Galaxy 5000 120 KVA parallel load Sharing per phase is not balance

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Galaxy 5000 120 KVA parallel load Sharing per phase is not balance
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
2
1560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:22 AM

Galaxy 5000 120 KVA parallel load Sharing per phase is not balance

Hi,

We have 3 UPSs (Galaxy 5000-120KVA) that are operated in parallel but amperes per phase in 3 UPSs is not balance. You can find it in below table.

UPSsPhase RPhase SPhase TN
UPS 145 A46 A29 A40 A
UPS 211 A46 A62 A55 A
UPS 354 A24 A42 A35 A

UPSs amperes In phase T are: 29 A, 62 A, 42A.

Is it normal or UPSs load sharing per phase must be equivalent?

Regards,

Attachments
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • 120kva
  • 5000
  • galaxy
  • load_balancing
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
0
1558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:22 AM

hi

some body can help me about galaxy 5000.

how much unbalance load can tolerate Galaxy 5000?

laughingDo you have power rate table of Galaxy 5000 in different kind of power factor load?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
0
1558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:22 AM

Hello,

I contacted our EMEA support for this UPS and here is their reply. If you would like to proceed with having them provide your maintenance history and provide serial numbers privately, I'd suggest you contact your local support team via Contact Us if the reply does not help.

First you have to check the technical level of MIZN card must be at least level 11

You can only see the technical level with the SOFT1 or by looking at it directly on the card program

When you have level 11 with the passage of time can unbalance the load, it may take some time until the problem occurs.

You can restart all the equipment for the currents to swing but if the technical level of the card does not change with time can occur.

This problem, has it arisen before or has it just happened now?

If you set up your computer recently, you may already have the card level 11

The distance of the output cables must also be identical but we do not think that's the problem.

If this does not help, please update us on serial numbers, etc so that we can check up on the maintenance history.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:22 AM

hi

some body can help me about galaxy 5000.

how much unbalance load can tolerate Galaxy 5000?

laughingDo you have power rate table of Galaxy 5000 in different kind of power factor load?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of