Hi,
We have 3 UPSs (Galaxy 5000-120KVA) that are operated in parallel but amperes per phase in 3 UPSs is not balance. You can find it in below table.
| UPSs | Phase R | Phase S | Phase T | N |
|---|---|---|---|---|
| UPS 1 | 45 A | 46 A | 29 A | 40 A |
| UPS 2 | 11 A | 46 A | 62 A | 55 A |
| UPS 3 | 54 A | 24 A | 42 A | 35 A |
UPSs amperes In phase T are: 29 A, 62 A, 42A.
Is it normal or UPSs load sharing per phase must be equivalent?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:05 AM . Last Modified: 2024-03-19 12:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:05 AM . Last Modified: 2024-03-19 12:22 AM
hi
some body can help me about galaxy 5000.
how much unbalance load can tolerate Galaxy 5000?
Do you have power rate table of Galaxy 5000 in different kind of power factor load?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:05 AM . Last Modified: 2024-03-19 12:22 AM
Hello,
I contacted our EMEA support for this UPS and here is their reply. If you would like to proceed with having them provide your maintenance history and provide serial numbers privately, I'd suggest you contact your local support team via Contact Us if the reply does not help.
First you have to check the technical level of MIZN card must be at least level 11
You can only see the technical level with the SOFT1 or by looking at it directly on the card program
When you have level 11 with the passage of time can unbalance the load, it may take some time until the problem occurs.
You can restart all the equipment for the currents to swing but if the technical level of the card does not change with time can occur.
This problem, has it arisen before or has it just happened now?
If you set up your computer recently, you may already have the card level 11
The distance of the output cables must also be identical but we do not think that's the problem.
If this does not help, please update us on serial numbers, etc so that we can check up on the maintenance history.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:05 AM . Last Modified: 2024-03-19 12:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:05 AM . Last Modified: 2024-03-19 12:22 AM
hi
some body can help me about galaxy 5000.
how much unbalance load can tolerate Galaxy 5000?
Do you have power rate table of Galaxy 5000 in different kind of power factor load?