Hello,
I'm attempting to upgrade the firmware on a handful of SmartUPS 700 RMs and it's failing to ftp the .bin file successfully. I've updated 10 Smart UPS 2200 devices, but for whatever reason, these 700s aren't being very receptive to my efforts.
I successfully used the upgrade utility to upgrade the 2200s - using the same utility, I get ftp file transfer problems with the 700s - as I also get when I attempt to manually ftp.
Are there any other remote methods for update these 700s, or perhaps something to look for?
Thanks,
Drew
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
Easy to overlook considering I never mentioned what card I had until the end -
Thank you much, the correct firmware did the trick.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
Hello Erasmus,
Different subnets from my (the updating PC) - but then again, so were the 2200s.
Is it possible to update the firmware via tftp?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
I assume you are referring to the NMC firmware upgrade? Are these 700s located on a different network subnet/segment or do they have any different network settings?
Keep in mind the firmware for the 2200 Smart-UPS is the same for the 700s. All Smart-UPS' use the same firmware for their NMCs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
not TFTP, only FTP.
you could try one via manual FTP, even though thats what the wizard does but it may work.
check [these instructions|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8515]
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
I'm getting ready to throw this thing out the window.
It's a fairly standard AP9606 NMC and I've tried everything to try and update the firmware.
It has aos301.bin and sumx301.bin loaded.
--------------------------------UPS Info:----------------------------------
About System
Model Number : AP9606
Manufacture Date : 10/13/2000 Hardware Revision : G9
Flash Vendor : STM
Description : Smart-UPS & Matrix-UPS APP
-----------------------------------------------------------------------
Name : sumx301.bin Type : StatApp
Version : v3.0.1 Sector : 4
Date : 07/11/2000 Time : 13:08:25
CRC16 : 72EC
Description : Web/SNMP Management Card AOS
-----------------------------------------------------------------------
Name : aos301.bin Type : APC OS
Version : v3.0.1 Sector : 11
Date : 06/27/2000 Time : 19:06:47
CRC16 : CB60
-----------------------------------------------------------UPS Event Log ----------------------------------------------------------------
Date: 05/04/2009 Time: 16:27:45
------------------------------------
Smart-UPS 700 RM named UPS700 : On
Date Time Event
--------------------------------------------------------------------------
05/04/2009 16:25:58 System: Control Console User apc logged in from
serial Control Console.
05/04/2009 16:12:44 System: File transfer failed.
05/04/2009 16:12:44 System: File transfer failed.
05/04/2009 16:11:26 System: File transfer failed.
05/04/2009 16:11:26 System: File transfer failed.
05/04/2009 16:10:48 System: File transfer failed.
05/04/2009 16:10:48 System: File transfer failed.
05/04/2009 16:10:08 System: File transfer failed.
05/04/2009 16:10:08 System: File transfer failed.
05/04/2009 16:08:54 System: Control Console User apc logged in from
serial Control Console.
05/04/2009 16:07:38 UPS: Communications established.
-----------------------------------------------ATTEMPT with LATEST firmware version:-----------------------------------------
Using AOS file : AOS = apc_hw02_aos_361.bin
Using Application file: APP = apc_hw02_sumx_358.bin
Checking network connection ... Checking version information ...
*************** Next **************
Before Upgrading the NMC the AOS is: ÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌ226 Closing data connection.
* Detected early version, two AOS upgrades required
Attempting to log in to 172.28.200.21 ... Log in sucessful
Loading OS, please wait ... Firmware download failed.
Attempting to log in to 172.28.200.21 ... Log in sucessful
Loading OS, please wait ... Firmware download failed.
Not all Network Management Cards were upgraded successfully:
172.28.200.21: Could not download AOS.
Encountered 1 failures during upgrade.
----------------------- ATTEMPT USING OLDEST AVAILABLE FIRMWARE-----------------------
Using AOS file : AOS = apc_hw02_aos_202.bin
Using Application file: APP = apc_hw02_sumx_253.bin
Checking network connection ... Checking version information ...
*************** Next **************
Before Upgrading the NMC the AOS is: ÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌ226 Closing data connection.
Attempting to log in to 172.28.200.21 ... Log in sucessful
Loading OS, please wait ... Firmware download failed.
Not all Network Management Cards were upgraded successfully:
172.28.200.21: Could not download AOS.
Encountered 1 failures during upgrade.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
okay. Erasmus and I both overlooked the fact that you are using the older discontinued AP9606 web management card which does NOT work with the wizard/firmware that you are using. that is why you are running into these problems. the other management cards may have been our more current AP9617, AP9618, or AP9619 which use the newer firmware you are trying to flash the AP9606 with.
here is the link to the correct firmware for the AP9606 card: ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v326b/
you will HAVE to use the instructions for FTP that I gave you since there is no wizard. download the aos326b.bin file in that folder above and then choose the appropriate APP, which looks to be sumx326a.bin for your Smart UPS.
[here are the FTP instructions again|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8515]
that should fix the issue.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:50 PM . Last Modified: 2024-03-14 11:34 PM
Easy to overlook considering I never mentioned what card I had until the end -
Thank you much, the correct firmware did the trick.