UPS general     State
04/12/2014 03:34:14  Bypass AC source voltage outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:34:14  Normal AC source voltage outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:34:13  AC Normal voltage extinction detection (Disappear) Normal AC sourc Fault
04/12/2014 03:34:13  Normal AC source frequency outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:34:13  AC Bypass out of tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:33:55  Low battery warning Battery         State
04/12/2014 03:33:43  Bypass AC source voltage outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:33:43  Normal AC source voltage outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:33:43  Normal AC source frequency outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:33:43  Bypass AC source phase sequence check done(Disappearance) Bypass AC sourc State
04/12/2014 03:33:43  AC Normal voltage extinction detection (Appear) Normal AC sourc Fault
04/12/2014 03:33:43  UPS unsynchronized with AC Bypass UPS general     State
04/12/2014 03:33:42  Bypass AC source frequency outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:33:42  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:33:42  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:33:42  AC Bypass out of tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:33:42  Bypass AC source frequency outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:33:42  Load on battery UPS general     State
04/12/2014 03:30:02  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:30:02  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:30:02  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:30:02  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:29:47  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:29:47  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:29:45  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:29:45  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:29:09  Low battery warning(Disappearance) Battery         State
04/12/2014 03:29:08  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:29:08  Load on battery(Disappearance) UPS general     State
04/12/2014 03:29:07  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:29:07  Bypass AC source phase sequence check done Bypass AC sourc State
04/12/2014 03:29:07  UPS synchronized with AC Bypass UPS general     State
04/12/2014 03:29:07  Bypass AC source voltage outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:29:07  Normal AC source voltage outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:29:07  AC Normal voltage extinction detection (Disappear) Normal AC sourc Fault
04/12/2014 03:29:07  Normal AC source frequency outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:29:06  AC Bypass out of tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:28:32  Low battery warning Battery         State
04/12/2014 03:28:28  Bypass AC source voltage outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:28:28  Normal AC source voltage outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:28:28  Bypass AC source phase sequence check done(Disappearance) Bypass AC sourc State
04/12/2014 03:28:28  UPS unsynchronized with AC Bypass UPS general     State
04/12/2014 03:28:28  AC Normal voltage extinction detection (Appear) Normal AC sourc Fault
04/12/2014 03:28:28  Normal AC source frequency outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:28:27  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:28:27  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:28:27  AC Bypass out of tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:28:27  Load on battery UPS general     State
04/12/2014 03:28:02  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:28:02  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:28:02  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:28:02  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:27:47  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:27:47  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:27:45  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:27:45  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:27:14  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:27:14  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:27:09  Low battery warning(Disappearance) Battery         State
04/12/2014 03:27:08  Load on battery(Disappearance) UPS general     State
04/12/2014 03:27:07  Bypass AC source phase sequence check done Bypass AC sourc State
04/12/2014 03:27:07  UPS synchronized with AC Bypass UPS general     State
04/12/2014 03:27:07  Bypass AC source voltage outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:27:07  Normal AC source voltage outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:27:07  AC Normal voltage extinction detection (Disappear) Normal AC sourc Fault
04/12/2014 03:27:07  Normal AC source frequency outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:27:06  AC Bypass out of tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:27:02  Low battery warning Battery         State
04/12/2014 03:26:58  Bypass AC source voltage outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:26:58  Normal AC source voltage outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:26:58  Bypass AC source phase sequence check done(Disappearance) Bypass AC sourc State
04/12/2014 03:26:58  Normal AC source frequency outside tolerances (Appear) Normal AC sourc Fault
04/12/2014 03:26:58  UPS unsynchronized with AC Bypass UPS general     State
04/12/2014 03:26:58  AC Normal voltage extinction detection (Appear) Normal AC sourc Fault
04/12/2014 03:26:57  Bypass AC source frequency outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:26:57  Load on battery UPS general     State
04/12/2014 03:26:57  Downgraded operation mode (minor fault) (Appear) UPS general     Fault
04/12/2014 03:26:57  Inverter/ AC Bypass unsynchronized (Appear) Bypass AC sourc Fault
04/12/2014 03:26:57  AC Bypass out of tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:26:57  Bypass AC source frequency outside tolerances (Appear) Bypass AC sourc Fault
04/12/2014 03:24:37  Low battery warning(Disappearance) Battery         State
04/12/2014 03:24:36  Downgraded operation mode (minor fault) (Disappear) UPS general     Fault
04/12/2014 03:24:36  Inverter/ AC Bypass unsynchronized (Disappear) Bypass AC sourc Fault
04/12/2014 03:24:35  Load on battery(Disappearance) UPS general     State
04/12/2014 03:24:35  Bypass AC source phase sequence check done Bypass AC sourc State
04/12/2014 03:24:35  UPS synchronized with AC Bypass UPS general     State
04/12/2014 03:24:34  Bypass AC source voltage outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:24:34  AC Normal voltage extinction detection (Disappear) Normal AC sourc Fault
04/12/2014 03:24:34  Normal AC source voltage outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:24:34  Normal AC source frequency outside tolerances (Disappear) Normal AC sourc Fault
04/12/2014 03:24:33  AC Bypass out of tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:24:33  Bypass AC source frequency outside tolerances (Disappear) Bypass AC sourc Fault
04/12/2014 03:24:33  Bypass AC source frequency outside tolerances (Appear) Bypass AC sourc Fault

Attachments
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:17 AM . Last Modified: ‎2024-03-19 12:20 AM

0 Likes
0
1878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:17 AM . Last Modified: ‎2024-03-19 12:20 AM

Hello,

Due to the complexity of this model of UPS and the questions you have, the best support we can provide will be via your local technical support office (how to contact -> http://www.apc.com/support/contact/). I tried to see if there was any detail we could provide here but unfortunately, there is not.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:17 AM . Last Modified: ‎2024-03-19 12:20 AM

0 Likes
0
1879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:17 AM . Last Modified: ‎2024-03-19 12:20 AM

Hello,

Due to the complexity of this model of UPS and the questions you have, the best support we can provide will be via your local technical support office (how to contact -> http://www.apc.com/support/contact/). I tried to see if there was any detail we could provide here but unfortunately, there is not.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore