Fix for Smart UPS dropping load on self test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Fix for Smart UPS dropping load on self test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:51 AM

0 Likes
5
2266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:51 AM

Fix for Smart UPS dropping load on self test

We have 8 Smart UPS (SU1500 & SU2200 models) in our envirment and we moved around some of the load and now a couple of them are dropping the load on self test and causing servers to reboot. We installed new batteries and they continue to fail. I read that this is a known issue.

Are there recommended adjustments that can be made to fix this issue?

A UPS should not cause the problem that it is meant to solve.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

0 Likes
0
2264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

We have 8 Smart UPS (SU1500 & SU2200 models) in our envirment and we moved around some of the load and now a couple of them are dropping the load on self test and causing servers to reboot. We installed new batteries and they continue to fail. I read that this is a known issue.

Are there recommended adjustments that can be made to fix this issue?

A UPS should not cause the problem that it is meant to solve.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

0 Likes
0
2264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

The two are both SUA1500 ups and the serial numbers are AS0527222230 & AS0526232090. Both are showing full charge and 33% load and no cables or cards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

0 Likes
0
2264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

Hi,

After the self test has been done, have you seen any indicator and audible alarm that says Replace Battery? Since you have said from the previous statement that you have moved around loads, have you checked if the UPS is sufficient to handle all of them by watts/va capacity?
You may also want to decrease load on the unit that is dropping the load and see the reposnse of the UPS.

Basically, when the UPS does an automatic self test or if the customer do it manually, and it dropped the load, it is more likely the battery is already weak and needs to be replaced or the battery charge is not sufficient to handle the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

0 Likes
0
2264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

You did mention you installed new batteries, though I'm curious if those are APC batteries?

I'm not sure where you heard/read this is a known issue, but it isn't. As you said, a UPS should not drop the load with a good, working battery for absolutely no reason. I know in the past, people mentioned that the UPS turned off when running a self-test (or during a power outage) with BAD batteries, but not with good ones. And that shouldn't be an issue on the newer SUA models. You first said SU and then SUA - which one is it?

Try disconnecting the servers and connecting something else (radio, lamp, anything) and run another self-test to see if that makes any difference. Also, how are you running these tests? You said there are no cables attached so that means you're not using the software to initiate a test.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

0 Likes
0
2264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

It would be good to understand specifically what kind of servers are rebooting. On the UPSs with this issue, does all the attached equipment reboot, or just select servers?

Also, have you tried shifting loads that do not reboot onto these UPSs to see if the behavior follows the UPS or the server? It's very unlikely that the UPSs are not performing to specification.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

0 Likes
0
2265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:22 AM . Last Modified: ‎2024-03-14 12:50 AM

We have 8 Smart UPS (SU1500 & SU2200 models) in our envirment and we moved around some of the load and now a couple of them are dropping the load on self test and causing servers to reboot. We installed new batteries and they continue to fail. I read that this is a known issue.

Are there recommended adjustments that can be made to fix this issue?

A UPS should not cause the problem that it is meant to solve.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore