While doing generator startup and ATS power transfer tests, we received a UPS thermal overload on battery alarm and UPS shut itself down completely. UPS recovered after manual restart. Can anyone tell under what circumstance this alarm is generated. What are the possible causes? Was the UPS doing its job? This alarm is different from inventer overload alarm, isn't it? Thanks.
09/26/2014 03:31:48 Appearance Battery charge current measurement fault Charger Fault
09/26/2014 03:31:48 Appearance No load current on measurement chain Charger Fault
09/26/2014 03:31:48 Appearance Standard or L.A. charger fault UPS general Fault
09/26/2014 03:31:48 Disappearance Bypass AC source frequency outside tolerances Bypass AC sourc Fault
09/26/2014 03:31:48 Disappearance Bypass AC source phase sequence check done Bypass AC sourc Status
09/26/2014 03:31:48 Appearance Inverter stopped Inverter Status
09/26/2014 03:31:48 Appearance UPS on Bypass Inverter Status
09/26/2014 03:31:48 Appearance Forced UPS desynchronization UPS general Status
09/26/2014 03:31:48 Appearance Rectifier OFF Rectifier Status
09/26/2014 03:31:48 Appearance Contactor KA1 open UPS general Status
09/26/2014 03:31:48 Appearance Bypass AC source outage Bypass AC sourc Fault
09/26/2014 03:31:48 Appearance No UPS output voltage Output Fault
09/26/2014 03:31:48 Appearance Bypass AC source voltage outside tolerances Bypass AC sourc Fault
09/26/2014 03:31:48 Appearance Normal AC source outage Normal AC sourc Fault
09/26/2014 03:31:48 Appearance Normal AC source frequency outside tolerances Normal AC sourc Fault
09/26/2014 03:31:48 Appearance Normal AC source voltage outside tolerances Normal AC sourc Fault
09/26/2014 03:31:48 Appearance UPS thermal overload on battery Rectifier Fault
09/26/2014 03:31:48 Disappearance Load protected Output Status
09/26/2014 03:31:48 Appearance Bypass AC source frequency outside tolerances Bypass AC sourc Fault
09/26/2014 03:31:48 Appearance AC Bypass out of tolerances Bypass AC sourc Fault
09/26/2014 03:31:48 Appearance System global alarm UPS general Fault
09/26/2014 03:31:48 Appearance Downgraded operation mode UPS general Fault
09/26/2014 03:30:51 Disappearance Load on battery UPS general Status
09/26/2014 03:30:48 Disappearance Downgraded operation mode UPS general Fault
09/26/2014 03:30:47 Appearance Bypass AC source phase sequence check done Bypass AC sourc Status
09/26/2014 03:30:47 Disappearance Forced UPS desynchronization UPS general Status
09/26/2014 03:30:47 Disappearance Bypass AC source voltage outside tolerances Bypass AC sourc Fault
09/26/2014 03:30:47 Disappearance Bypass AC source frequency outside tolerances Bypass AC sourc Fault
09/26/2014 03:30:47 Disappearance AC Bypass out of tolerances Bypass AC sourc Fault
09/26/2014 03:30:46 Disappearance Bypass AC source phase sequence check done Bypass AC sourc Status
09/26/2014 03:30:46 Appearance Forced UPS desynchronization UPS general Status
09/26/2014 03:30:46 Disappearance Bypass AC source outage Bypass AC sourc Fault
09/26/2014 03:30:46 Disappearance Bypass AC source voltage outside tolerances Bypass AC sourc Fault
09/26/2014 03:30:46 Disappearance Normal AC source outage Normal AC sourc Fault
09/26/2014 03:30:46 Disappearance Normal AC source frequency outside tolerances Normal AC sourc Fault
09/26/2014 03:30:46 Appearance Bypass AC source frequency outside tolerances Bypass AC sourc Fault
09/26/2014 03:30:46 Appearance AC Bypass out of tolerances Bypass AC sourc Fault
09/26/2014 03:30:46 Appearance Load on battery UPS general Status
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:20 AM . Last Modified: 2024-03-19 12:17 AM
ONE THING TO CHECK IS THE BATTERY STATIC SWITCH, THE DRIVER PCA MIGHT BE FAULTY.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:19 AM . Last Modified: 2024-03-19 12:17 AM
Hello,
I asked our 3 phase support team. They told me:
Part of the answer lies in how old the batteries are. The UPS was on battery for almost 1 minute before it could not sustain the load on battery at this point the bypass was not available, so the load dropped. The only way to know for sure would be for a Field Service Engineer to be on site and repeat the test and get readings and download service logs. If the batteries are old, it may not be able to support the load for a short period and would need to be replaced.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:19 AM . Last Modified: 2024-03-19 12:17 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:19 AM . Last Modified: 2024-03-19 12:17 AM
Our batteries are two years old. After UPS was restored, we opened/closed input breaker several times without any problem. The longest open/close switch was 5 minutes. We will do more tests on batteries to check their condition.
Can Galaxy 3000 UPS return to online from battery mode if the bypass source is not available?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:19 AM . Last Modified: 2024-03-19 12:17 AM
Hi again,
Here is what I got:
If the UPS is in battery mode it can not go to online if the utility power (bypass) is not available. Once utility power is restore, the UPS will leave battery power and be online.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:19 AM . Last Modified: 2024-03-19 12:17 AM
Hello there,
First, check battery,
second, might have a defective power supply,
third, issues with ups management PCBs.
Now, for the first issue, if you're techsavvy, it is ok for you to do troubleshooting, but 2nd and 3rd, have a Schneider FSE come down to see you, it is pretty interesting and not user/customer friendly repair.
hope I could help.
cheers.
M
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 06:20 AM . Last Modified: 2024-03-19 12:17 AM
ONE THING TO CHECK IS THE BATTERY STATIC SWITCH, THE DRIVER PCA MIGHT BE FAULTY.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.